Fujitsu ASTA09LCC error code
Good evening,
I have installed a Fujitsu ASTA09LCC unit approximately a month ago along with an ASTA12LCC and ASTA24LCC and the ASTA09 is having issues on the heating cycle, and I am looking for advice on the fault code presented if possible?
The system on start up will operate on a low indoor fan speed, then increase to high speed by itself blowing cold air for 45 seconds and then shuts off. The error code presented is the Red and Green lights flash twice together, then the red will flash a further four times and then start the flashing cycle again.
Does any Fujitsu expert have any definitions of the code available?
Kind Regards
Frank
-
12-08-2009, 08:31 PM #2
Re: Fujitsu ASTA09LCC error code
Any Gas still in it?
Heating required in Sydney?He who dies with the most Toys, WINS!
-
12-08-2009, 10:57 PM #3
Re: Fujitsu ASTA09LCC error code
Haha! System is still full of gas. The funny thing is sometimes it will work perfectly and sometimes it provides this error.
It does get cold in Sydney in Winter! But this job was a little further north towards Newcastle
-
13-08-2009, 09:54 AM #4
-
13-08-2009, 12:11 PM #5
Re: Fujitsu ASTA09LCC error code
Spoke to our distributor here and they stated it was a code for a lock fault but couldnt determine what it meant so they will be out to check the system. They seem to feel its the indoor fan thats faulty.
-
18-08-2009, 01:05 PM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Fujitsu ASTA09LCC error code
That code is not described in service manual. Are you sure in that lamp blinking pattern?
-
18-08-2009, 03:02 PM #7
Re: Fujitsu ASTA09LCC error code
Hi Nike,
I did find it in the service manual, it was stated as lock fault on the indoor fan. Its an Australian designated unit.
-
18-08-2009, 05:51 PM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Fujitsu ASTA09LCC error code
Sorry, I understood that you wrote operation (red) 2 times and timer (green) 4 times which is not described in manual.
The indoor fan speed is 0 rpm after 56 seconds from starting operation or from the time the fan mode was changed.
> Operation stop. (It releases by sending the operation stop signal from the remote controller).
[Diagnosis Point]
Fan motor connector loose /defective contact.
Fan motor defective
Controller PCB defective.Last edited by nike123; 19-08-2009 at 04:05 PM.
-
19-08-2009, 03:07 PM #9
Re: Fujitsu ASTA09LCC error code
i have error-codes sheet on fujitsu
if u want i can post it.
-
19-08-2009, 03:56 PM #10
Re: Fujitsu ASTA09LCC error code
i have error-codes sheet on fujitsu
if u want i can post it.
Similar Threads
-
Fujitsu Multi problem
By BMS1 in forum Heat PumpsReplies: 15Last Post: 02-09-2010, 06:41 AM -
your opinons on fujitsu please
By acgibo in forum Air ConditioningReplies: 18Last Post: 26-08-2009, 05:06 PM -
fujitsu wall mount volt free relay
By mike live in forum Air ConditioningReplies: 3Last Post: 09-04-2009, 08:26 PM -
Fujitsu PCB
By gwilliamson in forum Air ConditioningReplies: 6Last Post: 10-09-2008, 10:27 PM -
Fujitsu or not?
By LRAC in forum Air ConditioningReplies: 14Last Post: 29-08-2007, 09:45 AM