    Problem with LG split unit



    I have had this split unit about 6 months and it has worked great. We had our first snow and ice this week and the residual remained on for about 5 days. There is no ice on the external unit. However, when I try to use the heat, the defrost light comes on and the fan outside blows but no air comes out on the inside. The defrost light will not go out.

    I am in need of some advise



  2. #2
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Problem with LG split unit

    Quote Originally Posted by trprph View Post
    I have had this split unit about 6 months and it has worked great. We had our first snow and ice this week and the residual remained on for about 5 days. There is no ice on the external unit. However, when I try to use the heat, the defrost light comes on and the fan outside blows but no air comes out on the inside. The defrost light will not go out.

    I am in need of some advise
    How long are you leaving the unit on?

    IN very cold weather it can be nearlly 10minutes before the indoor unit will start to blow warm.

    The defrost light on the indoor unit lights up when the unit first turns on and is in pre heat mode... or when it goes into defrost. It also comes on when the unit has reached the set temp indoors and is on standby.

    Have you got your temp set right and left it about 10minutes to kick in?

  3. #3
    Join Date
    Sep 2008
    Location
    Letsby Avenue
    Posts
    359
    Rep Power
    17

    Re: Problem with LG split unit

    If you are operating in heating mode with outdoor temperatures down to freezing you will get very little heat bar that being generated by the compressor so whatever the kwatt rating of the compessor is you won't get much more than that.

  4. #4
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Problem with LG split unit

    Quote Originally Posted by spimps View Post
    If you are operating in heating mode with outdoor temperatures down to freezing you will get very little heat bar that being generated by the compressor so whatever the kwatt rating of the compessor is you won't get much more than that.
    What a load of rubbish, my lg system has heated the entire flat to 22C with temps as low as -8C outdoors! its rated down to -15C

  5. #5
    Join Date
    Sep 2008
    Location
    Letsby Avenue
    Posts
    359
    Rep Power
    17

    Re: Problem with LG split unit

    Quote Originally Posted by back2space View Post
    What a load of rubbish, my lg system has heated the entire flat to 22C with temps as low as -8C outdoors! its rated down to -15C
    Interesting,what model is that and would be interested in the spec ?
    Sorry I always understood they were ok down to +5c ish then performance in heating mode
    drops off,stand corrected if thats not the case.
    can't remember the heating spec but found this on lg's site in the spec for a s24 split(8k on heating) min/mid/max output on heating,
    W 3,605 /8,080 /8,407 Btu/hr 12,300 / 27,570 / 29,700
    How is this interpreted in terms of operating temperatures?
    BG
    Last edited by spimps; 06-02-2010 at 01:17 PM.

  6. #6
    Join Date
    Feb 2010
    Location
    US
    Posts
    12
    Rep Power
    0

    Re: Problem with LG split unit

    I have left it on all day and the defrost light will not go out, hence no heat.

  7. #7
    Join Date
    Feb 2010
    Location
    US
    Posts
    12
    Rep Power
    0

    Re: Problem with LG split unit

    Quote Originally Posted by spimps View Post
    Interesting,what model is that and would be interested in the spec ?
    Sorry I always understood they were ok down to +5c ish then performance in heating mode
    drops off,stand corrected if thats not the case.
    can't remember the heating spec but found this on lg's site in the spec for a s24 split(8k on heating) min/mid/max output on heating,
    W 3,605 /8,080 /8,407 Btu/hr 12,300 / 27,570 / 29,700
    How is this interpreted in terms of operating temperatures?
    BG

    The model is LSN182HE. It is a neo plasma LG unit. That's about all I know. I was thinking it may be the defrost control board or a temperature sensor.

  8. #8
    Join Date
    Feb 2010
    Location
    US
    Posts
    12
    Rep Power
    0

    Re: Problem with LG split unit

    Quote Originally Posted by back2space View Post
    How long are you leaving the unit on?

    IN very cold weather it can be nearlly 10minutes before the indoor unit will start to blow warm.

    The defrost light on the indoor unit lights up when the unit first turns on and is in pre heat mode... or when it goes into defrost. It also comes on when the unit has reached the set temp indoors and is on standby.

    Have you got your temp set right and left it about 10minutes to kick in?
    I have left it on all day. The temperature outside was 40+ and still the defrost light comes on. When the unit comes on, I set the temp to 70 and the defrost light comes on.

  9. #9
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Problem with LG split unit

    Quote Originally Posted by spimps View Post
    Interesting,what model is that and would be interested in the spec ?
    Sorry I always understood they were ok down to +5c ish then performance in heating mode
    drops off,stand corrected if thats not the case.
    can't remember the heating spec but found this on lg's site in the spec for a s24 split(8k on heating) min/mid/max output on heating,
    W 3,605 /8,080 /8,407 Btu/hr 12,300 / 27,570 / 29,700
    How is this interpreted in terms of operating temperatures?
    BG
    You lose output on all the inverter units below 5C but the performance drop off is not very much.

    http://mylg.co.uk/data%20for%20site/...%20outdoor.pdf

    Page 60 you should look at.

    Its the capacity tables as the temp drops off, at different temps.

  10. #10
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: Problem with LG split unit

    Quote Originally Posted by trprph View Post
    I have had this split unit about 6 months and it has worked great. We had our first snow and ice this week and the residual remained on for about 5 days. There is no ice on the external unit. However, when I try to use the heat, the defrost light comes on and the fan outside blows but no air comes out on the inside. The defrost light will not go out.

    I am in need of some advise
    See if the system operates in cooling. If you get no duty in cooling then I would say you might be looking at a refrigerant issue. The defrost light is also a pre heat indication. It sounds as if the indoor coil is not getting up to temperature this could be either a sensor issue or refrigerant issue. If system works in cooling then you can eliminate refrigerant issue.

  11. #11
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Problem with LG split unit

    Quote Originally Posted by AbsoluteWDJ View Post
    See if the system operates in cooling. If you get no duty in cooling then I would say you might be looking at a refrigerant issue. The defrost light is also a pre heat indication. It sounds as if the indoor coil is not getting up to temperature this could be either a sensor issue or refrigerant issue. If system works in cooling then you can eliminate refrigerant issue.
    Can you feel if the coil is getting warm?

    Usually you can feel through the filter if its warm or not.

  12. #12
    Join Date
    Feb 2010
    Location
    US
    Posts
    12
    Rep Power
    0

    Re: Problem with LG split unit

    Quote Originally Posted by AbsoluteWDJ View Post
    See if the system operates in cooling. If you get no duty in cooling then I would say you might be looking at a refrigerant issue. The defrost light is also a pre heat indication. It sounds as if the indoor coil is not getting up to temperature this could be either a sensor issue or refrigerant issue. If system works in cooling then you can eliminate refrigerant issue.
    It does not appear to be cooling either. I took the top off of the unit outside and pressed a small button on the curcuit board and it makes the heat work, but it does not regulate the temerature.

    I do not know what's going on.

  13. #13
    Join Date
    Feb 2010
    Location
    US
    Posts
    12
    Rep Power
    0

    Re: Problem with LG split unit

    Quote Originally Posted by back2space View Post
    Can you feel if the coil is getting warm?

    Usually you can feel through the filter if its warm or not.
    I'll check and see

  14. #14
    Join Date
    Feb 2010
    Location
    US
    Posts
    12
    Rep Power
    0

    Re: Problem with LG split unit

    No. It's not warm. Will it get warm even if no air is coming out?

  15. #15
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Problem with LG split unit

    Quote Originally Posted by trprph View Post
    No. It's not warm. Will it get warm even if no air is coming out?
    Yes the coil should feel warm and air doesnt blow out straight away as it pre heats the coil so you dont feel cold draughts, if the coil isnt getting up to temperature then it will stop the fan blowing so the air doenst feel cold.

  16. #16
    Join Date
    Feb 2010
    Location
    US
    Posts
    12
    Rep Power
    0

    Re: Problem with LG split unit

    Quote Originally Posted by back2space View Post
    Yes the coil should feel warm and air doesnt blow out straight away as it pre heats the coil so you dont feel cold draughts, if the coil isnt getting up to temperature then it will stop the fan blowing so the air doenst feel cold.
    It definetly is not getting warm. The wierd thing is I pushed a button on the curcuit bourd on the outside unit and it blew hot air. I think I may be dealing with some type of sensor problem. What do you think?

    Is there a sensor on the inside unit coil?

  17. #17
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Problem with LG split unit

    Quote Originally Posted by trprph View Post
    It definetly is not getting warm. The wierd thing is I pushed a button on the curcuit bourd on the outside unit and it blew hot air. I think I may be dealing with some type of sensor problem. What do you think?

    Is there a sensor on the inside unit coil?
    There are several on the indoor coil and outdoor coil however may not be visible without taking the unit apart.

    Best to get someone in to check.

  18. #18
    Join Date
    Feb 2010
    Location
    US
    Posts
    12
    Rep Power
    0

    Re: Problem with LG split unit

    that's what I was trying to avoid because they are charging me a rediculous service and labor fee, but the part is free due to the warranty. go figure.

  19. #19
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Problem with LG split unit

    Quote Originally Posted by trprph View Post
    that's what I was trying to avoid because they are charging me a rediculous service and labor fee, but the part is free due to the warranty. go figure.
    Can you find someone else?

  20. #20
    Join Date
    Jun 2007
    Location
    Cyprus
    Age
    73
    Posts
    252
    Rep Power
    17

    Re: Problem with LG split unit

    Hi,

    Can you clarify what is happening. Your post is not making sense. On the one hand you are saying the coil isn't warm, and elsewhere you say that you pressed a button and it blew hot air?? Perhaps you meant the outdoor unit blew hot air ?.

    First test: Raise the indoor flap, remove the RH side filter and look for a small encapsulated thermistor set just off the coil fins. Turn the unit on to cooling, and hold the thermistor between finger and thumb. You may have to wait a few minutes... The indoor fan will come on of course, but we are trying to establish whether the unit will cool or not. I know you tried this before, but if the room temp is not warm enough cooling will not occur. hence the thermistor test. Let us know what you find, and clear up the blow hot air thing...

  21. #21
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Problem with LG split unit

    A split won't go on proper defrost for at least 40min operation.
    If it's indicating defrost before that, it either a) in pre heat mode and not moving from that mode due to lack of refrigerant, compressor or fan operation, or the reversing vale is not operating. or b) faulty control PCB or thermistors.

    edit eg if the indoor coil gets hot, but the fan doesn't start, it's either the indoor coil thermistor faulty or the gas charge is low due to leak (or compressor or rv fault) that the coil doesn't quite get hot enough to start the heating cycle.
    Last edited by paul_h; 07-02-2010 at 04:55 PM.

  22. #22
    Join Date
    Sep 2008
    Location
    Letsby Avenue
    Posts
    359
    Rep Power
    17

    Re: Problem with LG split unit

    Quote Originally Posted by back2space View Post
    You lose output on all the inverter units below 5C but the performance drop off is not very much.

    http://mylg.co.uk/data%20for%20site/...%20outdoor.pdf

    Page 60 you should look at.

    Its the capacity tables as the temp drops off, at different temps.
    Cheers,never paid enough attention to the figures,seems like roughly around a 20% drop off at -7c ish so it's better than I thought.can sell for heating with a little less worry now.

  23. #23
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Problem with LG split unit

    Quote Originally Posted by spimps View Post
    Cheers,never paid enough attention to the figures,seems like roughly around a 20% drop off at -7c ish so it's better than I thought.can sell for heating with a little less worry now.
    Your best off oversizing the system slightly to allow for the drop off.

  24. #24
    Join Date
    Feb 2010
    Location
    US
    Posts
    12
    Rep Power
    0

    Re: Problem with LG split unit

    Quote Originally Posted by fridge doctor View Post
    Hi,

    Can you clarify what is happening. Your post is not making sense. On the one hand you are saying the coil isn't warm, and elsewhere you say that you pressed a button and it blew hot air?? Perhaps you meant the outdoor unit blew hot air ?.

    First test: Raise the indoor flap, remove the RH side filter and look for a small encapsulated thermistor set just off the coil fins. Turn the unit on to cooling, and hold the thermistor between finger and thumb. You may have to wait a few minutes... The indoor fan will come on of course, but we are trying to establish whether the unit will cool or not. I know you tried this before, but if the room temp is not warm enough cooling will not occur. hence the thermistor test. Let us know what you find, and clear up the blow hot air thing...

    Ok. The unit will not blow hot air or cold air. While investigating the situation, I took the top cover off of the unit outside to have a look inside. I noticed a curciut board on the backside of the front of the unit (on the inside); it had a green and yellow lED light on it. I also saw a small square botton. I pushed the button and it caused the green red light to com on. Pushed it again and it caused the green light to come on and againg and both lights came on.

    After pushing it a few times and going back to the inside unit, I figured out that when I pushed it a few times; the heat would blow inside. The wierd thing is that the display on the inside unit will go off anf the air panel will shut, but the hot air continues to blow. I fugure it's some type of over-ride?

    Anyway, that's where I am at now. By the way, I did the first test you ask and got no cold air.

  25. #25
    Join Date
    Feb 2010
    Location
    US
    Posts
    12
    Rep Power
    0

    Re: Problem with LG split unit

    Correction: Green and Red LED light . Sorry.

  26. #26
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Problem with LG split unit

    Quote Originally Posted by trprph View Post
    Correction: Green and Red LED light . Sorry.
    Are the red/green lights flashing at all?

    http://mylg.co.uk/data%20for%20site/...%20_gh-km_.pdf

    Page 2 shows the fault codes on the outdoor unit if there is any.

  27. #27
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Problem with LG split unit

    Quote Originally Posted by AbsoluteWDJ View Post
    If system works in cooling then you can eliminate refrigerant issue.
    No you cannot! Since different volumes of parts involved when cooling or heating there is also different amount of refrigerant required, and therefore, that diagnostic method is inconclusive. Only certain way to determine correct refrigerant amount is by recover and weigh it.

  28. #28
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Problem with LG split unit

    Quote Originally Posted by trprph View Post
    that's what I was trying to avoid because they are charging me a rediculous service and labor fee, but the part is free due to the warranty. go figure.
    What a funny warranty!
    Did you got some discount when you bought that unit with that warranty.

    And, please stop pressing buttons without knowing what they mean and do. Imagine yourself in saw-mill and pressing every possible button.

  29. #29
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: Problem with LG split unit

    Quote Originally Posted by nike123 View Post
    No you cannot! Since different volumes of parts involved when cooling or heating there is also different amount of refrigerant required, and therefore, that diagnostic method is inconclusive. Only certain way to determine correct refrigerant amount is by recover and weigh it.

    I some how sense that the guy has no refrigerant recovery machine or scales Nike. I'm giving the guy ideas of what to check! I would also say if the end user can detect their unit cooling then there would be refrigerant within the system but maybe I'm wrong!

  30. #30
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Problem with LG split unit

    Quote Originally Posted by AbsoluteWDJ View Post
    I some how sense that the guy has no refrigerant recovery machine or scales Nike. I'm giving the guy ideas of what to check! I would also say if the end user can detect their unit cooling then there would be refrigerant within the system but maybe I'm wrong!
    No, you are not wrong in that part. But you are wrong in this:
    If system works in cooling then you can eliminate refrigerant issue.
    I only said that fact that unit is cooling doesn't mean that refrigerant amount is correct.

    Also, I did not said that HE should recover or weigh system.

  31. #31
    scott1's Avatar
    scott1 Guest

    Question Re: Problem with LG split unit

    I think you can contact to the store where you bought unit?? the

  32. #32
    Join Date
    Feb 2010
    Location
    US
    Posts
    12
    Rep Power
    0

    Re: Problem with LG split unit

    Finally working. It was a sensor on the outside blower. The voltage was off, hence it was reading the wrong temperature.

Similar Threads

  1. Installing pipework for single split unit
    By electro in forum Air Conditioning
    Replies: 51
    Last Post: 05-03-2009, 06:02 PM
  2. Lennox unit problem
    By marc5180 in forum Air Conditioning
    Replies: 35
    Last Post: 08-11-2008, 10:16 PM
  3. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  4. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM
  5. Replies: 3
    Last Post: 04-03-2007, 07:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •