Results 1 to 3 of 3
  1. #1
    Join Date
    Aug 2009
    Location
    Surabaya
    Posts
    12
    Rep Power
    0

    Maximum discharge pressure ZB scroll compressor



    Need help ,

    Does anybody know maximum discharge pressure ZB76 scroll compressor?
    Is it possible if dirty oil happened can reduce discharge pressure?

    Thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Maximum discharge pressure ZB scroll compressor

    Maximum pressure is noted on compressor nameplate.
    Still, compressor operating pressure could be relatively low but discharge superheat high.
    Therefore, it is important to keep suction superheat low enough and, in that way, discharge superheat low.
    Important is, that discharge gases are below 120°C.

  3. #3
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Maximum discharge pressure ZB scroll compressor

    What nike123 says plus here's a link to the Copeland ZB bulletin which has more information.

    http://www.hvacrinfo.com/ae_index.htm

    Bulletin 4-1318
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

Similar Threads

  1. Replies: 5
    Last Post: 08-11-2009, 05:10 PM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  3. Scroll Compressor Seizure
    By jwasir in forum Trouble Shooting
    Replies: 9
    Last Post: 08-06-2008, 12:52 PM
  4. cooling &freezing comp.
    By afeef in forum Industrial Compressors
    Replies: 25
    Last Post: 15-12-2006, 09:29 PM
  5. Replies: 27
    Last Post: 27-10-2006, 03:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •