12-09-2009, 02:17 PM #1
Maximum discharge pressure ZB scroll compressor
Need help ,
Does anybody know maximum discharge pressure ZB76 scroll compressor?
Is it possible if dirty oil happened can reduce discharge pressure?
13-09-2009, 03:20 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Maximum discharge pressure ZB scroll compressor
Maximum pressure is noted on compressor nameplate.
Still, compressor operating pressure could be relatively low but discharge superheat high.
Therefore, it is important to keep suction superheat low enough and, in that way, discharge superheat low.
Important is, that discharge gases are below 120°C.
13-09-2009, 03:46 PM #3
What nike123 says plus here's a link to the Copeland ZB bulletin which has more information.
http://www.hvacrinfo.com/ae_index.htm
Bulletin 4-1318Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com