    Re: Altherma frequent compressor cycling

    Quote Originally Posted by afternine;179629OK
    , but what would be an optimal number of cycles in such mild conditions? What number of cycles per hour would you like to see if it was your heatpump?
    Without a buffer, it either runs more often or has wider temp swings... pick your poison. Six per hour is acceptable.

  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Altherma frequent compressor cycling

    Quote Originally Posted by Gary View Post
    Without a buffer, it either runs more often or has wider temp swings... pick your poison. Six per hour is acceptable.
    Agreed,
    I think this must be a well insulated house (or very small), and a quick acting system.

Similar Threads

  1. How are the Daikin Altherma units?
    By LucMan in forum Air Conditioning
    Replies: 11
    Last Post: 15-07-2010, 11:08 PM
  2. Daikin Altherma System 8kw
    By RB0001 in forum Domestic
    Replies: 5
    Last Post: 20-04-2009, 10:22 PM
  3. Sizing Low temperature rads for Daikin Altherma
    By Debonair Spain in forum Domestic
    Replies: 9
    Last Post: 20-04-2009, 10:21 PM
  4. Frequent refrigerant charging
    By desaipt2003 in forum Trouble Shooting
    Replies: 16
    Last Post: 31-03-2009, 02:37 AM
  5. Altherma from Daikin
    By Scott Samson in forum New Technologies
    Replies: 25
    Last Post: 20-02-2009, 11:03 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •