    I have an eliwell controller ID COOL series, problem is on the 240v supply in to the controller i am getting 240v out of the neutral, controller works but puts 240v accross all neutrals on the cabinet disabling compressor etc, controller is brand new, anyone else had similar problems
  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,703
    Rep Power
    46
    Re: eliwell controller problems
    Hi Northdude.
    Have you tried swapping Terminals 6 and 7 over?
    Grizzly
  3. #3
    Join Date
    Mar 2001
    Location
    Derby, England
    Age
    58
    Posts
    86
    Rep Power
    24
    Sounds like you've got a broken neutral. Work backwards from the neutral at the power supply until you find the break - its probably a loose connection somewhere.
  4. #4
    Join Date
    Oct 2008
    Location
    UK
    Age
    39
    Posts
    174
    Rep Power
    16
    yes tried swapping them over and still getting live down neutral. I disconnected my neutral off the controller so all i had was the live in, i tested the neutral terminal on the back of the controller and it had 240v on it so it must be the controller. Just seems strange
  5. #5
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17
    you've lost your neutral mate.
  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,703
    Rep Power
    46
    I agree with Frosty and Chillyblue.
    I suspect they are correct.
    Good luck and plesae let us know how you get on.
    Grizzly
  7. #7
    Join Date
    Jun 2007
    Location
    South Africa
    Age
    66
    Posts
    120
    Rep Power
    17
    You have a floating neutral. Try to find a fixed neutral point and connect all your neutral wiring to this point.
    I am not always right, but I'm never wrong!
  8. #8
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19
    does the display light up?
    mmm to beer or not to beer...........lets drink breakfast
Similar Threads
  1. Eliwell 901 Controller Parameters
    By Northdude in forum Commercial
    Last Post: 09-12-2009, 12:22 AM
  2. Daikin controller
    By mchild in forum Air Conditioning
    Last Post: 02-10-2009, 07:14 PM
  3. Eliwell EWPX172AR controller
    By fridgability in forum Electrical
    Last Post: 19-12-2008, 12:32 AM
  4. Eliwell ID961E & 985E controller
    By SPBDASAN in forum Electrical
    Last Post: 01-12-2008, 07:10 AM
  5. Daikin Controller
    Last Post: 24-11-2008, 02:34 AM
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts