Daikin Multi Split A/C problems
im having trouble with a DAIKIN MULTI SLPIT model no.MY56AV4N , all electrics are ok , the fault code says OL , IP activated, the unit starts to run for approx.5 secs and then trips overload and continues to do so, the system is charged correctly, any help or tips would be greatly appreciated
-
28-10-2004, 05:13 PM #2
Re: Daikin Multi Split A/C problems
Hi Tim
The MY56 "A" series is not one that I have seen in the Uk. I went on a Multi Split course in '94 and the current series then was "C". Looking through my notes and course syllabus I cannot find a reference to the fault code OL.
As the unit is tripping the OL (overload?) then my first guess would be to investigate the compressor motor windings. Have you done an insulation resistance reading? What about the fan motor as well - have you looked at this.
There are 2 reasons why a forced stop would be initiated:
1 Low outdoor air temperature
2 Outdoor coil exceeds 63 deg C (cooling mode)
None of these will cause the OL to trip though.
Perhaps you could give some additional information on the tests/checks you have carried out so far.
-
28-10-2004, 08:41 PM #3
Re: Daikin Multi Split A/C problems
personally I would take the amps then compare to the setpoint of the o/l
then I would take the result and proceed from there...
cheers
richard
-
28-10-2004, 11:02 PM #4
Re: Daikin Multi Split A/C problems
Originally Posted by timholmes204
It appears that at least the overload is working correctly but you need to take some readings to help us make some informed suggestions.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
18-05-2008, 08:01 AM #5
Re: Daikin Multi Split A/C problems
i am getting error code as j2 it is current sensor malfunction can any one tell me how to solve this problem
-
21-05-2008, 10:41 AM #6
Re: Daikin Multi Split A/C problems
e5 is comp overload code for daikans. if you have infared remote for indoor units point at anyone while pushing all 3 buttons at the same time- 'mode' 'temp up' temp down' this will bring up OO where temp set point is normally displayed. scroll up or down with temp up or down buttons (1st digit only) untill you here the beeping sound change tone, this is the 1st part of the fault code. press mode once to change to 2nd digit, scroll again with up and down listening for change of beep- 2nd part of code ie "E5". press mode again will bring up afunny looking T-test mode. press mode again to exit. once you have fault code get a manual and fix.
-
22-05-2008, 12:09 AM #7
Similar Threads
-
Daikin Controllers
By airefresco in forum Air ConditioningReplies: 5Last Post: 15-05-2008, 08:08 AM -
!!big Daikin Problem!! Codes,u4,pj, And E0
By airconengineer in forum Air ConditioningReplies: 21Last Post: 31-05-2007, 09:04 PM -
ceiling concealed multi split
By SIRROM in forum Air ConditioningReplies: 7Last Post: 22-08-2006, 01:47 PM -
Ascon ac multi split
By mike live in forum Air ConditioningReplies: 14Last Post: 30-06-2006, 08:52 PM -
Oil return problems
By Peter_1 in forum IndustrialReplies: 37Last Post: 23-08-2004, 11:30 PM