    Liebart System



    So here's the senario: I showd up at a server room about 2:00pm and the Liebert a/c system was off on high head. I was pretty sure that the (remote condenser) coil wasn't plugged cause I had blown it out myself less than 2 months ago. It's an R22 system and the gauge read around 350 psi on the LL (ambient is 88 degrees). It would creep to 370 and trip. After adjusting the fan blade in the shroud (an apprentice had installed a new condenser fan motor 3 months ago) nothing really semed to matter. Another tech had replaced a plugged tx valve on it a month ago but it had been working well until today. He said that he had checked the superheat and subcooling and had set the valve up for 8-9 degrees superheat and all was well. The chance of non condensibles seems really remote and if I pour some water on the coil the head pressure drops like a stone to 230. Suction pressure is 60-70psi. Is there anything I might be missing beore I rip out the charge and replace it with (for sure) clean refrigerant? Thanks in advance.



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Liebart System

    hi there check the replacment fan ,
    it would appear it is not the same as original( less cfm ) or possibly reversed in direction !
    let us know how it turned out

  3. #3
    Join Date
    Dec 2007
    Location
    Saui Arabia
    Posts
    12
    Rep Power
    0

    Re: Liebart System

    if ambient is 88 then condensing pressures looks very high and since tx is replaced there may be air in the system it must be bleeded if possible from a relief valve or you have to recover refrigerant and evacuate and dry the system and then recharge

  4. #4
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Liebart System

    Goshen sounds to be on the right path

    Before recovering the refrigerant check the condensor again
    i.e. air on and air off temps and volume of air across the coil.

    Also check for dead rows (indication of non condensibles)

    It might just be all the packing material from the new fan blocking the coil
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  5. #5
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Liebart System

    I remember years ago having a similar problem. It turned out to be a faulty pressure switch (head pressure controller) It wouldn't cut the fans in.
    a problem shared is a problem halved

  6. #6
    twisted22's Avatar
    twisted22 Guest

    Re: Liebart System

    I haven't been back there yet this morning, but I will check the fan motor. I thought it was ordered directly from Liebert as a replacement. There is no place to bleed air from the system so the refrigerant would have to be replaced. I will check for dead rows on the condenser coil but there was a ton of heat coming off it last night. I WILL cure the problem today and let you know how it turned out. It has to turn out good... today is friday.

  7. #7
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Liebart System

    I WILL cure the problem today and let you know how it turned out. It has to turn out good... today is friday.
    And if you listen very carefully a solitairey bell tolls in the distance, amidst darkening skies as the sunlight is obscured by the ominous thunder heads stampeding from the horizon.
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  8. #8
    twisted22's Avatar
    twisted22 Guest

    Re: Liebart System

    Quote Originally Posted by TRASH101 View Post
    And if you listen very carefully a solitairey bell tolls in the distance, amidst darkening skies as the sunlight is obscured by the ominous thunder heads stampeding from the horizon.
    Yet a single ray of sunlight peeks thru stark blackness and a chorus of singing angels gently serenade the dawning a new day ... Okay, I myself didn't make it back to this job but I did dispatch an apprentice to recover and replace the charge. When I phoned him to see how the task was going he said good but the vacuum was proceeding very slowly. I then realized what was wrong. The tech that replaced the tx valve didn't energize the solenoid valve when he was pulling the vacuum. Once I told him to disconnect the compressor contactor and turn the unit on to open the solenoid the vacuum dropped like a stone. The charge was weighed back in and the head pressure dropped to 220psi. All is well but then why wouldn't it be ... it's friday!

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Ammonia Heat Pumps
    By US Iceman in forum New Technologies
    Replies: 39
    Last Post: 22-03-2010, 06:36 PM
  3. Enthalpy Increasing Buffer System
    By Reflexive in forum Technical Speculations
    Replies: 3
    Last Post: 23-12-2008, 03:18 PM
  4. Fan model for system optimization
    By autt in forum System Optimization
    Replies: 8
    Last Post: 31-03-2007, 05:34 AM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •