    nitro purgin



    All the manufactors ask us to nitro purge there pipe work but none give us any flow rates for doing this?? I was told as long as you can feel the nitro comeing out the end of the pipe with the back of your hand that ok.Now that seems a bit old hat doing it like that so does anyone have more info on this ???



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: nitro purgin

    Quote Originally Posted by cooltools View Post
    All the manufactors ask us to nitro purge there pipe work but none give us any flow rates for doing this?? I was told as long as you can feel the nitro comeing out the end of the pipe with the back of your hand that ok.Now that seems a bit old hat doing it like that so does anyone have more info on this ???

    Uless you have a flow rate valve how would you
    measure the flow anyway.
    The acctual rate is 2 ltr a min but unless you can
    measure it that is accademic.

    So the best way is with a sensative piece of your
    skin and make sure all the pipe ends are capped with
    just a small vent hole to alow flow.

    Cheers taz.

    .

  3. #3
    Join Date
    Nov 2009
    Location
    Western PA
    Age
    48
    Posts
    69
    Rep Power
    15

    Re: nitro purgin

    Taz gave as good of an explanation as I can, if not better.

    I usually hold my hose to my cheek and feel for the slight flow. Then I hook it up to the piping.

  4. #4
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: nitro purgin

    doesnt hurt to have a vertical section at the end either as you know the pipe will fill regardless of your relief hole location
    mmm to beer or not to beer...........lets drink breakfast

  5. #5
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: nitro purgin

    Nitrogen...

    Nitro is an abbreviation for nitroglycrine... Won't get me going there, I promise.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  6. #6
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: nitro purgin

    Quote Originally Posted by desA View Post
    Nitrogen...

    Nitro is an abbreviation for nitroglycrine... Won't get me going there, I promise.

    Anybody purging with nitroglycrine will get every one going. Away!! Fast!!



    Cheers taz

    .

  7. #7
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: nitro purgin

    You can get those vertical flow meters with a floating bobbin with adjusting screw at the bottom , they are the same type that welders use for mig and tig welding

  8. #8
    Join Date
    Apr 2008
    Location
    north west runcorn
    Age
    57
    Posts
    28
    Rep Power
    0

    Re: nitro purgin

    so 2ltr a min it is then boc sell a flow meter will pick one up .thanks for that taz

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: nitro purgin

    Another way is to punch a hole in the rubber or plastic plugs on the tubing. This will vent enough nitrogen through the tubing to keep it clean and you don't need another regulator.
    If all else fails, ask for help.


  10. #10
    Adi cool's Avatar
    Adi cool Guest

    Re: nitro purgin

    Just use an old service manifold. Use compound side or H.p if you like and set up using hose to pipe or component that your brazing. Set at 5 p.s.i.g ( will vary depending on pipe size) and make sure system is open e.g open service valves or remove pipe caps. Hope this helps

  11. #11
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: nitro purgin

    not how i do it, but i red it in a refrigeration book that u ad the other end to a hose and the hose you add it in a bottle of water, and theoretically if u feel once the system with nitrogen, then you just need it to bobble in the water a little bit so you make shore no air is getting back in the system