Results 1 to 14 of 14
Thread: How to design a simple condenser
16-07-2009, 12:02 AM #1
I am a student which involves in a project which needed to build a refrigeration system, and the part that I am responsible to, is design an air cooled condenser which do not have a fan to cool it, because the system is an outdoor unit, so we plan to use natural wind to cool it, and I do not have any clue on how to start.. can anyone guide me?
And is it possible if I just asked the manufacturer of copper finned tube to bent the 6.5m tube in a coil shape and use it as a condenser?
16-07-2009, 01:24 AM #2
Re: How to design a simple condenser
You will need to speak to a manfacturer/ wholesaler and provide him with the total heat of rejection* If you dont know this, the unit model, refrigerant, ambient temperature the condenser will operate in,the expected minimum wind velocity over the condenser and the application so the THR*and condenser size can be calculated.
16-07-2009, 01:47 AM #3
The refrigerant will be using R134a, ambient temperature will be around 20c and minimum wind velocity will be 0.. This is because when there is wind, the system will only then generate, will be using the wind turbine to drive the compressors.. and the minimum wind speed when the compressor can work is 3m/s..
16-07-2009, 01:55 AM #4
16-07-2009, 06:49 PM #5
Hello Waisk.
Water is better. I would stake on the power of ocean(s) in your coutry-continent surrounded by them - from compressors powering to the whole refrigeration cycle.
16-07-2009, 08:01 PM #6
Originally Posted by waisk
They operate on convective air currents only. Hot air rises and pulls cooler air behind the warm air flow upwards.
If this is for an engineering class you need to do some calculations on establishing convection air currents induced by the temperature differential achieved between the design condensing temperature and the ambient air.
If this is for a shop class you might try to find an old refrigerator that has a similar type of condenser and scale it up. Measure the condenser tubing length, height, width, etc. Next...try to find the compressor size.
Use the above to proportion the new condenser from what the old one is.If all else fails, ask for help.
17-07-2009, 01:23 AM #7
17-07-2009, 01:45 AM #8
Finned tubing could help reduce the size of the condenser, however, the fins can also accumulate dust and dirt too, which reduces the heat transfer rate.
Try looking for convection heat transfer on Google.If all else fails, ask for help.
17-07-2009, 03:38 AM #9
Oh.. I am an engineering student, and doing a final year project which is similar to a refrigeration system. The project is using the mechanical power of the wind turbine to power up the compressor. The compressor that we are using is taken out from a car. So, I planned to use the finned tubing to stimulate the condenser. But I am not sure the total length of the tubing that I needed to use, and also the size of the tubing as well.
I have searched about the convection heat transfer from the google. And slightly know what is that mean, and for my case, it is natural convection, and you mentioned that calculate the convection air current, is that mean the Rayleigh number?
17-07-2009, 07:06 AM #10
Check the rear of any fridge or freezer in your house. It has that black pipe that feels hot, at the back of the unit. It's usually inter connected with thin wire.
That's the condenser you want to build.
If you take some temperature readings and have a look at the convection airflow across it, it's a good place to start. You may even get kw readings and compressor sizes etc.
It's a place to start from.
17-07-2009, 07:19 AM #11
First calculate thr as follows :
Refrigeration load + motor kw at design condition + 20% for pull down
and you can get a condenser from yr mkt
17-07-2009, 04:15 PM #12
I know how the refrigerator condenser look like after I searched the image from google. But how to have a look at the convection airflow? And the compressor that we have is from a car, and as I know the car condenserhave a lot of fin and also a fan in it. So, how do I actually need to modify my condenser? The compressor have a power rating of 1kw.
17-07-2009, 04:16 PM #13
21-07-2009, 11:49 AM #14
Product load + lossess etc put together will be your cooling load
parallel flow condenser design for appliance a.c
By saurabh_23jan in forum Air ConditioningReplies: 2Last Post: 14-11-2008, 06:12 AM -
method to design air cooled condenser
By abbasi in forum New TechnologiesReplies: 4Last Post: 12-02-2008, 08:34 AM -
Efficient Water-Source Condenser Design?
By Enginerd in forum FundamentalsReplies: 4Last Post: 28-05-2007, 05:11 AM -
air cooled condenser design
By abbasi in forum FundamentalsReplies: 1Last Post: 26-03-2005, 08:33 PM