16-12-2004, 03:59 AM #1
System charging
Has anyone had problems with charging a system with liquid in the low side of a domestic refrigerator using 134A? I have always been taught and have also read that there is a risk of compressor damage by doing this.
-
16-12-2004, 09:25 AM #2
Re: System charging
Originally Posted by Dylan
It could be argued that the maximum system charge for the fridge/compressor should ensure safe operation but with a cold compressor on start up and charging a risk is there.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
16-12-2004, 12:30 PM #3
Re: System charging
Originally Posted by Dylan
Good Practice is to charge with vapours only but in case of blends where refrigerant has to be charged in liquid state only then do the what I have mentioned earlier.
Tejbir singh
-
16-12-2004, 06:18 PM #4
Re: System charging
Hi Dylan
I use a cap-kit ie a copper spun drier with a length of capillary c/w 1/4 brass connection.
Best regards MarkLast edited by Mark; 16-12-2004 at 06:22 PM.
-
16-12-2004, 06:51 PM #5
Re: System charging
i use one of those flow reducer things from "yellow jacket" seems to work ok.
i timed it a couple of days ago, it took 15mins for 600g of 134a.
cheers
eggs
-
16-12-2004, 08:03 PM #6
Re: System charging
There is a small device called KWIK CHARGE that you connect to the suction line and charge with liquid refrigerant.
Never used it, only saw it. I believe it made by Imperial of USA.
Chemi
-
16-12-2004, 10:36 PM #7
Re: System charging
As good practice I always take my time when filling with liquid.
On the comps I have opened the intake is at the top inside the body and probebly not much chance of completly filling the body with liquid.
I thought it was that when even a smallish amount of liquid is put in, in boils off and lifts the oil into the pump which can destroy it and not the actual refrigerant liquid.
Exspeicially when youve already evacuated the system and the oil is ready to absorb most of the charge before it warms up.
ps any chance of getting a spell checker on this page. cos mine is atrotiousIF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
16-12-2004, 10:56 PM #8
Re: System charging
just write it full of spelling mistakes and bad grammer, i've only been sort of told off for it once.
cheers
eggs
-
17-12-2004, 04:58 PM #9
Re: System charging
where's 'quinte'??
cheers
richard
-
17-12-2004, 04:59 PM #10
Re: System charging
Use a drier that has a schreader valve fitted ,then charge directly into the liquid line.(NRS)
-
17-12-2004, 10:37 PM #11
Re: System charging
Originally Posted by rbartlett
According to the WWW it is in Canada, which I suppose means that it is really somewhere completely differentBrian - Newton Abbot, Devon, UK
Retired March 2015
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
System Burn Out Troubleshooting
By altaf22m in forum Technical DiscussionsReplies: 13Last Post: 07-05-2010, 09:24 AM -
CARE refigerants by BOC
By dogma in forum RefrigerantsReplies: 8Last Post: 23-03-2010, 12:39 PM -
Burn out System, Clean up procedure. & Troubleshooting.
By altaf22m in forum CommercialReplies: 19Last Post: 15-04-2008, 07:03 PM -
Charging a system
By shark26 in forum FundamentalsReplies: 32Last Post: 31-01-2006, 06:41 PM