    Re: Daikin RY60EV1A unit trips circuit breaker E3 ?

    u might be right i did not say that but it depends dose the compressor start for a moment or just trips the C/B , but then it might be a C/B fault also

  2. #2
    amref's Avatar
    amref Guest

    Re: Daikin RY60EV1A unit trips circuit breaker E3 ?

    Did a check on the compressor windings there was no readings to ground. but the compressor had seized
    So a new compressor is required
    By the way the code E3 or high pressure switch fault does not exist on this model, according to daikin there is no HPS on this unit ??
    Thank you for all for the support.