    Cvgd trouble



    sorry about my english. i have trouble with my cvgd. indicated b E7. please help me



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Cvgd trouble

    What is a CVGD please?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Cvgd trouble

    Quote Originally Posted by daywalker View Post
    sorry about my english. i have trouble with my cvgd. indicated b E7. please help me
    Try yellow pages. Turn to 'air conditioning contractors' pick up phone and arrange for an engineer to visit.

  4. #4
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Thumbs up Re: Cvgd trouble

    Hi,
    bE7 is a high motor temperature fault indication.
    Check the motor cooling line ( 1 1/8 ), the line running from the bottom of the condenser pot to the motor.
    There is an inline filter, a temperature drop across this filter would indicate a blockage.
    If the motor is still cool whilst running I would then suggest that you check the Thermistor Terminals in the small junction box between the rear of the motor and the condenser.
    First Isolate the Main and control circuit supplies, then remove the small junction box cover.
    Inside are 4 spade terminals. Check for continuity and balanced resistance across the terminals. 1 common and 3 Thermistor readings +- 75ohm @75F.
    If any thermistor is open circuit this is your problem.
    Good Luck

  5. #5
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Thumbs up Re: Cvgd trouble

    Trane Water Cooled 2 stage Centrifugal Chiller.R134a /R12

  6. #6
    Join Date
    Jun 2009
    Location
    indonesia
    Age
    51
    Posts
    8
    Rep Power
    0

    Re: Cvgd trouble

    Quote Originally Posted by centrecipew View Post
    Hi,
    bE7 is a high motor temperature fault indication.
    Check the motor cooling line ( 1 1/8 ), the line running from the bottom of the condenser pot to the motor.
    There is an inline filter, a temperature drop across this filter would indicate a blockage.
    If the motor is still cool whilst running I would then suggest that you check the Thermistor Terminals in the small junction box between the rear of the motor and the condenser.
    First Isolate the Main and control circuit supplies, then remove the small junction box cover.
    Inside are 4 spade terminals. Check for continuity and balanced resistance across the terminals. 1 common and 3 Thermistor readings +- 75ohm @75F.
    If any thermistor is open circuit this is your problem.
    Good Luck
    Thx for your solution

Similar Threads

  1. Trouble shooting tx valves
    By TECH TIM in forum Trouble Shooting
    Replies: 11
    Last Post: 01-02-2011, 06:13 PM
  2. books for Trane trouble shooting
    By RobertK in forum Refrigeration Books
    Replies: 11
    Last Post: 15-07-2009, 12:17 PM
  3. MD-II SR Trouble Codes
    By lherring81 in forum Transport
    Replies: 8
    Last Post: 22-05-2009, 12:18 AM
  4. How to trouble shoot a system
    By US Iceman in forum Trouble Shooting
    Replies: 12
    Last Post: 16-02-2007, 09:23 AM
  5. Trouble Shooting
    By Vincent Yu in forum Fundamentals
    Replies: 20
    Last Post: 22-11-2005, 03:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •