    Question Seized Scrolls



    Hi,

    From past some time, we are getting some seized scrolls. These are ZR types from Copeland w/o oil sight glass.

    After replacing the compressor, no unsual parameters were noticed. The suction, discharge, SH, subcooling, etc all are within the envelope.

    I wonder what happens during night, which causes low lubricant and seizes the compressor.

    Any thoughts and ideas!!



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Seized Scrolls

    Quote Originally Posted by jwasir View Post
    Hi,

    From past some time, we are getting some seized scrolls. These are ZR types from Copeland w/o oil sight glass.

    After replacing the compressor, no unsual parameters were noticed. The suction, discharge, SH, subcooling, etc all are within the envelope.

    I wonder what happens during night, which causes low lubricant and seizes the compressor.

    Any thoughts and ideas!!
    hi check head pressure control causes liquid to return in suction line and oil diilution and migration
    also check sump heater usualy wrapped arround compressor
    a scroll can handle liquid slugging( not for long periodes ) but cant handle no oil

  3. #3
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    19

    Re: Seized Scrolls

    Thanks Goshen,

    There is fan cycling controls on the system but mostly they fail in summers, when Head pressure is within the range.

    All the comp's are equipped with crank case heaters.

    I cant understand what is causing NO OIL conditions?

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Seized Scrolls

    So far, all we know about this system is that it has a scroll compressor. For all we know it could be anything from a cascade freezer to a heat pump to a process system to whatever. It could be TXV or cap tube or fixed orifice or low side float or whatever. It could use any of the multitudes of refrigerants out there along with any of the many types of oil. It could have infinite variations of control strategies... or maybe it just plugs into the wall.

    We can't see it from here. All we can see is your description and you haven't even begun to describe it.

Similar Threads

  1. Copeland Scrolls going to earth
    By Latte in forum Trouble Shooting
    Replies: 7
    Last Post: 19-08-2008, 09:08 PM
  2. seized inv compressor
    By flash in forum Air Conditioning
    Replies: 2
    Last Post: 09-04-2008, 06:56 PM
  3. Copeland Scrolls & Green Slime formation
    By powell in forum Air Conditioning
    Replies: 0
    Last Post: 09-04-2008, 11:31 AM
  4. Question on EER & Low Capacity Scrolls
    By pjauff in forum Air Conditioning
    Replies: 0
    Last Post: 04-03-2008, 01:14 AM
  5. A site thats changing to scrolls
    By WebRam in forum Supermarket Refrigeration
    Replies: 21
    Last Post: 05-03-2004, 10:08 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •