04-09-2009, 12:19 AM #1
Liebart System
So here's the senario: I showd up at a server room about 2:00pm and the Liebert a/c system was off on high head. I was pretty sure that the (remote condenser) coil wasn't plugged cause I had blown it out myself less than 2 months ago. It's an R22 system and the gauge read around 350 psi on the LL (ambient is 88 degrees). It would creep to 370 and trip. After adjusting the fan blade in the shroud (an apprentice had installed a new condenser fan motor 3 months ago) nothing really semed to matter. Another tech had replaced a plugged tx valve on it a month ago but it had been working well until today. He said that he had checked the superheat and subcooling and had set the valve up for 8-9 degrees superheat and all was well. The chance of non condensibles seems really remote and if I pour some water on the coil the head pressure drops like a stone to 230. Suction pressure is 60-70psi. Is there anything I might be missing beore I rip out the charge and replace it with (for sure) clean refrigerant? Thanks in advance.
-
04-09-2009, 10:49 AM #2
Re: Liebart System
hi there check the replacment fan ,
it would appear it is not the same as original( less cfm ) or possibly reversed in direction !
let us know how it turned out
-
04-09-2009, 11:19 AM #3
Re: Liebart System
if ambient is 88 then condensing pressures looks very high and since tx is replaced there may be air in the system it must be bleeded if possible from a relief valve or you have to recover refrigerant and evacuate and dry the system and then recharge
-
04-09-2009, 11:23 AM #4
Re: Liebart System
Goshen sounds to be on the right path
Before recovering the refrigerant check the condensor again
i.e. air on and air off temps and volume of air across the coil.
Also check for dead rows (indication of non condensibles)
It might just be all the packing material from the new fan blocking the coilQuidvis Recte Factum Quamvis Humile Praeclarum.
Latine dictum, sit altum videtur.
Si hoc comprehendere potes, gratias age magistro Latinae.
-
04-09-2009, 11:23 AM #5
Re: Liebart System
I remember years ago having a similar problem. It turned out to be a faulty pressure switch (head pressure controller) It wouldn't cut the fans in.
a problem shared is a problem halved
-
04-09-2009, 02:01 PM #6
Re: Liebart System
I haven't been back there yet this morning, but I will check the fan motor. I thought it was ordered directly from Liebert as a replacement. There is no place to bleed air from the system so the refrigerant would have to be replaced. I will check for dead rows on the condenser coil but there was a ton of heat coming off it last night. I WILL cure the problem today and let you know how it turned out. It has to turn out good... today is friday.
-
04-09-2009, 02:37 PM #7
Re: Liebart System
I WILL cure the problem today and let you know how it turned out. It has to turn out good... today is friday.Quidvis Recte Factum Quamvis Humile Praeclarum.
Latine dictum, sit altum videtur.
Si hoc comprehendere potes, gratias age magistro Latinae.
-
05-09-2009, 12:29 AM #8
Re: Liebart System
Yet a single ray of sunlight peeks thru stark blackness and a chorus of singing angels gently serenade the dawning a new day ... Okay, I myself didn't make it back to this job but I did dispatch an apprentice to recover and replace the charge. When I phoned him to see how the task was going he said good but the vacuum was proceeding very slowly. I then realized what was wrong. The tech that replaced the tx valve didn't energize the solenoid valve when he was pulling the vacuum. Once I told him to disconnect the compressor contactor and turn the unit on to open the solenoid the vacuum dropped like a stone. The charge was weighed back in and the head pressure dropped to 220psi. All is well but then why wouldn't it be ... it's friday!
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
Ammonia Heat Pumps
By US Iceman in forum New TechnologiesReplies: 39Last Post: 22-03-2010, 06:36 PM -
Enthalpy Increasing Buffer System
By Reflexive in forum Technical SpeculationsReplies: 3Last Post: 23-12-2008, 03:18 PM -
Fan model for system optimization
By autt in forum System OptimizationReplies: 8Last Post: 31-03-2007, 05:34 AM -
Automotive A/C Vent Temp Range vs System
By Don Browney in forum Air ConditioningReplies: 1Last Post: 15-05-2002, 06:19 AM