    Post trane rtad 125 chiller, reverse phase issue



    hi all, im working on a trane chiller at present.circuit 1 hasnt been working for years so loads of fun. pressure tested,vac and weighed in new gas.had hp issue on controller without system 1 running, reset hp switch.this seemed to solve problem and comp kicked in.isolated unit to put electrical covers back on, now controller displaying reverse phase detection? any pointers would be helpfull thank you



  2. #2
    Join Date
    Nov 2008
    Location
    australia
    Posts
    136
    Rep Power
    16

    Re: trane rtad 125 chiller, reverse phase issue

    hi, are all phases still on at machine?

  3. #3
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: trane rtad 125 chiller, reverse phase issue

    Is this option even installed or did you enable it when the option is not present?
    If it ain't broke, don't fix it!

  4. #4
    Join Date
    Aug 2009
    Location
    east anglia
    Age
    49
    Posts
    95
    Rep Power
    15

    Re: trane rtad 125 chiller, reverse phase issue

    hi, its a reverse phase detection device alarm that is showing on control. spoke to trane technical and the guy on the phone seems to think it could be any electrical fault issue. going to change dual hp switch, to eliminate this.asked trane about linking hp switch out, seems you cant link this type out according to trane.all 3 phases are in right order if this helps.first contactor kicks in but fault before second contactor can kick in. thanks for replys

  5. #5
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: trane rtad 125 chiller, reverse phase issue

    Check that the Current transformer connections are good and that the ct`s resistances are balanced. Alternatively swap the compressor modules between the circuits. If the problem is transported to the other circuit the fault is with the module. Good Luck

  6. #6
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: trane rtad 125 chiller, reverse phase issue

    Usually the HP pressostat is a double one. There are two reset switches, one on top, the second on the front, when you remove the cover.

    How many CT's are there in the chiller and what type is it?
    If it ain't broke, don't fix it!

Similar Threads

  1. AEC Pinical chiller with trane comp
    By cptrdbrd in forum Commercial
    Replies: 1
    Last Post: 28-10-2009, 09:47 PM
  2. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM
  3. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 05:11 PM
  4. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •