    Prestcold Condensing Unit

    Hello,

    Wondering if anyone knows the following:

    Upon arriving at site found compressor cycling on klixon. checked the capacitors and found none of them (start and run) to be original, the start was rated 160-200uF and the run at 5uF. As there was a capacitor on the fan motor rated at 3uF, I tested the run capacitor on that it and it didn't work. I didn't have another capacitor to test for the bigger one.

    The question is what should they be? I thought the run was usually about 7uF?

    The unit is single phase (240v 50hz) and is a K75

    If anyone can help let me know

    Many thanks

  2. #2
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Prestcold Condensing Unit

    Hi Sighman,

    It may be more expensice to go through them but why no go to NRS how sell the spares for these units

    Start Cap NRS Pt No 676450 £44.85 list
    Run Cap NRS Pt No 676457 £13.13 list
    Relay NRS Pt No 676856 £44.65 list

    or Complete Electric pack (all of above in box)
    690333 £67.08 list.


    have had loads of probs with these, check over the pot internatl elecs because the first sign the compressors is on way out is it keeps blowing capacitors. The amount of times i have known engineers to spend hours looking for an electrical fault, changing elecs and then finding pot u/s is riduculas

    Regards

    Fatboy

  3. #3
    Join Date
    Oct 2003
    Location
    UK
    Posts
    22
    Rep Power
    0

    Re: Prestcold Condensing Unit

    Hi Rdocwra,
    How would you confirm your assumption that the compressor is on its way out?
    Alan B.

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Prestcold Condensing Unit

    found compressor cycling on klixon
    This is a good sign that it is on its out. Especially if the starting gear still connected.
    These parts hardly ever go out.


    Chemi
    Last edited by chemi-cool; 26-02-2005 at 10:08 AM.

  5. #5
    Join Date
    Mar 2002
    Location
    San Francisco Bay Area
    Posts
    180
    Rep Power
    23

    Re: Prestcold Condensing Unit

    Quote Originally Posted by chemi-cool
    This is a good sign that it is on its out. Especially if the starting gear still connected.
    These parts hardly ever go out.
    I have to disagree with you here, Chemi. I change many more relays than compressors. Just consider a set of points opening and closing against an inductive load up to six times an hour for a few years. Compare them to contactors on a 3-phase unit. Can you say that contactors hardly ever go out?

    Quote Originally Posted by rdocwra
    the first sign the compressors is on way out is it keeps blowing capacitors.
    Only if the relay was changed each time with a factory spec. replacement. Blowing capacitors is the sign of a faulty or mis-applied relay. Never change a capacitor without changing the relay or you'll be back. Even if the relay works great while you're there, a failed capacitor points to a failing relay.

    I hired an experienced air conditioning tech once and was surprised to learn he was unable to draw a start diagram for a CSIR (capacitor-start, induction-run) type compressor. He had always worked with 3-phase or PSC (permanent split-capacitor) units. (I discovered this when he called me at two in the morning because the walk-in compressor he had been called out on had fused wiring and he didn't know how to reconnect to run a start test with spares.)

    Get yourself a capacitor tester! They are inexpensive, save time (especially on a freezing rooftop in the rain at night!) and last a loooong time.

    Since I do light commercial service with lots of single-phase units, I carry standard capacitor sizes, both start and run. True, some of them I have had on the truck for years, but they don't take up much space, they are relatively cheap and they can save a room full of perishables, not to mention your reputation.

    I carry the highest voltages, since they can be used on lower voltage, and they can be combined in parallel to sum their capacitances when needed. Likewise I carry the most common factory relays and a few universal relays for emergencies, but I change them for factory spec at the first opportunity.

    I have probably gained a new customer or two every year when called out for a second opinion on a condemned compressor because the original company sent a guy who "didn't seem to know what he was doing." Usually I find a bad relay, blown capacitor and normal compressor. Avarice or ignorance?

    Rog

  6. #6
    Join Date
    Jan 2004
    Location
    South Africa
    Posts
    71
    Rep Power
    21

    Re: Prestcold Condensing Unit

    I agree with Rog,

    Cheers,
    Feeze

  7. #7
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Prestcold Condensing Unit

    1) get a megger and do an earth leakage check
    2) Shut the pot off, reclaim gas and wip the head off and have a look inside to see how stiff the pistons are

    Regards

    Fatboy

  8. #8
    Join Date
    Jan 2004
    Location
    Queenstown, New Zealand
    Age
    48
    Posts
    18
    Rep Power
    0

    Re: Prestcold Condensing Unit

    Hi,

    I was thinking more that someone had put the wrong capacitors onto the system, and perhaps these have caused a failure of the compressor?

    From the above part numbers I can see that it should be 160uF and 5uF

    The windings seem ok on ohm testing. The relay didn't have any scorch marks on it, just didn't have a big enough capacitor with me to try replacing start cap..........nearest supplier was 60 miles away!
    Last edited by sighman; 26-02-2005 at 10:52 AM.

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Prestcold Condensing Unit

    Can you give the compressor hp size and manufacturer?

    Chemi

Similar Threads

  1. M I T S U S H I T A ac unit with no condensing unit
    By Chinua in forum Air Conditioning
    Replies: 2
    Last Post: 28-07-2006, 06:54 PM
  2. York/Bristol Condensing Unit
    By Abe in forum Commercial
    Replies: 1
    Last Post: 03-02-2003, 07:46 PM
  3. Matching Evaporator with Condensing Unit
    By Abe in forum Technical Discussions
    Replies: 12
    Last Post: 25-07-2001, 08:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •