    water expansion tank



    we usually install the expansion tank at return pipe of system pump. is there any concern if install at output of the pump?



  2. #2
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: water expansion tank

    Is it an expansion tank for a heating system . eg boiler ???
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: water expansion tank

    If it is an open vented system then ideally the tank should be connected at the neutral point as regards pressure.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Mar 2002
    Location
    San Francisco Bay Area
    Posts
    180
    Rep Power
    23

    Re: water expansion tank

    Quote Originally Posted by lc_shi
    we usually install the expansion tank at return pipe of system pump. is there any concern if install at output of the pump?
    The expansion tank provides a constant pressure point in the system. When operating, the pump pressure rise equals the total system pressure drop. If the expansion tank is placed at the pump intake, it provides a constant pressure at the pump suction and the pump pressure rise is added to the static value.

    If placed at the discharge of the pump, it will maintain its static value at that point and the pump suction presssure will drop in relation to the static value. The potential harm is in cavitation at the impeller due to low pressure. Cavitation damages impellers.

    Rog

  5. #5
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Smile Re: water expansion tank

    professional answer! very good. thx indeed.

  6. #6
    shogun7's Avatar
    shogun7 Guest

    Re: water expansion tank

    Quote Originally Posted by RogGoetsch
    The expansion tank provides a constant pressure point in the system. When operating, the pump pressure rise equals the total system pressure drop. If the expansion tank is placed at the pump intake, it provides a constant pressure at the pump suction and the pump pressure rise is added to the static value.


    Rog
    This is also known as the point of no pressure change

Similar Threads

  1. design of expansion tank
    By scherif in forum Technical Discussions
    Replies: 8
    Last Post: 24-08-2010, 11:24 PM
  2. open cycle R718 A/C that also provides high purity water?
    By star882 in forum Technical Speculations
    Replies: 7
    Last Post: 27-07-2006, 04:18 AM
  3. expansion water tank sizing program
    By Lc_shi in forum Fundamentals
    Replies: 0
    Last Post: 01-09-2005, 04:24 AM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  5. chilled water storage tank!
    By dchatta in forum Technical Discussions
    Replies: 4
    Last Post: 24-05-2004, 04:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •