18-01-2010, 07:18 PM #1
dakin repairs
hi can anybody help I am working on a dakin split and the fault code is E 0 which I know means outdoor activation of outdoor saftey device what does this mean what should I be looking at
many thanks
matt shaw
-
18-01-2010, 07:33 PM #2
Re: dakin repairs
Unit is tripping on High pressure switch or Low pressure switch.
Connect your gauges to find out which and go from there.The difference between genius and stupidity is that genius has its limits.
Marc
-
18-01-2010, 07:46 PM #3
Re: dakin repairs
As Marc said HP or LP. condenser fans ok, condenser coil blocked, refrigerant leak. These would be most common but could be other reasons
-
18-01-2010, 08:12 PM #4
Re: dakin repairs
Hi,
What’s the unit model number? The safety devices that can cause an E0 error depends on the unit.
LP will not cause an E0 error.
Possible causes:
1/ Compressor contactor overload
2/ Condenser fan motor klixon
3/ Instantaneous power failure
4/ abnormally high discharge temp
5/ Activation of compressor internal safety (RY71/100)
6/ Loose pcb plug connection.
7/ Faulty outdoor pcb.
-
18-01-2010, 08:13 PM #5
Re: dakin repairs
Got to disagree guys.
On the older units, Lp & Hp trips generate their own fault codes.
E0 error codes are generated when the protection devices for the compressor or condenser fan(s) activate (thermistors etc embedded in the windings)
When you look at the outdoor unit, follow the electrical path of the wiring on the GREY wires coming from the outdoor PCB
-
19-01-2010, 05:00 PM #6
Re: dakin repairs
thanks lads im going to the job 2moz so i will let you know i have got a lot to look at then.
-
19-01-2010, 07:28 PM #7
Re: dakin repairs
if I follow the grey wires then what how do I rectifie the problem if the thermisters are holding the compressor or evap fan how do I reset them etc
-
19-01-2010, 07:31 PM #8
Re: dakin repairs
If you can measure 240v going out on one grey wire and coming back on the other then you have continuity through the compressor or fan motor, which ever the case may be. If you measure 240v on one grey wire but not coming back on the other then the motor protection has gone open circuit.
How experienced are you in electrical testing?
-
22-01-2010, 10:24 AM #9
Re: dakin repairs
Hate to disagree guys but i've been called out to a Daikin split tripping on "E0" "safety devices activated" 2001 model on R22
Tracing through the wiring diagram the safety devices connected are
1) High pressure switch
2)Thermo switch for condensor fans
3)over current relay for comp.
Connected my gauges and found the LP at 0 Bar so the unit was tripping on compressor overcurrent
So an LP fault must be able to cause a safety device activation.The difference between genius and stupidity is that genius has its limits.
Marc
-
22-01-2010, 12:56 PM #10
Re: dakin repairs
I take it you’re referring to a R(Y)71~125FJ unit.
Tracing through the wiring diagram the safety devices connected are
1) High pressure switch – Yes the HP switch is wired in series with other safeties but if you look closely at the wiring diagram you will see that the HP is the last device and is the only one connected to safety device input 2. This allows the unit to detect an E0 or E3 error. HP trip will not display an E0 error
IE.
Comp o/c or fan klixon trip – power is lost to safety device input 1&2 = E0 error
HP trip – power is lost safety device input 2 only = E3 error
2)Thermo switch for condensor fans – This will display an E0 as per above & previous post
3)over current relay for comp
Connected my gauges and found the LP at 0 Bar so the unit was tripping on compressor overcurrent.
This is the compressor contactor overload which will only trip when compressor draws excessive current (amps) and has nothing to do with an LP trip.
So an LP fault must be able to cause a safety device activation.
If you have a shortage of refrigerant the compressor and discharge temps will obviously increase resulting in abnormally high discharge temp which can cause E0 error as per my previous post.
This would be the reason your unit tripped on E0, but i suspect if you had checked the fault history you would also have found previous F3 or E4 errors .Last edited by VRVIII; 22-01-2010 at 02:13 PM.
Similar Threads
-
dakin e3 code
By coolflow in forum Air ConditioningReplies: 2Last Post: 19-07-2008, 09:24 AM -
Dakin Download
By superswill in forum Trouble ShootingReplies: 9Last Post: 14-06-2007, 10:04 PM -
tool repairs
By acgibo in forum Tools and CalculatorsReplies: 0Last Post: 28-06-2006, 09:49 PM -
dakin controller
By mike live in forum Air ConditioningReplies: 5Last Post: 27-06-2006, 08:12 PM -
York process chiller repairs
By Matt in forum CommercialReplies: 5Last Post: 23-03-2004, 11:07 PM