    Speaking of automatic ex valves how many of you have used constant-pressure expansion valves in place of or in parallel with capillary tubes in air conditioning applications. They work quite well because at low-load conditions, the AXV maintains a higher suction pressure, thus preventing coil freeze-up. Additionally, at higher load conditions, the AXV maintains a lower suction pressure, thus reducing power consumption and protecting the compressor against overload.



  2. #2
    shogun7's Avatar
    shogun7 Guest

    Re: Cap tube vs AEV on AC units

    Quote Originally Posted by Marc O'Brien
    Additional considerations would have to made like whether to go critically charged or not, whether to use an accumulator and how large. These might be common considerations just that in the case of AEV's they would surely be more important.
    An automtic exp Valve with a bypass or bleeder one would need the above requirements , however, one doesn't have to use this type. Still the fact remains that since the AXV maintains a constant suction pressure, this will result in a more efficient compressor operation than the cap tube; this allows us to use a lower-capacity compressor which gives us a better COP.
    Last edited by shogun7; 30-08-2004 at 06:39 AM.

  3. #3
    shogun7's Avatar
    shogun7 Guest

    Re: Cap tube vs AEV on AC units

    Quote Originally Posted by Marc O'Brien
    You may be incorrect.
    OH, I forgot to add [using the original condenser]

Similar Threads

  1. oxidation scale in copper tube and fittings
    By DeB in forum Fundamentals
    Replies: 8
    Last Post: 23-06-2006, 09:45 PM
  2. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 06:57 AM
  3. The amazing Mr. Cap Tube
    By shogun7 in forum Domestic
    Replies: 52
    Last Post: 07-01-2006, 07:33 PM
  4. Mitsibishi VRV System 8 out of 10 units work
    By moondawn in forum Air Conditioning
    Replies: 5
    Last Post: 29-09-2005, 11:02 PM
  5. AC units as cooling units
    By Peter_1 in forum Commercial
    Replies: 11
    Last Post: 18-03-2005, 06:42 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •