    Carrier Help Please



    Hi there,

    I hope somebody can help me. I was called to look at a carrier ac that was not responding to remote control. But if you pressed the test or emergency buttons it would start and run fine. I have found that there is a constant red flashing LED on the PCB of the indoor. I tried replaceing the IR circuit board but that has not helped. Next I shall try the Main PCB. Now I have a second Carrier Ac doing the same thing at another location. Can somebody please help me?



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Carrier Help Please

    Change the battery in the remote might help. They don't last forever.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Carrier Help Please

    Model number ?

    If I remember my limited Carrier indoor knowledge they can do that a lot without much help from the manuals.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Advical's Avatar
    Advical Guest

    Re: Carrier Help Please

    The Model is a 42g150hp (53g150hp) if that helps. I cannot find any manuals on it. Thanks for the reply.

  5. #5
    Advical's Avatar
    Advical Guest

    Re: Carrier Help Please

    Changing the battery was the first thing I did. No joy there. I wish it was that simple.

  6. #6
    Bunyamyn's Avatar
    Bunyamyn Guest

    Re: Carrier Help Please

    We have Carrier chillers Model: 30RA-200-BO244-PEE, supplied from M/s Carrier Africa. The problem is water penetrated to cooling circuit from evaporator(heat exchanger) recently 2 chiller units were malfunctioned due to same course. So, some please help me for assist to solve this problem. In Maldives Chiller systems having same problem, previously used RC chiller (Italy) as the happened I mentioned.
    What are the factors I have to check?

  7. #7
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Carrier Help Please

    Quote Originally Posted by Bunyamyn View Post
    We have Carrier chillers Model: 30RA-200-BO244-PEE, supplied from M/s Carrier Africa. The problem is water penetrated to cooling circuit from evaporator(heat exchanger) recently 2 chiller units were malfunctioned due to same course. So, some please help me for assist to solve this problem. In Maldives Chiller systems having same problem, previously used RC chiller (Italy) as the happened I mentioned.
    What are the factors I have to check?

    Have you checked the tubes for leaks its sounds as if it has frozen up and burst the tubes, and check the safety switches

    Toosh
    My wife used to say you never listen to a word I say at least I think that what she said

  8. #8
    Bunyamyn's Avatar
    Bunyamyn Guest

    Re: Carrier Help Please

    its hard to find leak, becouse totally sealed the heat exchanger,there is noway to check for leak inside it.only we noticed system low pressure dropping & shutdown the cooling circuit

  9. #9
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Carrier Help Please

    Quote Originally Posted by Bunyamyn View Post
    its hard to find leak, becouse totally sealed the heat exchanger,there is noway to check for leak inside it.only we noticed system low pressure dropping & shutdown the cooling circuit
    Does the refrigerant flow through the tubes. you will need to remove the insulation to get to the end plate. Also with this happening before it sounds like a water flow problem.
    But not being there its hard to diagnose

    Toosh
    My wife used to say you never listen to a word I say at least I think that what she said

  10. #10
    Join Date
    Jan 2009
    Location
    Athnes Greece
    Age
    43
    Posts
    9
    Rep Power
    0

    Re: Carrier Help Please

    If pressure drops suddenly doesn't necessary means the RA has a broken evaporator.You should check the filter and also the sight-glass. Then if it froze up i think then you can do nothing about it.

  11. #11
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Carrier Help Please

    Quote Originally Posted by Bunyamyn View Post
    its hard to find leak, becouse totally sealed the heat exchanger,there is noway to check for leak inside it.only we noticed system low pressure dropping & shutdown the cooling circuit
    Well how do you know its moisture has the compressor oil changed colour. if it is a murky creamy colour then its moisture

    Toosh
    My wife used to say you never listen to a word I say at least I think that what she said

  12. #12
    Bunyamyn's Avatar
    Bunyamyn Guest

    Re: Carrier Help Please

    4 chiller units breakdown of evaporator cracked & water penetrated to refrigerant (gas)circuit.
    havent noticed any problem from hydraunic module.
    the water we are using is desalinated,but its not acidic.
    All Ineed to know motive of this issue.
    whether it might acourse of water camistry?
    In maldidives we having bad experience of using chiller system.

