    Supermarket rack oil return issues..



    same old same old.. but i have a frigrite copeland
    rack that is losing oil from its seperator after a week or so..
    compressors have trax oil control..oil line to them is warm/hot..
    system has heat reclaim and i fear the 3 way valve may be leaking, logging oil in heat coil. reason i say this is when i power 3 way s/v coil the oil returns...
    but also suspect sep faulty due to hot return line..
    any ideas???



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Supermarket rack oil return issues..

    Quote Originally Posted by pooletable View Post
    same old same old.. but i have a frigrite copeland
    rack that is losing oil from its seperator after a week or so..
    compressors have trax oil control..oil line to them is warm/hot..
    system has heat reclaim and i fear the 3 way valve may be leaking, logging oil in heat coil. reason i say this is when i power 3 way s/v coil the oil returns...
    but also suspect sep faulty due to hot return line..
    any ideas???

    The seperator will only return the oil that is inside it.
    If there is no oil and it is passing that could mean that the float
    valve in the bottom is jammed open and passing?? That may be
    your problem but I would look to a few other things as well.

    1st check each comp for oil return because if one of the comps is
    passing oil it will flush all the oil out.

    2nd check the heating coil and perhaps isolate it for a few days if
    possible to prove if it is that.

    If the heating coil valve is faulty (passing) you need to look at r
    eplaceing / repairing it or if it is ok you need to look at a way to
    get the oil back.

    Go back to basics.

    How old is the system and has it worked ok till now?
    If yes then look for the common denominator that links the faults together.

    Cheers taz.

    .

  3. #3
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: Supermarket rack oil return issues..

    i would check that you dont have any nrv's passing on a compressor, as what can happen when compressor cut's of, the discharge presure comes back through and lifts out all the oil, i have suffered this on many a old Hussmann pack!

  4. #4
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Supermarket rack oil return issues..

    Quote Originally Posted by pooletable View Post
    same old same old.. but i have a frigrite copeland
    rack that is losing oil from its seperator after a week or so..
    compressors have trax oil control..oil line to them is warm/hot..
    system has heat reclaim and i fear the 3 way valve may be leaking, logging oil in heat coil. reason i say this is when i power 3 way s/v coil the oil returns...
    but also suspect sep faulty due to hot return line..
    any ideas???
    Hi Pooletable

    would the oil separator be a Colecent type with a filter in it needing changing

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  5. #5
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: Supermarket rack oil return issues..

    If its a Frigrite rack with copeland comps chances are it is an old one and has a temprite oil separator - Andy's comments are valid
    ...and she said "give it to me you big fridgie"

Similar Threads

  1. Supermarket rack oil reservoir question
    By friocold2008 in forum Supermarket Refrigeration
    Replies: 2
    Last Post: 05-12-2009, 07:38 AM
  2. trouble with liquid return after defrost in rack
    By coldkeeper1 in forum Supermarket Refrigeration
    Replies: 12
    Last Post: 18-09-2009, 09:46 PM
  3. Best place for return air sensors, in the room or ceiling void?
    By back2space in forum Air Conditioning
    Replies: 27
    Last Post: 06-07-2009, 06:21 AM
  4. temporary communication failure in supermarket rack controller
    By racktech2008 in forum Supermarket Refrigeration
    Replies: 12
    Last Post: 27-04-2008, 09:17 AM
  5. R744 Supermarket Rack
    By 750 Valve in forum Supermarket Refrigeration
    Replies: 5
    Last Post: 28-07-2006, 03:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •