27-01-2010, 05:32 PM #1
daikin vrv pumpdown!
evening all, just to cut a long story short i am refiitting an indoor unit which has had a leak repaired to a vrv system which is back up and running. basically i havent got the model details to hand but its a vrv with expansion unit added! (extra condenser) on R407c! i was hoping to pump as much gas back as possible into the outdoor but how much do you think it can hold until i have to reclaim. system holds 30kg in total, and from what i remember the factory charge was 15kg! any help greatly appreciated!!
-
27-01-2010, 06:06 PM #2
Re: daikin vrv pumpdown!
Hi Bigrac,
Sounds like a K series, you will have to disconnect a solenoid valve whilst the system is running otherwise it will never pumpdown, can't remember if its Y1S or Y3S , if I were you I would abandon the pumpdown idea, put the unit into refrigerant recovery mode and reclaim all of the refrigerant. You can also verify the system charge as well.
CheersTutto il Mondo e un Paese
-
27-01-2010, 08:01 PM #3
Re: daikin vrv pumpdown!
Hi Bigrac
El Padre is right there's always a hot gas bypass to avoid low pressure at the suction of the compressor... let's say these kind of scroll compressor "do not like" a low pressure below 3 bars, you could lead it down to earth..
AFAIK there's no recovery mode with a K series coupled with an extra condensor...
rgds
cool#9
-
28-01-2010, 11:30 PM #4
Re: daikin vrv pumpdown!
i would not be pumping the unit down if you have additional charge in it.
How much additional charge do you have?
-
01-02-2010, 07:28 PM #5
Re: daikin vrv pumpdown!
cheers for the response guys. i went down your root and decanted the full charge.
i was just clutching at straws hoping i could work around it, as i basically had a 2 hour window to empty the pipes if i wanted to finish same day, due to accessability! (restaurant). as you say aswell, atleast i know the charge is still correct- so no more leaks on the system. strange though that i found 2 indoor coils to have leaks on in near enough the same places. had to cut into the coils to repair as coils/ and or complete indoor units now obsolete and none on shelf. just happy to have this one done with. oh well... keeps me out of freezers
cheers
Similar Threads
-
Daikin not working... many problems
By stankovicv in forum Air ConditioningReplies: 26Last Post: 11-12-2010, 09:01 AM -
Panasonic Urban rebadged Daikin
By complete HVAC in forum Air ConditioningReplies: 0Last Post: 19-08-2009, 04:35 PM -
Daikin AC parts from UK
By skel00 in forum Air ConditioningReplies: 5Last Post: 05-04-2009, 01:24 PM -
Fixing Daikin A3 Error
By Stuffy in forum Air ConditioningReplies: 3Last Post: 27-03-2009, 06:02 AM -
Daikin Comp and inverter
By WCC73 in forum Air ConditioningReplies: 5Last Post: 08-11-2008, 08:44 PM