  13. #13
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Carrier Help Please

    Quote Originally Posted by Bunyamyn View Post
    4 chiller units breakdown of evaporator cracked & water penetrated to refrigerant (gas)circuit.
    havent noticed any problem from hydraunic module.
    the water we are using is desalinated,but its not acidic.
    All Ineed to know motive of this issue.
    whether it might acourse of water camistry?
    In maldidives we having bad experience of using chiller system.
    HI In Saudi Arabia we used desalinated water on over 60 large centrifugal chillers with no problems, I think you will need to cut open chiller to find exact cause then go from there.

    Toosh
    My wife used to say you never listen to a word I say at least I think that what she said

  14. #14
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Carrier Help Please

    Hi again Have you had an analysis of the water to see if there is a reaction between the copper and steel in in the evaporator, also you may have to use water treatment in the chilled water

    Toosh
    My wife used to say you never listen to a word I say at least I think that what she said

  15. #15
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Carrier Help Please

    Quote Originally Posted by Bunyamyn View Post
    4 chiller units breakdown of evaporator cracked & water penetrated to refrigerant (gas)circuit.
    havent noticed any problem from hydraunic module.
    the water we are using is desalinated,but its not acidic.
    All Ineed to know motive of this issue.
    whether it might acourse of water camistry?
    In maldidives we having bad experience of using chiller system.
    Hi You mention the evaporator cracked can you be more specific on where it cracked

    Toosh
    My wife used to say you never listen to a word I say at least I think that what she said

  16. #16
    Bunyamyn's Avatar
    Bunyamyn Guest

    Re: Carrier Help Please

    Quote Originally Posted by Toosh View Post
    Hi You mention the evaporator cracked can you be more specific on where it cracked

    Toosh
    I have seen just edgs of the evaporator gas coil a crack, the part which was coonnected distributer plate.

  17. #17
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Carrier Help Please

    Quote Originally Posted by Bunyamyn View Post
    I have seen just edgs of the evaporator gas coil a crack, the part which was coonnected distributer plate.
    Im confused is this a shell and tube evaporator with the refrigerant flowing through the tubes
    My wife used to say you never listen to a word I say at least I think that what she said

  18. #18
    Join Date
    Mar 2009
    Location
    Jersey
    Posts
    6
    Rep Power
    0

    Re: Carrier Help Please

    Quote Originally Posted by Advical View Post
    Changing the battery was the first thing I did. No joy there. I wish it was that simple.
    To test infra red controllers point it at the lens of ya camera on mobile phone, press any button whilst looking at phone screen and you should see light flashing on the controller

  19. #19
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Carrier Help Please

    Quote Originally Posted by Advical View Post
    Hi there,

    I hope somebody can help me. I was called to look at a carrier ac that was not responding to remote control. But if you pressed the test or emergency buttons it would start and run fine. I have found that there is a constant red flashing LED on the PCB of the indoor. I tried replaceing the IR circuit board but that has not helped. Next I shall try the Main PCB. Now I have a second Carrier Ac doing the same thing at another location. Can somebody please help me?
    Need to change the main PCB. I've never had a lot of luck repairing these things otherwise.
    I learnt a few things here from nike about recievers and capacitors, those tricks work fine with mits and fujitsu units (solder in a new capacitor, and then a new reciever)
    But with LG/kelvinator and carrier (which don't have a capacitor in the reciever circuit, and nothing stands out on the main PCB as the capacitor for the remote), you just have to change the main PCB.

