    Daikin RY60EV1A unit trips circuit breaker E3 ?



    Hi ,
    Im new to this forum .I have a Daikin ducted RY60EV1A outdoor unit when its turned on after a few seconds it trips the saftey switch.
    When the saftey switch is reset the leds on the circuit board on the out door unit has a green fashing light indicating the systems ok. When a button is activated on the panel inside it indicates an E3 error according to the fault chart indicates a High Pressure switch on the outdoor unit '
    Can I get some help on this unit Thanks.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Daikin RY60EV1A unit trips circuit breaker E3 ?

    Clean (wash) the outdoor unit fins and check if fan is rotating freely and happily.

  3. #3
    amref's Avatar
    amref Guest

    Re: Daikin RY60EV1A unit trips circuit breaker E3 ?

    Have checked the fan, spins freely and the fins seem reasonably clean. Will give it a wash anyway.
    Have tried the unit in fan mode only the unit works fine but trips the saftey switch in Heating and cooling mode.
    Would the filters in the unit in the roof need cleaning.
    Thanks

  4. #4
    Join Date
    May 2009
    Location
    uk
    Age
    62
    Posts
    44
    Rep Power
    0

    Re: Daikin RY60EV1A unit trips circuit breaker E3 ?

    could be compressor is burned out dissconnect compressor wires and operate if it does not trip then compressor is faulty

  5. #5
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin RY60EV1A unit trips circuit breaker E3 ?

    check your earth resistance to the compressor, make sure there is none. it will either be the compressor down to earth or the capacitor is faulty.

  6. #6
    amref's Avatar
    amref Guest

    Re: Daikin RY60EV1A unit trips circuit breaker E3 ?

    Thank you for the quick response I will check the compressor later today and let you know the results.
    would anybody have a PDF of the RY60EV1A service manual

  7. #7
    Join Date
    Oct 2005
    Location
    In a 2 bedroom unit. Why's That? :)
    Posts
    314
    Rep Power
    19

    Re: Daikin RY60EV1A unit trips circuit breaker E3 ?

    E3 : High pressure
    switch (HPS)
    activated.

    Dirty Heat Exchanger.


    Check the condenser fan for free spin, disconnect the fan, rest the fault codes, run test. If it's the fan the CB won't trip but you'll still get E3 hp fault.


    If it's the fan replace the outdoor pcb with the fan, the short is generally in the board.


    Regards


    DOGMA



    ps.... that's after giving the coils a good clean...
    Last edited by dogma; 09-11-2009 at 11:59 AM. Reason: huh?

  8. #8
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: Daikin RY60EV1A unit trips circuit breaker E3 ?

    Don't forget to make shore that no one did overcharge the system and the safety switch is not uncalibrated

  9. #9
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin RY60EV1A unit trips circuit breaker E3 ?

    a high pressure fault should not take out the C/B....

  10. #10
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: Daikin RY60EV1A unit trips circuit breaker E3 ?

    brunstar

    it can, because of the high pressure the compressor is absorbing more amps , and/or liquid back to compressor dose the same thing

  11. #11
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin RY60EV1A unit trips circuit breaker E3 ?

    if the system is full of that much liquid it might trip the breaker but if it is only pumping for a few seconds, by the sounds of it the unit is not even turining over.
    It will either be down to earth, seized or capacitor faulty.
    I think the E3 fault is just an old fault.

  12. #12
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: Daikin RY60EV1A unit trips circuit breaker E3 ?

    u might be right i did not say that but it depends dose the compressor start for a moment or just trips the C/B , but then it might be a C/B fault also

  13. #13
    amref's Avatar
    amref Guest

    Re: Daikin RY60EV1A unit trips circuit breaker E3 ?

    Did a check on the compressor windings there was no readings to ground. but the compressor had seized
    So a new compressor is required
    By the way the code E3 or high pressure switch fault does not exist on this model, according to daikin there is no HPS on this unit ??
    Thank you for all for the support.

Similar Threads

  1. Transmission wiring on Daikin VRV2
    By Markie in forum Air Conditioning
    Replies: 19
    Last Post: 25-09-2009, 06:24 PM
  2. Daikin a/c units.
    By rick in forum Air Conditioning
    Replies: 59
    Last Post: 18-02-2008, 09:22 PM
  3. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM
  4. Daikin Indoor Unit
    By ebo in forum Air Conditioning
    Replies: 10
    Last Post: 15-03-2006, 03:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •