    Oh, myVRV3 system down to 21 C when i setup 23 inremote ???

    please help me !!!
    i try best but can not fix it !!!
    My friends , could you help me ???
    Please,
    Thank you a lot !!!

  2. #2
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Oh, myVRV3 system down to 21 C when i setup 23 inremote ???

    Quote Originally Posted by vietvho View Post
    please help me !!!
    i try best but can not fix it !!!
    My friends , could you help me ???
    Please,
    Thank you a lot !!!
    Need more information. Are you in heating mode or cooling mode? How many indoor units are having this problem? What are the model numbers of the indoor units that are having this problem? Are you using the temp sensor in the remote or in the indoor unit? Do you have separate remote temp sensors?

  3. #3
    Join Date
    Jan 2010
    Location
    Viet Nam
    Posts
    18
    Rep Power
    0

    thank

    I setup it in cooling mode !!! (23 degree) but it down to 20-21 stil do'nt stop !!! i don't remember model of it !!! but it is VRV3 system ,indoor unit is duct type !!!
    Thank You a lot !!! my friend

  4. #4
    Join Date
    Jan 2010
    Location
    Viet Nam
    Posts
    18
    Rep Power
    0

    thank

    i try to setup in both (enable,disable sensor of remote controller) . and finish in fally hic..hic..hic

  5. #5
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: thank

    Quote Originally Posted by vietvho View Post
    I setup it in cooling mode !!! (23 degree) but it down to 20-21 stil do'nt stop !!! i don't remember model of it !!! but it is VRV3 system ,indoor unit is duct type !!!
    Thank You a lot !!! my friend

    There are a number of things that can cause this.

    Is this the only indoor unit?

    Are there other indoor units continuing to run?

    Is the remote controller only controlling this one unit?

    How many remote controllers are there?

    Do you have remote sensors?

    Is the remote controller in the room where the air is being supplied or is it in an area that is warmer?

    Is the return air duct (air that is being drawn from the room into the ducted unit to be cooled) pulling warm air into the indoor unit? Is the return air duct insulated so as the air inside the duct does not get warm from the outside the duct?

    Need answers to each question to help you.

  6. #6
    Join Date
    Feb 2008
    Location
    england
    Posts
    502
    Rep Power
    21

    Re: Oh, myVRV3 system down to 21 C when i setup 23 inremote ???

    with ducted units it is best ot fit remote air sensors to control the room temp and not the space where the indoor unit is as the temp may not be the same as the room

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Oh, myVRV3 system down to 21 C when i setup 23 inremote ???

    Isn't it surprising how many designers/installers leave a free back return on ducted fan coils and then expect the system to operate correctly....

  8. #8
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Oh, myVRV3 system down to 21 C when i setup 23 inremote ???

    Quote Originally Posted by frank View Post
    Isn't it surprising how many designers/installers leave a free back return on ducted fan coils and then expect the system to operate correctly....
    That is exactly what I thought might be happening with this one.

  9. #9
    Join Date
    Jan 2010
    Location
    Viet Nam
    Posts
    18
    Rep Power
    0

    Thank you for you repply !!!

    I tested with your advice and saw that all were correct !!!
    But the temp still count down !!!
    I try to set up code : 10-3-1 and then it work correctly until now (i still worry , because it work correct before )
    Thank all my friends for your kind !!!
    I will up more information of this problem if it have !!!
    Thank you and best wish !!!
    Hope for Sustainable development !!!

  10. #10
    Join Date
    Jan 2010
    Location
    Viet Nam
    Posts
    18
    Rep Power
    0

    Problem

    The time still down until 20(set up is 23degC) to turn off . when it turn off ,I check temp : return air 23
    temp of room 20 .
    I think the return air must higher than supply air ?OK ?
    so why it stop at 23 degC of return air ?what is error ? can i setting to change this value ?
    Thank My Friends !!!
    Best Regard !!!

Similar Threads

  1. Ammonia Heat Pumps
    By US Iceman in forum New Technologies
    Replies: 39
    Last Post: 22-03-2010, 06:36 PM
  2. Enthalpy Increasing Buffer System
    By Reflexive in forum Technical Speculations
    Replies: 3
    Last Post: 23-12-2008, 03:18 PM
  3. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  4. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 03:42 PM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •