06-02-2010, 04:22 AM #1
Problem with LG split unit
I have had this split unit about 6 months and it has worked great. We had our first snow and ice this week and the residual remained on for about 5 days. There is no ice on the external unit. However, when I try to use the heat, the defrost light comes on and the fan outside blows but no air comes out on the inside. The defrost light will not go out.
I am in need of some advise
-
06-02-2010, 05:07 AM #2
Re: Problem with LG split unit
How long are you leaving the unit on?
IN very cold weather it can be nearlly 10minutes before the indoor unit will start to blow warm.
The defrost light on the indoor unit lights up when the unit first turns on and is in pre heat mode... or when it goes into defrost. It also comes on when the unit has reached the set temp indoors and is on standby.
Have you got your temp set right and left it about 10minutes to kick in?
-
06-02-2010, 08:41 AM #3
Re: Problem with LG split unit
If you are operating in heating mode with outdoor temperatures down to freezing you will get very little heat bar that being generated by the compressor so whatever the kwatt rating of the compessor is you won't get much more than that.
-
06-02-2010, 10:46 AM #4
-
06-02-2010, 12:31 PM #5
Re: Problem with LG split unit
Interesting,what model is that and would be interested in the spec ?
Sorry I always understood they were ok down to +5c ish then performance in heating mode
drops off,stand corrected if thats not the case.
can't remember the heating spec but found this on lg's site in the spec for a s24 split(8k on heating) min/mid/max output on heating,
W 3,605 /8,080 /8,407 Btu/hr 12,300 / 27,570 / 29,700
How is this interpreted in terms of operating temperatures?
BGLast edited by spimps; 06-02-2010 at 01:17 PM.
-
06-02-2010, 02:23 PM #6
Re: Problem with LG split unit
I have left it on all day and the defrost light will not go out, hence no heat.
-
06-02-2010, 02:28 PM #7
-
06-02-2010, 02:37 PM #8
-
06-02-2010, 04:35 PM #9
Re: Problem with LG split unit
You lose output on all the inverter units below 5C but the performance drop off is not very much.
http://mylg.co.uk/data%20for%20site/...%20outdoor.pdf
Page 60 you should look at.
Its the capacity tables as the temp drops off, at different temps.
-
06-02-2010, 08:00 PM #10
Re: Problem with LG split unit
See if the system operates in cooling. If you get no duty in cooling then I would say you might be looking at a refrigerant issue. The defrost light is also a pre heat indication. It sounds as if the indoor coil is not getting up to temperature this could be either a sensor issue or refrigerant issue. If system works in cooling then you can eliminate refrigerant issue.
-
06-02-2010, 08:08 PM #11
-
06-02-2010, 08:10 PM #12
-
06-02-2010, 08:17 PM #13
-
06-02-2010, 08:21 PM #14
Re: Problem with LG split unit
No. It's not warm. Will it get warm even if no air is coming out?
-
06-02-2010, 08:32 PM #15
-
07-02-2010, 03:59 AM #16
Re: Problem with LG split unit
-
07-02-2010, 04:13 AM #17
-
07-02-2010, 04:29 AM #18
Re: Problem with LG split unit
that's what I was trying to avoid because they are charging me a rediculous service and labor fee, but the part is free due to the warranty. go figure.
-
07-02-2010, 05:28 AM #19
-
07-02-2010, 08:38 AM #20
Re: Problem with LG split unit
Hi,
Can you clarify what is happening. Your post is not making sense. On the one hand you are saying the coil isn't warm, and elsewhere you say that you pressed a button and it blew hot air?? Perhaps you meant the outdoor unit blew hot air ?.
First test: Raise the indoor flap, remove the RH side filter and look for a small encapsulated thermistor set just off the coil fins. Turn the unit on to cooling, and hold the thermistor between finger and thumb. You may have to wait a few minutes... The indoor fan will come on of course, but we are trying to establish whether the unit will cool or not. I know you tried this before, but if the room temp is not warm enough cooling will not occur. hence the thermistor test. Let us know what you find, and clear up the blow hot air thing...
-
07-02-2010, 04:51 PM #21
Re: Problem with LG split unit
A split won't go on proper defrost for at least 40min operation.
If it's indicating defrost before that, it either a) in pre heat mode and not moving from that mode due to lack of refrigerant, compressor or fan operation, or the reversing vale is not operating. or b) faulty control PCB or thermistors.
edit eg if the indoor coil gets hot, but the fan doesn't start, it's either the indoor coil thermistor faulty or the gas charge is low due to leak (or compressor or rv fault) that the coil doesn't quite get hot enough to start the heating cycle.Last edited by paul_h; 07-02-2010 at 04:55 PM.
-
07-02-2010, 06:05 PM #22
-
07-02-2010, 06:23 PM #23
-
08-02-2010, 02:20 AM #24
Re: Problem with LG split unit
Ok. The unit will not blow hot air or cold air. While investigating the situation, I took the top cover off of the unit outside to have a look inside. I noticed a curciut board on the backside of the front of the unit (on the inside); it had a green and yellow lED light on it. I also saw a small square botton. I pushed the button and it caused the green red light to com on. Pushed it again and it caused the green light to come on and againg and both lights came on.
After pushing it a few times and going back to the inside unit, I figured out that when I pushed it a few times; the heat would blow inside. The wierd thing is that the display on the inside unit will go off anf the air panel will shut, but the hot air continues to blow. I fugure it's some type of over-ride?
Anyway, that's where I am at now. By the way, I did the first test you ask and got no cold air.
-
08-02-2010, 02:28 AM #25
Re: Problem with LG split unit
Correction: Green and Red LED light . Sorry.
-
08-02-2010, 03:45 AM #26
Re: Problem with LG split unit
Are the red/green lights flashing at all?
http://mylg.co.uk/data%20for%20site/...%20_gh-km_.pdf
Page 2 shows the fault codes on the outdoor unit if there is any.
-
08-02-2010, 02:15 PM #27
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Problem with LG split unit
No you cannot! Since different volumes of parts involved when cooling or heating there is also different amount of refrigerant required, and therefore, that diagnostic method is inconclusive. Only certain way to determine correct refrigerant amount is by recover and weigh it.
-
08-02-2010, 02:29 PM #28
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
11-02-2010, 09:55 PM #29
Re: Problem with LG split unit
-
11-02-2010, 10:34 PM #30
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Problem with LG split unit
No, you are not wrong in that part. But you are wrong in this:
If system works in cooling then you can eliminate refrigerant issue.
Also, I did not said that HE should recover or weigh system.
-
12-02-2010, 12:52 PM #31
Re: Problem with LG split unit
I think you can contact to the store where you bought unit?? the
-
26-03-2010, 11:32 PM #32
Re: Problem with LG split unit
Finally working. It was a sensor on the outside blower. The voltage was off, hence it was reading the wrong temperature.
Similar Threads
-
Installing pipework for single split unit
By electro in forum Air ConditioningReplies: 51Last Post: 05-03-2009, 06:02 PM -
Lennox unit problem
By marc5180 in forum Air ConditioningReplies: 35Last Post: 08-11-2008, 10:16 PM -
SL/SB-400 Pump Down Procedures
By absolute-zero in forum TransportReplies: 1Last Post: 29-01-2008, 09:27 PM -
Problem with ducted Daikin
By jutty in forum Trouble ShootingReplies: 8Last Post: 23-07-2007, 05:34 AM -
Problem with Mitsubishi Heavy Indusry Unit blowing 3 amp fuse
By kelvin01 in forum Air ConditioningReplies: 3Last Post: 04-03-2007, 07:03 PM