    Copeland 9RB oil level

    Hey, unfortunately i am by on my own where i i work and am the only hvac tech here. I hope someone could halp me out with this copeland compressor i got. I am running a chamber with this model comp using r-12 it came pre filled with oil as most do. it was at half level, i charged the system. For further info the original motor burnt out due to acid i flushed the system changed the oil separator, and changed all pressure switches. put new comp in and pumped down. i ran the system overnight ast 86+ uncontrolled humidity just so i could focus on the charge without controlling de-humidity system. When charging system i started charging first with liquid isolated comp so not to floodback ref into comp and then continued with gas after, like i said i came in this morning to the sight glass for the oil.. bubbling, the oil pressure at the crank case was fluctuating from 55 to 65psig. i shut down comp. but doesnt that mean either the oil is over filled or there is a floodback into compressor?
    P.S. the oil pressure diff switch did trip set for 10 psi

  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Copeland 9RB oil level

    soundes like liquid flood back ,or wrong oil vicosity,u might also check your direction of rotation this should not be a problem but all dependes.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. R290 Suction Scrubber HI Level
    By Knappyfro in forum Trouble Shooting
    Replies: 1
    Last Post: 28-11-2009, 05:15 PM
  2. "Unstable" Rack Receiver Liquid Level
    By chweber in forum Commercial
    Replies: 3
    Last Post: 09-02-2009, 08:58 AM
  3. Risk in high compressor oil level?
    By Ice Queen in forum Trouble Shooting
    Replies: 0
    Last Post: 20-05-2008, 02:28 PM
  4. Oil level control question
    By racknovice in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 06-09-2007, 09:29 PM
  5. liquid receiver low level alarm
    By racknovice in forum Supermarket Refrigeration
    Replies: 8
    Last Post: 18-08-2007, 06:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •