    evening all, just to cut a long story short i am refiitting an indoor unit which has had a leak repaired to a vrv system which is back up and running. basically i havent got the model details to hand but its a vrv with expansion unit added! (extra condenser) on R407c! i was hoping to pump as much gas back as possible into the outdoor but how much do you think it can hold until i have to reclaim. system holds 30kg in total, and from what i remember the factory charge was 15kg! any help greatly appreciated!!



  2. #2
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: daikin vrv pumpdown!

    Hi Bigrac,

    Sounds like a K series, you will have to disconnect a solenoid valve whilst the system is running otherwise it will never pumpdown, can't remember if its Y1S or Y3S , if I were you I would abandon the pumpdown idea, put the unit into refrigerant recovery mode and reclaim all of the refrigerant. You can also verify the system charge as well.

    Cheers
    Tutto il Mondo e un Paese

  3. #3
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: daikin vrv pumpdown!

    Quote Originally Posted by El Padre View Post
    Hi Bigrac,

    Sounds like a K series, you will have to disconnect a solenoid valve whilst the system is running otherwise it will never pumpdown, can't remember if its Y1S or Y3S , if I were you I would abandon the pumpdown idea, put the unit into refrigerant recovery mode and reclaim all of the refrigerant. You can also verify the system charge as well.

    Cheers
    Hi Bigrac
    El Padre is right there's always a hot gas bypass to avoid low pressure at the suction of the compressor... let's say these kind of scroll compressor "do not like" a low pressure below 3 bars, you could lead it down to earth..
    AFAIK there's no recovery mode with a K series coupled with an extra condensor...
    rgds
    cool#9

  4. #4
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: daikin vrv pumpdown!

    i would not be pumping the unit down if you have additional charge in it.
    How much additional charge do you have?

  5. #5
    Join Date
    Nov 2008
    Location
    north west
    Posts
    13
    Rep Power
    0

    Re: daikin vrv pumpdown!

    cheers for the response guys. i went down your root and decanted the full charge.
    i was just clutching at straws hoping i could work around it, as i basically had a 2 hour window to empty the pipes if i wanted to finish same day, due to accessability! (restaurant). as you say aswell, atleast i know the charge is still correct- so no more leaks on the system. strange though that i found 2 indoor coils to have leaks on in near enough the same places. had to cut into the coils to repair as coils/ and or complete indoor units now obsolete and none on shelf. just happy to have this one done with. oh well... keeps me out of freezers
    cheers

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Panasonic Urban rebadged Daikin
    By complete HVAC in forum Air Conditioning
    Replies: 0
    Last Post: 19-08-2009, 04:35 PM
  3. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  4. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  5. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •