    Approach Temperature



    Hi all,

    I have 15 kW scroll chiller (R22) with shell and tube configuration on the heat exchangers.

    My refrigerant properties at the condenser inlet and outlet as following:-

    a) Cond in Temp = 80.6 deg C
    Cond in Pressure = 15 barg (T sat = 41.8 C)
    b) Cond out Temp = 40.9 deg C
    Cond out Pressure = 14.9 barg (T sat = 41.6 C)

    While the cooling water inlet and outlet temperature are 29.3 C and 34.7 C respectively with a flow rate of 50.5 Lpm

    From this, the approach temperature is 41.6-34.7 = 6.9 deg C.

    Why is the approach temperature is too high? Is this acceptable? Please correct if im wrong.

    Please comment.

    Regards,
    jaya



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Approach Temperature

    Quote Originally Posted by jayaeros View Post
    From this, the approach temperature is 41.6-34.7 = 6.9 deg C.

    Why is the approach temperature is too high? Is this acceptable? Please correct if im wrong.
    The approach temperature should be no more than 11C. Your approach at 6.9C is not too high.

  3. #3
    Join Date
    Jun 2008
    Location
    singapore
    Age
    41
    Posts
    34
    Rep Power
    0

    Re: Approach Temperature

    Thanks for the reply. I was thinking all this while that approach temperature should be very low; less than 2 degree C.

    I have also calculated that the effectiveness of the condenser

    Effectiveness = (T Cool water out - T Cool Water in) / (TCond sat-TCool W in)

    Effectiveness = (34.7-29.3) / (41.6-29.3) = 0.44

    I believe that effectiveness can be increased if the approach temperature is much lower. Thus, indicating the need for the sub-cooling and hence the condenser is actually undersized.

    Please correct if my understanding is wrong.

    Thanks

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Approach Temperature

    There is a difference between questioning what is acceptable and what is optimum.

    What is the intended purpose of this system? Optimum cooling in the evaporator? Optimum heating in the condenser? Both?

    No doubt lowering the approach will increase the effectiveness, but at what price? Where is the point of diminishing returns?
    Last edited by Gary; 22-07-2009 at 04:20 PM.

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Approach Temperature

    Looking through your other thread it seems that you are modifying parts of the system without considering the effect the modifications have on other parts of the system. You need to look at the system as a whole.

    Start here:

    http://www.refrigeration-engineer.co...ad.php?t=19701

  6. #6
    Join Date
    Jun 2008
    Location
    singapore
    Age
    41
    Posts
    34
    Rep Power
    0

    Re: Approach Temperature

    The system is intended for optimum cooling. Actually, i am trying to find the performance of the system, like internal entropy generation, heat transfer coefficient and etc.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Approach Temperature

    First you need to get the system working right.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  3. LG heat pump problem
    By back2space in forum Heat Pumps
    Replies: 132
    Last Post: 01-02-2009, 11:23 PM
  4. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •