    dakin repairs



    hi can anybody help I am working on a dakin split and the fault code is E 0 which I know means outdoor activation of outdoor saftey device what does this mean what should I be looking at

    many thanks

    matt shaw



  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: dakin repairs

    Unit is tripping on High pressure switch or Low pressure switch.

    Connect your gauges to find out which and go from there.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  3. #3
    Join Date
    Sep 2009
    Location
    england
    Posts
    10
    Rep Power
    0

    Re: dakin repairs

    As Marc said HP or LP. condenser fans ok, condenser coil blocked, refrigerant leak. These would be most common but could be other reasons

  4. #4
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: dakin repairs

    Quote Originally Posted by shawy1 View Post
    hi can anybody help I am working on a dakin split and the fault code is E 0 which I know means outdoor activation of outdoor saftey device what does this mean what should I be looking at

    many thanks

    matt shaw
    Hi,

    What’s the unit model number? The safety devices that can cause an E0 error depends on the unit.

    LP will not cause an E0 error.

    Possible causes:
    1/ Compressor contactor overload
    2/ Condenser fan motor klixon
    3/ Instantaneous power failure
    4/ abnormally high discharge temp
    5/ Activation of compressor internal safety (RY71/100)
    6/ Loose pcb plug connection.
    7/ Faulty outdoor pcb.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: dakin repairs

    Got to disagree guys.

    On the older units, Lp & Hp trips generate their own fault codes.

    E0 error codes are generated when the protection devices for the compressor or condenser fan(s) activate (thermistors etc embedded in the windings)

    When you look at the outdoor unit, follow the electrical path of the wiring on the GREY wires coming from the outdoor PCB

  6. #6
    Join Date
    Jan 2010
    Location
    england
    Posts
    5
    Rep Power
    0

    Re: dakin repairs

    thanks lads im going to the job 2moz so i will let you know i have got a lot to look at then.

  7. #7
    Join Date
    Jan 2010
    Location
    england
    Posts
    5
    Rep Power
    0

    Re: dakin repairs

    if I follow the grey wires then what how do I rectifie the problem if the thermisters are holding the compressor or evap fan how do I reset them etc

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: dakin repairs

    If you can measure 240v going out on one grey wire and coming back on the other then you have continuity through the compressor or fan motor, which ever the case may be. If you measure 240v on one grey wire but not coming back on the other then the motor protection has gone open circuit.

    How experienced are you in electrical testing?

  9. #9
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: dakin repairs

    Hate to disagree guys but i've been called out to a Daikin split tripping on "E0" "safety devices activated" 2001 model on R22

    Tracing through the wiring diagram the safety devices connected are
    1) High pressure switch
    2)Thermo switch for condensor fans
    3)over current relay for comp.

    Connected my gauges and found the LP at 0 Bar so the unit was tripping on compressor overcurrent

    So an LP fault must be able to cause a safety device activation.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  10. #10
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: dakin repairs

    Quote Originally Posted by VRVIII View Post
    Hi,

    What’s the unit model number? The safety devices that can cause an E0 error depends on the unit.

    LP will not cause an E0 error.

    Possible causes:
    1/ Compressor contactor overload
    2/ Condenser fan motor klixon
    3/ Instantaneous power failure
    4/ abnormally high discharge temp
    5/ Activation of compressor internal safety (RY71/100)
    6/ Loose pcb plug connection.
    7/ Faulty outdoor pcb.
    Quote Originally Posted by marc5180 View Post
    Hate to disagree guys but i've been called out to a Daikin split tripping on "E0" "safety devices activated" 2001 model on R22
    I take it you’re referring to a R(Y)71~125FJ unit.

    Tracing through the wiring diagram the safety devices connected are
    1) High pressure switch – Yes the HP switch is wired in series with other safeties but if you look closely at the wiring diagram you will see that the HP is the last device and is the only one connected to safety device input 2. This allows the unit to detect an E0 or E3 error. HP trip will not display an E0 error
    IE.
    Comp o/c or fan klixon trip – power is lost to safety device input 1&2 = E0 error
    HP trip – power is lost safety device input 2 only = E3 error

    2)Thermo switch for condensor fans – This will display an E0 as per above & previous post

    3)over current relay for comp
    Connected my gauges and found the LP at 0 Bar so the unit was tripping on compressor overcurrent.
    This is the compressor contactor overload which will only trip when compressor draws excessive current (amps) and has nothing to do with an LP trip.

    So an LP fault must be able to cause a safety device activation.
    If you have a shortage of refrigerant the compressor and discharge temps will obviously increase resulting in abnormally high discharge temp which can cause E0 error as per my previous post.
    This would be the reason your unit tripped on E0, but i suspect if you had checked the fault history you would also have found previous F3 or E4 errors .
    Last edited by VRVIII; 22-01-2010 at 02:13 PM.

Similar Threads

  1. dakin e3 code
    By coolflow in forum Air Conditioning
    Replies: 2
    Last Post: 19-07-2008, 09:24 AM
  2. Dakin Download
    By superswill in forum Trouble Shooting
    Replies: 9
    Last Post: 14-06-2007, 10:04 PM
  3. tool repairs
    By acgibo in forum Tools and Calculators
    Replies: 0
    Last Post: 28-06-2006, 09:49 PM
  4. dakin controller
    By mike live in forum Air Conditioning
    Replies: 5
    Last Post: 27-06-2006, 08:12 PM
  5. York process chiller repairs
    By Matt in forum Commercial
    Replies: 5
    Last Post: 23-03-2004, 11:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •