    GSHP discharge temp high



    one GSHP made by four compressors and two plate exchangers:
    structure:
    comp#1&2 parellel with plate HX #1
    comp#3&4 parellel with plate HX #2

    the norm suction pressure and the discharge pressure is 3/20bar. The comp #4 's discharge pressure reach 21bar and the temp is 120C . I dont know what's the reason.
    the comp is copeland scroll.
    pls advice.



  2. #2
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    193
    Rep Power
    20

    Re: GSHP discharge temp high

    excuse my ignorance what is GSHP and what is the nature of the problem??

  3. #3
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: GSHP discharge temp high

    Can you please specify the problem and give symptoms so we can help
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: GSHP discharge temp high

    Is the GSHP a DX unit or secondary coolant?
    Heating side: air or water Lc?
    High pressures can only come from non condensables and/or perhaps a sudden lack of usefull condenser area.
    But that did you knew already.
    Was it OK in the past? Is there perhaps a NRV in the discharge between the 2 parallel compressors which wont open enough anymore?
    Last edited by Peter_1; 20-01-2005 at 07:01 AM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: GSHP discharge temp high

    Quote Originally Posted by bill1983
    excuse my ignorance what is GSHP and what is the nature of the problem??
    Ground source heat pump.
    Even 20 bar under normal conditions seems not high but very high. There must be a low COP and I assume this wasn't the meaning of installing a GSHP. You certainly have to reach a COP of 4,measured compressor-side.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Nov 2004
    Location
    perth australia
    Age
    77
    Posts
    14
    Rep Power
    0

    Re: GSHP discharge temp high

    HI GUY'S
    Have you or any one else put gas in the system latley, sounds like you have a ****tail gas in the system.
    also has the compressor got an internal releif valve?, at that head you could could be recirculating the gas internally within the compressor giving you a very high discharge temp.
    Reg's Tony.

  7. #7
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Smile Re: GSHP discharge temp high

    all of your ideas are appreciated.
    now the actual situation is : changed the compressor and redo evacuating. The system is still occur this problem while all four compressor in work. Doubt it's related the ground heat exchanger capacity not matched well or deteriorated. it's still in check. Will update later.

Similar Threads

  1. High Temp Heat Pumps
    By US Iceman in forum Heat Pumps
    Replies: 68
    Last Post: 29-05-2011, 05:19 PM
  2. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Replies: 7
    Last Post: 25-04-2010, 07:43 PM
  3. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Replies: 111
    Last Post: 13-04-2010, 08:58 PM
  4. R406a for high temp heat pump
    By Lc_shi in forum Refrigerants
    Replies: 1
    Last Post: 14-10-2005, 09:08 PM
  5. Disharge temp
    By reggie in forum Fundamentals
    Replies: 4
    Last Post: 12-09-2002, 05:41 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •