25-02-2005, 11:08 PM #1
Prestcold Condensing Unit
Hello,
Wondering if anyone knows the following:
Upon arriving at site found compressor cycling on klixon. checked the capacitors and found none of them (start and run) to be original, the start was rated 160-200uF and the run at 5uF. As there was a capacitor on the fan motor rated at 3uF, I tested the run capacitor on that it and it didn't work. I didn't have another capacitor to test for the bigger one.
The question is what should they be? I thought the run was usually about 7uF?
The unit is single phase (240v 50hz) and is a K75
If anyone can help let me know
Many thanks
-
25-02-2005, 11:36 PM #2
Re: Prestcold Condensing Unit
Hi Sighman,
It may be more expensice to go through them but why no go to NRS how sell the spares for these units
Start Cap NRS Pt No 676450 £44.85 list
Run Cap NRS Pt No 676457 £13.13 list
Relay NRS Pt No 676856 £44.65 list
or Complete Electric pack (all of above in box)
690333 £67.08 list.
have had loads of probs with these, check over the pot internatl elecs because the first sign the compressors is on way out is it keeps blowing capacitors. The amount of times i have known engineers to spend hours looking for an electrical fault, changing elecs and then finding pot u/s is riduculas
Regards
Fatboy
-
26-02-2005, 09:37 AM #3
Re: Prestcold Condensing Unit
Hi Rdocwra,
How would you confirm your assumption that the compressor is on its way out?
Alan B.
-
26-02-2005, 10:05 AM #4
Re: Prestcold Condensing Unit
found compressor cycling on klixon
These parts hardly ever go out.
ChemiLast edited by chemi-cool; 26-02-2005 at 10:08 AM.
-
27-02-2005, 11:11 PM #5
Re: Prestcold Condensing Unit
Originally Posted by chemi-cool
Originally Posted by rdocwra
I hired an experienced air conditioning tech once and was surprised to learn he was unable to draw a start diagram for a CSIR (capacitor-start, induction-run) type compressor. He had always worked with 3-phase or PSC (permanent split-capacitor) units. (I discovered this when he called me at two in the morning because the walk-in compressor he had been called out on had fused wiring and he didn't know how to reconnect to run a start test with spares.)
Get yourself a capacitor tester! They are inexpensive, save time (especially on a freezing rooftop in the rain at night!) and last a loooong time.
Since I do light commercial service with lots of single-phase units, I carry standard capacitor sizes, both start and run. True, some of them I have had on the truck for years, but they don't take up much space, they are relatively cheap and they can save a room full of perishables, not to mention your reputation.
I carry the highest voltages, since they can be used on lower voltage, and they can be combined in parallel to sum their capacitances when needed. Likewise I carry the most common factory relays and a few universal relays for emergencies, but I change them for factory spec at the first opportunity.
I have probably gained a new customer or two every year when called out for a second opinion on a condemned compressor because the original company sent a guy who "didn't seem to know what he was doing." Usually I find a bad relay, blown capacitor and normal compressor. Avarice or ignorance?
Rog
-
28-02-2005, 05:56 AM #6
Re: Prestcold Condensing Unit
I agree with Rog,
Cheers,
Feeze
-
26-02-2005, 10:06 AM #7
Re: Prestcold Condensing Unit
1) get a megger and do an earth leakage check
2) Shut the pot off, reclaim gas and wip the head off and have a look inside to see how stiff the pistons are
Regards
Fatboy
-
26-02-2005, 10:43 AM #8
Re: Prestcold Condensing Unit
Hi,
I was thinking more that someone had put the wrong capacitors onto the system, and perhaps these have caused a failure of the compressor?
From the above part numbers I can see that it should be 160uF and 5uF
The windings seem ok on ohm testing. The relay didn't have any scorch marks on it, just didn't have a big enough capacitor with me to try replacing start cap..........nearest supplier was 60 miles away!Last edited by sighman; 26-02-2005 at 10:52 AM.
-
26-02-2005, 11:55 AM #9
Re: Prestcold Condensing Unit
Can you give the compressor hp size and manufacturer?
Chemi
Similar Threads
-
M I T S U S H I T A ac unit with no condensing unit
By Chinua in forum Air ConditioningReplies: 2Last Post: 28-07-2006, 06:54 PM -
York/Bristol Condensing Unit
By Abe in forum CommercialReplies: 1Last Post: 03-02-2003, 07:46 PM -
Matching Evaporator with Condensing Unit
By Abe in forum Technical DiscussionsReplies: 12Last Post: 25-07-2001, 08:57 AM