    Electronic leak teasting



    Hi all
    Could sombody help please?
    I have just installed a freezer cold room and when it came to the pressure test, it was leaking.
    I am loosing about 2 psi/hour.
    The soapy water test came up blank.
    I am going back in the morning with the electronic tester and the question is:

    How much 404a do i need to mix with my nitrogen to enable the detector to detect ?

    appx 4mtr pipe run of 3/8 and 7/8, and a working charge of appx 12kg. (the details are still on site).

    Hope this is enough info

    Please Help, it drove me mad yesterday.

    cheers

    eggs



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Electronic leak teasting

    Before you start adding 404a to your test pressure a couple of questions/thoughts...

    Have you tried testing in sections ? Condensing unit - liquid line - evaporator - suction line. Is the condensing unit precharged ? in which case - are the line valves holding, has the condensing unit pressure increased ?

    Is your gauge set/hoses leaking ?

    Is the TEV leaking around the head ? Is your soapy water mix good and strong so that the bubbles stay on the leak and are not blown away ? Try building up your test pressure in stages so that you get an indication of when the leak starts, this can sometimes point you towards the likely size of the hole; bear in mind that an increase in pressure can push two pieces of tube together and partially close a leak off.

    Anyway Eggs, I wish you well.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Electronic leak teasting

    The trouble is the job is in a prison and we only have very short working times, because the freezer is next to the excercise yard and all tools have to be locked away before one group of convicts get banged back up and the next load of rabble go for their walkies.So we only get about 45 mins to seperate the system to test the seperate parts.

    Another frustrating day ahead me thinks !!!


    cheers eggs

  4. #4
    Join Date
    Dec 2001
    Location
    nottingham
    Age
    62
    Posts
    96
    Rep Power
    23

    Re: Electronic leak teasting

    Quote Originally Posted by Brian_UK

    Is your gauge set/hoses leaking ?
    Sounds like the cause to me

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Electronic leak teasting

    Hi Eggs.

    We have discussed the leak test using Helium.
    From what was said there, I am using today as Andy suggested 85% OFN and 15% helium.

    No need for any electronic gadgets, just soapy water, you will find the leak in seconds, check the gages as well.

    Good luck.

    Chemi

  6. #6
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Electronic leak teasting

    Found the bloody thing !
    Right in the middle of the evaporator coil.
    Funny thing is, when i opened up the system to install the pipes, there was pressure there ???
    Must have been the increase in pressure that opened the hole it up.
    Anyway "Warranty Claim"

    Cheers for the thoughts


    eggs

  7. #7
    Join Date
    Oct 2002
    Location
    australia
    Posts
    28
    Rep Power
    0

    Re: Electronic leak teasting

    why helium? how does it work in helping find a leak?

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Electronic leak teasting

    Hi adam.

    Helium molecules are smaller then OFN and therefore escape from smaller holes in the pipework so its easier to locate a leak.

    Of course you need to use soapy water or buy a special Helium leak detector (very expensive).

    Hope this answers your question.
    The best, have a go. You will be surprised from the results.

    Chemi

Similar Threads

  1. Leak detectors
    By Temprite in forum Tools and Calculators
    Replies: 54
    Last Post: 18-08-2010, 04:15 PM
  2. Evasive gas leak
    By Feeze in forum Technical Discussions
    Replies: 24
    Last Post: 18-08-2008, 07:22 AM
  3. Tiff 5000 leak detector
    By davidchesson in forum Tools and Calculators
    Replies: 6
    Last Post: 06-11-2006, 04:26 AM
  4. Can't find leak with UV Dye
    By jd_boggs in forum Transport
    Replies: 6
    Last Post: 16-09-2006, 06:22 PM
  5. Helium for leak detection
    By chemi-cool in forum Refrigerants
    Replies: 51
    Last Post: 08-03-2005, 01:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •