    gentlemen...I am working in a ship with 4 cold chambers. I have been noticing frost build up on TXVs of meat and fish chambers. These rooms are kept at -25 degrees centigrade. The system uses R404a as refrigerants. Is frosting in this case normal or will I start looking for causes of the problem?
    Oct 2008
    mallorca, spain,
    75
    768
    Re: frost in expansion valve
    mrfrost, at-25c you would expect a bit of frost, dose the frost build up? have you seen the system go onto de- frost
    let us know what happenes ,
    Jul 2009
    philippines
    5
    Thanks for the reply sedgy. The frost builds up but seems to decrease during defrosting. Defrosting is set at about 30minutes every 12 hours.
    Oct 2008
    mallorca, spain,
    75
    768
    mrfrost, can you make a note of suc, pressure , discharge pressure, supperheat? and which type of de-frost please?
    Mar 2008
    55
    273
    Quote Originally Posted by mrfrost View Post
    Hi there, You could see if this helps ,Set room temp at -21 as colder than this is not needed for meat or fish. Also defrost period is incorrect, I would sugest you set these rooms up for 4 defrosts per 24 hours with a 30 minute duration. Try this and report back with results
    Transvestites are men who like to eat, drink, and be Mary.
    Oct 2004
    Scotland
    1,454
    21
    Dirty expansion valve filters.
    Chillin
    and go get a cuppa
    Jul 2009
    philippines
    5
    Thanks for your replies...
    sedgy, yes I will provide you data later...
    chillin out, i have already cleaned the TXV filters...
    philfridge, yes I will try that.
    I appreciate your help...
    Jul 2009
    philippines
    5
    Hi guys
    The system is ok as of now. Seems that philfridge got it. Thanks to you all.
    Feb 2008
    adelaide sth.oz
    1,015
    ya better tip his scales then
    Jul 2009
    New zealand
    47
    15
    Hey i agree with chillin out check the filters on in the expansion valve, also what suction pressure are you getting?
  1. LEV does not open
    By Yuri B. in forum Air Conditioning
    Last Post: 19-07-2009, 02:37 PM
  2. Actual Expansion Valve Process
    By AastroGuru in forum Fundamentals
    Last Post: 03-02-2009, 09:53 AM
  3. Setting of Hand expansion valve
    By Iceehot in forum NH3
    Last Post: 10-09-2008, 01:25 AM
  4. the function of the electronic expansion valve
    By Crystal-426 in forum Fundamentals
    Last Post: 22-06-2008, 12:29 PM
  5. Need Divine Intervention - plugged drier or expansion valve?
    By archibaldtuttle in forum Trouble Shooting
    Last Post: 08-06-2008, 06:52 PM