LG ducted air system=code ch46 fault
Can anyone help me a diagnosis of this fault. Don't know whether we need to call in an engineer or not.
Newbie on the site.Thanks for any help.Last edited by Brian_UK; 16-10-2009 at 11:05 PM. Reason: Moved post to correct section.
-
16-10-2009, 11:09 PM #2
Re: LG ducted air system=code ch46 fault
HI, fault code says this...
CH46 Outdoor unit suction sensor fault. Disconnect from PCB and measure resistance. 10 kOhm at 10°C and 4 kOhm at 30°C. If OK replace PCB, if not replace sensor.
Full list available here..
http://mylg.co.uk/data%20for%20site/...%20Sept%29.pdf
Also try the above site http://mylg.co.uk for any other info that may be useful to you in your quest.Brian - Newton Abbot, Devon, UK