Have a trane Chiller ECGCD206 on R22
need advice on drop in refrigerants for this chiller was considering Isceon 59 do not want to change oil.
would appreciate your comments if you have
carried this.(Do trane still have a technical depatment?)
Thanks
Freecool
-
02-09-2009, 07:44 PM #2
Re: Trane Chillers
What's Isceon 59? R422d?
If so you will need to change the oil!
For info on local support: http://www.trane.comIf it ain't broke, don't fix it!
-
06-09-2009, 12:50 PM #3
Re: Trane Chillers
Pretty sure the oil will have to be changed ive not heard of isceon 59. If it can be done let me know got a couple of Trane chillers on R22 that will need changing soon. Trane do have a technical department but they always seem to be busy or out of the office try ringing 01925623660 and they should find you somebody to talk to
-
08-09-2009, 08:55 PM #4
Re: Trane Chillers
Trane do not support any " Drop in " refrigerant conversions. The standard supported operation is to Retrofit to R404a-including oil flushes, TEV change, o-rings drier cores and PRV`s.
-
08-09-2009, 09:32 PM #5
Re: Trane Chillers
Hello freecool which compressors are on these chillers,because the old recipes which are 75hp-100hp have internal o rings in the loading cages and if they swell up with chemical reaction then you,ll have to strip the machine down.ihav,nt seen any on diffrent gas, so its best to speak to trane for guidance
-
09-09-2009, 12:11 AM #6
Re: Trane Chillers
Isceon 59 - R-417a
You want to change the gas, you have to change the oil and do some retrofitting on the machine
If you're not going to change the oil, be prepare of what is going to happen next as to what has been just indicated by Ghaz.
-
17-09-2009, 08:11 PM #7
Re: Trane Chillers
Depends on the application but Isceon 29 (R422d) is the gas for chillers. Isceon 59 is for DX- it operates at higher temps than a chiller ( DX runs at 18-25degrees, a chiller at 6-10degrees. Typically). Isceon 29 will work on Mineral. Sometimes you may need to change some components for larger ones and some seals as well.
-
18-09-2009, 11:35 AM #8
Re: Trane Chillers
Trane will not advise on a drop-in. They will ask unit details and site location and then submit a quotation for their own engineers to carry out the work.
Similar Threads
-
AEC Pinical chiller with trane comp
By cptrdbrd in forum CommercialReplies: 1Last Post: 28-10-2009, 09:47 PM -
Air cooled chillers vibration isolation
By vijay_study in forum Air ConditioningReplies: 3Last Post: 06-10-2009, 08:53 PM -
Optimising parallel water chillers for energy saving
By Electrocoolman in forum System OptimizationReplies: 7Last Post: 27-07-2009, 01:56 PM -
New to Forum, Facing problems related with TRANE Chiller
By neerajpuranik in forum Air ConditioningReplies: 3Last Post: 10-12-2008, 02:43 AM -
Trane CVHE 450 R11 Centrifugal Chiller
By albertjoseph in forum Air ConditioningReplies: 4Last Post: 06-10-2008, 03:23 PM