    hp trip



    hi all

    new to forum, first post here. I am going to a job on friday to change a hp transducer on carrier chiller as it has an intermittent fault. Engineer that visited site previously also said system tripping on hp even though coil is clean and cond fan running at full capacity. not come across this before, any suggestions?



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,703
    Rep Power
    46

    Re: hp trip

    Welcome to the forum Han.
    You seem to have answered the question yourself.
    Basically the hp is monitored from within the chiller software.
    Using the Hp transducer signal input.
    Therefore if the transducer is as you say faulty.
    It is reasonable to assume that the signal it supplies the chiller software is also faulty?
    Therefore could not the pressure it reads be "High" causing an false high pressure fault?
    Cheers Grizzly

  3. #3
    Join Date
    Sep 2009
    Location
    england
    Posts
    10
    Rep Power
    0

    Re: hp trip

    hi grizzly
    thanks for the response to my post. Spoke to engineer who originally attended job and he is saying condenser coil is hot to the touch and that he applied a guage and found discharge pressure to be around 26 bar. I understand that there could be a false pressure reading on the digital display from the faulty transducer but would this actually effect the coil temp/pressure with the fan at full capacity. Is it possible the compressor is faulty aswell? Im on the job tomorrow so can investigate further myself.
    han81

  4. #4
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: hp trip

    Quote Originally Posted by han81 View Post
    hi grizzly
    thanks for the response to my post. Spoke to engineer who originally attended job and he is saying condenser coil is hot to the touch and that he applied a guage and found discharge pressure to be around 26 bar. I understand that there could be a false pressure reading on the digital display from the faulty transducer but would this actually effect the coil temp/pressure with the fan at full capacity. Is it possible the compressor is faulty aswell? Im on the job tomorrow so can investigate further myself.
    han81
    Unless you are having hot weather in your area, 26 Bar is quite high. See for yourself if the condenser coil is clean. Otherwise you may have quite a heat load on the system, amongst many other reasons for high condensing temperatures. Take all your pressure/temperature readings, superheat, subcooling etc and make your own mind up.

    I hate inheriting other people's jobs. Sometimes they misdiagnose a fault, and then you're stuck with explaining to the customer why it still isn't fixed.
    Last edited by acnerd; 17-09-2009 at 05:48 PM. Reason: grammatical error
    If at first you DO succeed, try to hide your astonishment!!

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,703
    Rep Power
    46

    Re: hp trip

    Quote Originally Posted by han81 View Post
    hi grizzly
    thanks for the response to my post. Spoke to engineer who originally attended job and he is saying condenser coil is hot to the touch and that he applied a guage and found discharge pressure to be around 26 bar. I understand that there could be a false pressure reading on the digital display from the faulty transducer but would this actually effect the coil temp/pressure with the fan at full capacity. Is it possible the compressor is faulty aswell? Im on the job tomorrow so can investigate further myself.
    han81
    Thanks for the update Han,
    Armed with this further information.
    I assume that you have 2 separate issues as implied!
    To be able to comment further more information is needed.
    26 bar does seem high, but that depends upon what refrigerant we are talking about?
    Good Luck Grizzly!

Similar Threads

  1. Trane RTAC 170 , Phase reversal trip?
    By THE WOMBAT in forum Commercial
    Replies: 26
    Last Post: 09-07-2010, 01:23 AM
  2. Denco unit L.P trip
    By N.Lewis in forum Air Conditioning
    Replies: 9
    Last Post: 09-04-2010, 10:23 PM
  3. Ciat chiller trip
    By twisty in forum Commercial
    Replies: 4
    Last Post: 29-07-2009, 05:05 PM
  4. Low pressure trip !!
    By oilzee in forum Trouble Shooting
    Replies: 47
    Last Post: 03-11-2008, 03:27 PM
  5. Reasons for High Pressure / Low Pressure Trip outs
    By majikman in forum Air Conditioning
    Replies: 19
    Last Post: 02-02-2007, 08:47 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •