    Thermosiphon Issues



    Hi Guys,

    We have a plant that runs on NH3, single stage approx 10MW Refrigeration Capacity,

    However we have a new Thermosiphon system (approx 3 years old) and every now and then, (more so in the summer) it is causing the compressors to trip on high discharge temp/high oil temp,

    There is usually no problem when all 7 Compressors are running ''UNITL'' one compressor cycles off on temperature and then we have 2-3 compressors alarming on high oil temp, sometimes if left it will sort itself out (after approx 15-20mins) and the oil temperatures will go back to normal 52 degree's,

    Other days there are no issues at all,

    The thermosiphon system is a closed loop circuit, and has a dedicated condensor which controls @10.5BARg,
    The liquid level is 3/4 full, so plenty of liquid present, its like the other oil cooler(s) are being starved once 'a' compressor is turns off.
    To hand I don't have any info on the oil coolers but will get access to this tommoro.
    There are no valves on the liquid inlet to the oil cooler or outlet ,only isolation valves.

    Any ideas?

    Regards



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Thermosiphon Issues

    What you are describing sounds like some other systems I have seen. These are usually piping related issues that cause liquid to not be available where it is needed. This can be the result of vapor locking or flow issues.
    If all else fails, ask for help.


  3. #3
    Join Date
    Apr 2009
    Location
    Durban
    Age
    70
    Posts
    31
    Rep Power
    0

    Re: Thermosiphon Issues

    What about oil logging and can you give us a piping layout showing traps?

  4. #4
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Thermosiphon Issues

    Quote Originally Posted by freezerman11 View Post
    Hi Guys,

    We have a plant that runs on NH3, single stage approx 10MW Refrigeration Capacity,

    However we have a new Thermosiphon system (approx 3 years old) and every now and then, (more so in the summer) it is causing the compressors to trip on high discharge temp/high oil temp,

    There is usually no problem when all 7 Compressors are running ''UNITL'' one compressor cycles off on temperature and then we have 2-3 compressors alarming on high oil temp, sometimes if left it will sort itself out (after approx 15-20mins) and the oil temperatures will go back to normal 52 degree's,

    Other days there are no issues at all,

    The thermosiphon system is a closed loop circuit, and has a dedicated condensor which controls @10.5BARg,
    The liquid level is 3/4 full, so plenty of liquid present, its like the other oil cooler(s) are being starved once 'a' compressor is turns off.
    To hand I don't have any info on the oil coolers but will get access to this tommoro.
    There are no valves on the liquid inlet to the oil cooler or outlet ,only isolation valves.

    Any ideas?

    Regards
    Can you give us more information about condenser, receiver? How do you control 10.5 bars(pumps, fans sequence)?

  5. #5
    Join Date
    Jan 2008
    Location
    newzealand
    Age
    47
    Posts
    44
    Rep Power
    0

    Re: Thermosiphon Issues

    US iceman is right, what type of receivers and condensers are being used? If it occurs more in summer then one thing to look at would be the condensers.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Thermosiphon Issues

    Quote Originally Posted by benji
    If it occurs more in summer then one thing to look at would be the condensers.
    It depends on what the problem is. I have seen some that operated fine in the cool months and later find out the summer problems were due to the oil cooler itself.

    These are just like gravity flooded evaporators. When they do not work it is a pain to fix.
    If all else fails, ask for help.


  7. #7
    Join Date
    Sep 2007
    Location
    UK
    Age
    60
    Posts
    45
    Rep Power
    0

    Re: Thermosiphon Issues

    I've seen one of these systems where the thermosiphon oil coolers are totally seperate from the main plant, the thermosiphon phx is mounted above a liquid receiver and uses the pond water from the evaporative condensers. The pressure is controlled by inverter driven pumps to 10 Bar. Is the liquid line common to all oil coolers & has the system been balanced?

    Pavilion

  8. #8
    Join Date
    Sep 2007
    Location
    India
    Age
    60
    Posts
    3
    Rep Power
    0

    Re: Thermosiphon Issues

    Hi FM11
    First isolate individual compr by stopping them.Then close the isolation valve for Liquid in and out of oil cooler. Drain the trapped Nh3 liquid safely to outside. while doing so if there any oil trapped in the oil cooler refrigerant area it will get drained out. After that flush it with Nitrogen to remove all the trapped oil if any.Then put back this compressor in operation.Similarly carry out the same for balance 6 comprs and observce. This this plant is working for 3 years with Thermosyphon, it could be one of the problem. Best of luck

  9. #9
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Thermosiphon Issues

    Ask a question and never respond... Oh Well

  10. #10
    Join Date
    Jul 2009
    Location
    New zealand
    Age
    47
    Posts
    15
    Rep Power
    0

    Re: Thermosiphon Issues

    Have you got an auto-purger on your system? if not also check for non-condensables as this would cause a difference in pressure in the oil cooler restricting the liquid seal.

  11. #11
    Join Date
    Jan 2008
    Location
    UK
    Posts
    16
    Rep Power
    0

    Re: Thermosiphon Issues

    hey guys,
    sorry I haven't replied, have not been on for sometime now to respond,

    the problem was a heavily fouled condenser.
    Checked the sump water temperature and found that there was a 4C-5C split from the condensing temperature.
    Purged air from condensor and seems to be ok so far.
    Thanks for all the help!!

Similar Threads

  1. NH3 thermosiphon oil cooler
    By cygbob in forum NH3
    Replies: 38
    Last Post: 22-06-2008, 05:12 PM
  2. Propane compressor suction drum level issues
    By inuendo in forum Trouble Shooting
    Replies: 8
    Last Post: 02-06-2008, 09:19 AM
  3. Replies: 3
    Last Post: 27-11-2007, 10:00 AM
  4. Liquid injection vs thermosiphon oil cooling
    By Josip in forum Technical Speculations
    Replies: 25
    Last Post: 25-07-2007, 09:42 PM
  5. Blast freezer related issues ~~
    By spiderman in forum Fundamentals
    Replies: 5
    Last Post: 24-05-2007, 07:59 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •