    York Chiller question



    York VSM89 liquid screw chiller.
    Can anybody point me in the right direction. The oil pump has very little oil pressure. The pump was replaced, the screens and valves were all cleaned. A fairly large amount of metal shavings were removed from the oil filter.
    Alarms still set off on low oil pressure, can anybody help. Received no help from York.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,700
    Rep Power
    47

    Re: York Chiller question

    TCHC.
    Hi.
    I cannot comment upon your particular screw compressor.
    But if the metal deposits found within the oil filter, are as numerous and large as you say?
    I would begin to suspect that there is so much internal wear that.
    Not enough back pressure can be developed as the oil is "pouring" through the machine.
    This is quite common when the wear is excessive.
    No matter how good the oil pump is you will never achieve the required pressures if this is the case.
    How many run hours has this machine done?
    Have you re-checked the oil filter because is the alarm actual oil pressure. Or is it not Oil differential across the filter?
    Lots of questions as your info is a little scant!
    Cheers Grizzly

  3. #3
    Azmath Syed's Avatar
    Azmath Syed Guest

    Re: York Chiller question

    Keep on running the oil pump can clean the meshes this is the only way of the lines are not choked

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: York Chiller question

    Quote Originally Posted by tchc View Post
    York VSM89 liquid screw chiller.
    Can anybody point me in the right direction. The oil pump has very little oil pressure. The pump was replaced, the screens and valves were all cleaned. A fairly large amount of metal shavings were removed from the oil filter.
    Alarms still set off on low oil pressure, can anybody help. Received no help from York.
    hi if u found metal shavings inside your comp u have to find out what is going on ?
    why was the previous pump changed?
    was the oil changed with the oil pump?
    good luck

Similar Threads

  1. York Chiller problems
    By ingherrera in forum Commercial
    Replies: 18
    Last Post: 26-07-2011, 03:10 PM
  2. York (YK FK FL P9-CZFS CENTIFUGAL CHILLER)
    By ahs in forum Trouble Shooting
    Replies: 8
    Last Post: 11-11-2009, 01:38 PM
  3. York Chiller startup when on Emergency Power
    By Apollo10 in forum Trouble Shooting
    Replies: 3
    Last Post: 22-12-2008, 07:13 PM
  4. york chiller motor rotation error
    By cesarnino in forum Trouble Shooting
    Replies: 7
    Last Post: 13-12-2008, 03:43 PM
  5. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •