    Can anybody back my theory up?



    I got sent on a call out today to the British Red Cross, to deal with a unit blowing out "Black Soot". When I arrived I found a Toshiba Split system with the indoor wall mounted unit iced up.
    Upon investigating, I found that the fan scroll was extremely, and I mean extremely, clogged. My innitial theory was that the deminished air flow across the evaporator caused the ice build up. That was untill I looked at the outdoor unit. This was only very briefly as I had to leave to make it to evening class for my HNC. I found that even though the indoor unit setpoint was 29 degc(to melt the ice) the comp was still running. Even when I had it in fan only mode, the comp was still running.
    Now it is a very old system and as far as I'm aware does not have an emergency run mode. I also thought it might have been the return air thermistor but ruled it out when the comp was running in fan mode! I am going back tomorrow to fully investigate the poblem. Now, after thinking a bit about the problem the only thing I can think of is that the indoor pcb is knackered, therefore sending the signal to the comp to run when it shouldn't!
    • Firstly does anybody know much about toshiba, your help will be greatly appreciated
    • Does anybody have a number for their tech dept here in the uk.
    • Does anybody have any suggestions


    Never underestimate anybody, you never know when they will make you look like an idiot!

  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Can anybody back my theory up?

    2 points come to mind but the first is probably the one that is causing the trouble - sounds like the contactor is welded.

    The second one is to check the indoor coil sensor

  3. #3
    rbartlett's Avatar
    rbartlett Guest

    Re: Can anybody back my theory up?


  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Can anybody back my theory up?

    I'll back up Franks comment, there is a small power relay on the indoor board, about the size of a matchbox, that welds itself in the ON position. Disconnect the power wire and watch the compressor stop.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2004
    Location
    U.K.-London
    Posts
    144
    Rep Power
    20

    Re: Can anybody back my theory up?

    Turned out to be the contactor after all!
    Still had continuity across the switch with the unit isolated.
    Never underestimate anybody, you never know when they will make you look like an idiot!

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Can anybody back my theory up?

    Quote Originally Posted by Coolie
    Turned out to be the contactor after all!
    Still had continuity across the switch with the unit isolated.
    Is this where we all go - Told you so

    Glad that you sorted the problem Coolie especially on a friday.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. back pressure valve in chiller
    By vinod in forum Air Conditioning
    Replies: 2
    Last Post: 12-06-2006, 06:29 PM
  2. Back Pressure Valve
    By guapo in forum Industrial Compressors
    Replies: 2
    Last Post: 18-03-2006, 04:38 PM
  3. Flood Back After 2 years..
    By Mahmoud in forum Fundamentals
    Replies: 10
    Last Post: 27-09-2005, 11:06 AM
  4. Compressor back pressure rating
    By Cary in forum Fundamentals
    Replies: 9
    Last Post: 05-12-2004, 08:42 AM
  5. Low back pressure compressor application
    By Abe in forum Technical Discussions
    Replies: 5
    Last Post: 31-07-2001, 11:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •