hi guys, quick question, when commissioning a DX system (TEV) with evap in air handling unit, what load isit best to use?
ie, the air handler can either blow full fresh air over the coil or it can exchange some heat with the internal air?
on a summers day it may be 28'C ambiant external which would be alot of load on the evap, isit best to start with full fresh air when commissioning to allow for worst case load situations.
-
20-07-2009, 11:02 PM #2
Re: commissioning DX air cooled
Just try and acheive the design conditions for the coil, that's all you can do really.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
21-07-2009, 12:21 AM #3
Re: commissioning DX air cooled
Use the force Luke
If not have you got pre-heat or use re-heat on recirc you can use to supplement the load?
As Brian says you just got to try get as close to the coil spec as poss.Quidvis Recte Factum Quamvis Humile Praeclarum.
Latine dictum, sit altum videtur.
Si hoc comprehendere potes, gratias age magistro Latinae.
Similar Threads
-
reusing heated water from water cooled cond.
By Richvacr in forum Technical SpeculationsReplies: 5Last Post: 11-02-2011, 10:55 PM -
Refrigerant Temperature in the Water/Air Cooled Chiller
By jinx in forum FundamentalsReplies: 16Last Post: 19-02-2009, 11:43 PM -
EC and Air cooled condensers working in parallel
By Josip in forum NH3Replies: 9Last Post: 30-01-2009, 07:50 AM -
Water Cooled System
By puddleboy3 in forum Air ConditioningReplies: 15Last Post: 08-05-2008, 12:31 PM -
Standard of Commissioning
By supermarketguy in forum CommissioningReplies: 3Last Post: 28-06-2007, 12:43 AM