Results 1 to 2 of 2
Thread: Tonnage calculation
-
25-06-2009, 11:21 AM #1
Tonnage calculation
Hi All, i have struck up with some queries!!!
can anybody help me out for calculating the TR of an unit, by taking superheat and subcooling temperature...is there any formula for it or is there any calculator for this
And as we are using R410a refrigerant for the first time, i also would like to know the superheat and subcooling range of temperature for it, and its Low pressure(LP) and high pressure(HP) recommended.
-
25-06-2009, 05:58 PM #2
Re: Tonnage calculation
hi if u are trying tu calculate how much tonnage u are getting out of your unit this is the correct and easy calculation
delta t *1.8 *500*GPM divided by 12000= TR
Similar Threads
-
Need Help in Refrigeration Calculation
By Jason_09 in forum FundamentalsReplies: 7Last Post: 30-06-2009, 07:10 PM -
Calculating Tonnage of refrigeration machine
By batmon18 in forum CommercialReplies: 6Last Post: 09-06-2009, 11:21 PM -
Flash gas calculation software
By nike123 in forum Tools and CalculatorsReplies: 4Last Post: 12-03-2009, 09:25 AM -
NH3 thermosiphon evaporator calculation
By cygbob in forum NH3Replies: 3Last Post: 27-11-2007, 10:00 AM -
Cooling load calculation
By raviperumal in forum Technical DiscussionsReplies: 6Last Post: 02-03-2007, 04:09 AM