Results 1 to 3 of 3
Thread: Vacuum specification
-
13-11-2009, 08:58 PM #1
Vacuum specification
Anybody can venture an opinion !! Does anyone have a definitive spec for the depth of vacuum in a close control unit, My thoughts are 1-2 mbar (750-1500 microns) the local agent for the machine is asking for 400 microns and can't give a valid reason why it has to be so low. Can you help me ?
-
14-11-2009, 12:05 AM #2
Re: Vacuum specification
Because 400 is drier than 750 ??
Around 1000 micron for AC stuff but you should go lower for refrigeration type levels.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
12-01-2010, 05:06 AM #3
Re: Vacuum specification
500 microns is a good pull the reason being is if you got a tight system youll get that if it leaks you wont.