    I carry a soldering iron around and use it as much as I do my gauges these days. Fuji ducted with the solid state relay, stuff paying $100 for the PCB, the sharp relay is $16. Shorted diode bridge in a fuji? $6.
    Breezair evap cooler not working, probably just the $8 TRIAC, stuff paying $400 for a whole new control system. ( A company called tekelec makes most of the PCBs for all different evap coolers here, try looking up www.tekelek.com.au they don't want to talk to anyone, too busy making control systems in europe and the USA to bother providing service here, and all the evap cooler maunfacturers keep selling "upgrades" of tekeleks inferior stuff to the new model, meaning huge expense for a simple PCB fault in an evap cooler, the PCBs seriously have like 4 components in them for fan speed control, and they charge $400 for a wall control or wireless remote control, prices that worldwide refrigeration split systems would be ashamed off. I wish I knew an electronics guru to take those PCBs to pieces and get rid of the tekelek scam.).

    But anyway, what I'm saying is that even though I do stuff around changing components on PCBs, I've never got a carrier a/c which is not recieving the remote signal working buy changing the IR sensor or capacitors. Getting them to work without changing the main PCB is above my knowledge.

    edit:
    Also, heres a tip, buy a universal remote to carry around and test with, if it doesn't work with that, the main PCB needs replacing. The best/cheapest universal remote are from www.dealextreme.com
    these ones http://www.dealextreme.com/details.dx/sku.14835 are US$7 (shipping is free but takes 3 weeks)and have louvre swing and backlight unlike the rest. Those remotes even work with the really old sliding switches in daikin/fuji a/cs out there, so I've bought heaps to sell to customers with really old gear they want to fix cheap.
    Last edited by paul_h; 12-03-2010 at 02:16 PM.

  20. #20
    ivan1974's Avatar
    ivan1974 Guest

    Re: Carrier Help Please

    Have you checked "flow switch"? If there is an issue with flow switch it is possible for water freezing. Except continiously flashing of RED light on the PCB do have any alarms on the PRO-Dialog?

  21. #21
    Join Date
    Feb 2010
    Location
    uae
    Age
    48
    Posts
    39
    Rep Power
    0

    Re: Carrier Help Please

    r u people talking of chillers or split units? its so confusing, 1 question at a time please

  22. #22
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Carrier Help Please

    Quote Originally Posted by muju View Post
    r u people talking of chillers or split units? its so confusing, 1 question at a time please

    This arises when someone jumps into a thread and not starting a new one
    My wife used to say you never listen to a word I say at least I think that what she said

  23. #23
    Join Date
    Jan 2010
    Location
    australia
    Age
    39
    Posts
    32
    Rep Power
    0

    Re: Carrier Help Please

    remember there can be dipswitch s where batteries r for remote control i think most carrier splits have this feature a and b dipswitch by memory sometimes when changing batteries etc this setting can be changed stopping signal getting to reciever on indoor unit more than likely though sounds like main pcb

  24. #24
    Join Date
    Jun 2007
    Location
    Australia
    Posts
    8
    Rep Power
    0

    Re: Carrier Help Please

    Advical,
    If you follow the below link, it will take you to the service manual for this unit. The manual has a different model, but it is the same unit (they are re-model numbered overseas).
    eto.carrier.com/litterature/Service_Manuals/AEM001E1.pdf
    Remeber to put http in front. I am unable to do this, not enough posts.
    Regards
    Mat

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Carrier Chillers
    By Ed Burris in forum Technical Discussions
    Replies: 6
    Last Post: 27-03-2010, 02:00 AM
  3. Geoff in NY ~ Carrier Parts
    By Futsal1st in forum Trouble Shooting
    Replies: 6
    Last Post: 30-12-2009, 04:07 AM
  4. Help identifying carrier HiWall dom. split
    By paul_h in forum Air Conditioning
    Replies: 4
    Last Post: 12-12-2008, 09:12 AM
  5. carrier remote
    By superswill in forum Trouble Shooting
    Replies: 2
    Last Post: 26-04-2006, 09:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •