Results 1 to 20 of 20
Thread: PHE's problem
09-08-2009, 09:21 AM #1
PHE's problem
would like to address this problem and hear from you how to solve it:
PHEs used in HVAC system, the contractor started up the system with out flushing it and the PHEs got filled with mud and sand as far as they say.
what could have happenned to the PHE ?? could the plates got damadged ??
if the plates are OK, can the PHE get cleaned and reused again??
yes, what would be the best way to wash the plates and the gaskets ?? (Jet water, .... etc)
i appreciate your help
thank you
09-08-2009, 09:35 AM #2
Re: PHE's problem
Doubt plates are damaged , so as you have said pull it apart and clean it .
Avoid getting any water in refrigerant channels or obvious other problems will occur .
If its sand or mud it will just wash off anyway .
You could try a reverse flush if it is possible .
If its new all gaskets should be ok , then pressure test .
09-08-2009, 09:46 AM #3
Re: PHE's problem
Thank you for your quick reply, i just want to emphesize that it is water to water Plate heat exchanger
09-08-2009, 10:29 AM #4
Re: PHE's problem
09-08-2009, 10:57 AM #5
Re: PHE's problem
Usually low pressure water would clean it in your case using a brush if necassary .
09-08-2009, 12:33 PM #6
Re: PHE's problem
If we want to avoid opening the PHEs, can we open the upper and lower flenge and clean the PHE by 3-4 bar pressurized water ??
would it clean the sand and mud ?
09-08-2009, 01:19 PM #7
Re: PHE's problem
if all else fails read the instructions !
09-08-2009, 06:23 PM #8
Re: PHE's problem
Why don't you use the CIP (Clean in Place)?. This is the process named by the ALFA LAVAL. They use chemistry cleaning products such as ALFAPHOS, ALFANEUTRA, etc...
The time-consuming work of opening plate heat exchangers can thus often be avoided by using an Alfa Laval Cleaning in Place (CIP) unit.
Regards and hope this help.To make progress is never good enough, I want to do better and better and better
09-08-2009, 06:27 PM #9
Re: PHE's problem
If its just sand and mud then a simple reverse flushing should do the trick. Chemicals are not needed.
09-08-2009, 06:31 PM #10
Re: PHE's problem
Using the Alfa Laval Tecnik is quite good. Sand can fill the space between the plates, because the space between two plates is quite narrow.
If it's an new install the guys who did thr install are responsible for cleaning it and all costs involved!
09-08-2009, 07:02 PM #11
Re: PHE's problem
I have agree with those who said revers flushing, its the best way without taking it apart.
Why there was no filter before the PHE in the firs place??
Its a must when you use PHE with such a small water passage. about 80 mesh is the right filter.
09-08-2009, 08:44 PM #12
Re: PHE's problem
If one checks the manual of the manufacturers of chillers or PHE's they all specify the use of a filter!
09-08-2009, 11:37 PM #13
Re: PHE's problem
I would suggest that these PHE were left out in the sand with the tube covers off before being fitted.
That is why Abu 3ali has this problem.Brian - Newton Abbot, Devon, UK
10-08-2009, 05:44 AM #14
Re: PHE's problem
I can only add that plate heat exchangers are the biggest con since pantyhose, difficult to work with, close tolerance , no margn for error and lot of greif.
magoo
10-08-2009, 07:19 AM #15
Re: PHE's problem
Guys thank you for your very helpful replys. i really appreciated it.
10-08-2009, 07:59 AM #16
10-08-2009, 08:02 AM #17
10-08-2009, 08:03 AM #18
Re: PHE's problem
I totally agree with the reverse flushing
10-08-2009, 01:53 PM #19
Re: PHE's problem
If it's only sand that is stock between the plates I also agree with the reverse flushing.
11-08-2009, 02:10 AM #20
Re: PHE's problem
would it be possible to invert unit when reverse flushing to make sand drop and loosen?
MFI AMP6855 defrost problem
By gliderpilot47 in forum DomesticReplies: 4Last Post: 12-01-2011, 12:11 PM -
problem with GE air con power problem
By Richie101 in forum Air ConditioningReplies: 6Last Post: 05-11-2009, 04:00 PM -
Trane CCUH oil problem
By wingman in forum Air ConditioningReplies: 25Last Post: 04-08-2009, 07:07 AM -
Saunier Duval Problem
By mallorcanangel in forum Air ConditioningReplies: 1Last Post: 10-07-2009, 01:26 AM -
Furance problem
By ALONEI in forum Trouble ShootingReplies: 10Last Post: 14-05-2008, 11:32 AM