11-07-2004, 09:30 AM #1
Trane Air cooled condenser
I have been asked to look at this unit, it’s a dual circuit condensing unit with two compressors on each side.
The problem is on start up in hot weather they bang out on h/p intermittently, discharge go’s to 29 bar straight away and triggers the h/p. another company looked at the unit last summer and suggested non return valves, I think the fault is that on start up both compressors on each circuit are coming on at the same time I think there should be a delay, as usual there is no info on site the unit is nearly 3 years old.
-
11-07-2004, 09:54 AM #2
Re: Trane Air cooled condenser
fridge geezer will be here for this one..get model numbers first though
cheers
richard
-
11-07-2004, 10:50 AM #3
Re: Trane Air cooled condenser
Originally Posted by jan behnke
Condensor is selected/made for those two compressors.
And it worked always in the past.
You can easily try it yourself by switching off one compressor (for example push on the button of the overload relay or unscrew a wire of one relay or fit a switch between one relay....)
Is there a liquid receiver?
TEV or capillary?
How fast is it going in HP? Is it in a few seconds or after some minutes?
If it is in minutes, how high is discharge temperature and liquid out of the condensor?
If it happens in a few seconds, you probably have a restriction somewhere.
If it is in a longer time (speaking in terms of 30 seconds to minutes) then possible causes: tech before you overcharged it (probably he charged in the winter till his HP was OK and then overcharged it)
Air entered in the system?
Clogged dryer?
Condensor clean?
Has the other tech charged wrong gas in the system?
Is it that airco model (can't find/remember the type number) with the 2 independent compressors with their own condensor, woven into each other) or is it more a high capacity model with Trane scrolls with the electronic PCB board?
Advice: First check if you have no restriction somewhere (dryer, service valves..) Then evacuate gas, vacuum system and restart complet with gas charging. Then you're sure for yourself that there is no air in the system, proper gas and proper gas filling. You eliminate so many possible causes.
Let this forum know what you found. We all can learn of it.
-
11-07-2004, 06:07 PM #4
Re: Trane Air cooled condenser
Hi Jan.
Had similar problem some time ago. Condensers were of the roof. Installed NRV on each discharge line about 20cm after the discharge king valve and problem gone.
Tha discharge line was full with oil and on start up there was hydraulic pressure and HP tripped.
To make sure, close the king valve and realese some pressure into a bucked and see what comes out - gas or oil.
Chemi
-
11-07-2004, 09:15 PM #5
Re: Trane Air cooled condenser
Thanks for your help i think traped oil could be the problem the AHU are about 15m above the unit, there are mag valves fitted to the liquid line's ( i wonder if they are slow to open)
comps are not scrolls and no electronics,
-
11-07-2004, 10:06 PM #6
Re: Trane Air cooled condenser
Originally Posted by jan behnke
Is there no siphon fitted in the discharge just after the compressor?
This is then a fault of whom initiallty installed the system.
-
12-07-2004, 06:09 AM #7
Re: Trane Air cooled condenser
Chemi could be right
Chemi
-
12-07-2004, 11:41 AM #8
Re: Trane Air cooled condenser
Originally Posted by chemi-cool
-
12-07-2004, 12:52 PM #9
Re: Trane Air cooled condenser
Chemi could be right ???????????????
This is what it should look like.
Chemi
-
13-07-2004, 09:48 PM #10
Re: Trane Air cooled condenser
Ta Richard!
Right, Jan, what's the model no. for a start, and please describe the installation - pipe run, pipe size, refrigerant, riser length - any traps fitted?
If it's a 3 year old Trane, and it's got 4 compressors, then it's probably a 3-D scroll or similar. Are the compressors CSHA100k / 150K's? I see that there's no SMM (computerised controller)...
Got to go - I'll try to answer more at work tomorrow.
-
14-07-2004, 07:27 AM #11
Re: Trane Air cooled condenser
I have been booked in to return some time this week, i will get all the info, yes it has four scrolls in it, as far as i can see there are no oil traps, from memory liquid 1 1/4 suction 2 1/4 inch 3 bends in the pipe run about 15m away from the cond,s all above the unit
-
14-07-2004, 09:11 AM #12
Re: Trane Air cooled condenser
Originally Posted by jan behnke
-
14-07-2004, 09:31 AM #13
Re: Trane Air cooled condenser
No, the AHU consists only of the evaporator coil, fan and filters and the condensing unit holds the condensor and compressor.
So the evaporator is 15 m. above the condensing unit, a common setup I should say.
-
14-07-2004, 02:58 PM #14
Re: Trane Air cooled condenser
A common problem with this type of setup is migration of liquid to the evaporator during the off cycle. Gravity delivers the migrated liquid down the suction line to the compressor, causing problems at startup.
Looping the suction line up above the evaporator then down to the compressor traps the liquid in the evaporator.
Liquid line solenoid valves can prevent the migration if they are at the evaporator, especially if they pump down before the unit shuts off. If the solenoid valves are at the condensing unit (without pumpdown), then the contents of the liquid line will end up in the evaporator, and possibly the compressor.Last edited by Gary; 14-07-2004 at 03:00 PM.
-
26-07-2004, 08:19 AM #15
Re: Trane Air cooled condenser
Hey Jan, have you got the details yet? If I know what the unit is, I might have an IOM somwhere that will tell us if you need traps, etc. Or is the problem solved?
ATB
FreezerGeezer
-
27-07-2004, 08:37 PM #16
Re: Trane Air cooled condenser
Sorry have not been back to it yet, due to work load, but there is on thing, there are two scroll,s in each circuit, looking in the panel i think tere was four delay timers for all the comp contactors, but when each circuit came on there was no time delay for the second comp they both came on at the same time, would this cause the head pressure to go to 29bar in a few seconds and trip the h/p, if there was a delay would this lower the head pressure on start up.
thanks Jan
-
28-07-2004, 02:02 PM #17
Re: Trane Air cooled condenser
Hello Jan
Yes, it may be possible, especially if the condenser fans aren't kicking in correctly. I seem to remember an IOM from Trane that said that traps were required in the liquid line if the evap. was higher than the condenser, to stop oil & liquid forming too heavy a seal on the condenser. However, I may well be getting mixed up. I need to talk to someone on that. It would really help if we knew the model no. of the unit. I take it that this one is electro-mechanically controlled, rather than with a SMM (computerised controller for Trane 3-D scrolls)? Trane normally have a compressor on-on delay of a couple of minutes on SMM controlled scrolls, if I remember right.
-
28-07-2004, 02:26 PM #18
Re: Trane Air cooled condenser
Hi Jan.
It was not clear from what you have written if the condenser is higher then evaporator or the other way around?
Scrolls take time to build up high pressure not like reciprocating that build it up in no time.
Please, post a clear description of the unit.
It will make it easier to come up with an idea.
Chemi
-
28-07-2004, 07:22 PM #19
Re: Trane Air cooled condenser
would this cause the head pressure to go to 29bar in a few seconds and trip the h/p,
-
28-07-2004, 07:34 PM #20
Re: Trane Air cooled condenser
Hi Frank.
In the case where SV is closed, there is no suction, therefore, the head pressure will not rise much even if condenser fans not working at start up.
The condenser is designed for tow compressors so I don't think the problem is there.
Gauges should be fitted to see if the pressure is that high at start up or maybe the pressure controll is foulty.
Un fortunatly, Jan doe's not supply enough details we kind of guessing all the time.
Chemi
-
28-07-2004, 10:09 PM #21
Re: Trane Air cooled condenser
Hi Marc
That's what I was thinking - I'll have to see if I can find the IOM I mentioned earlier.
Jan, any more detail you can add would be good. Is there anyone on site who can supply the model no?
-
31-07-2004, 10:47 AM #22
Re: Trane Air cooled condenser
More likely the IOM referred to trapping the discharge line if the condenser is higher than the compressor.
-
02-08-2004, 08:25 AM #23
Re: Trane Air cooled condenser
Hi Gary, Marc. Yes, I think you're right - as I said, I can't remember the thing exactly, and it may well be talking about remote condenser applications. Anyway, I'll see what I can find. If I ever get 5 minutes to look!
-
03-08-2004, 12:46 PM #24
Re: Trane Air cooled condenser
Traps are for oil,if the condenser is higer than the compressor they should be installed on the discharge line every six metres of vertical pipe.If the compressor is higher traps should be installed on the liquid line but not more than one as there's the risk of flash gas,that's liquid gas that evaporates when the balance between pressure and temperature is lost.To help avoid this you should have a high subcooling.
-
05-08-2004, 07:31 AM #25
Re: Trane Air cooled condenser
Sorry have been left out of the loop on this one by my service manager, asked him what was happening, the owners of the kit have looked at there service records and decided to call back the company that installed it apparently it been like this since it was installed. I would like to know the out come so I will try and find out, thank you all for your time and effort, its nice to know there is a lot of great help out there.
Similar Threads
-
method to design air cooled condenser
By abbasi in forum New TechnologiesReplies: 4Last Post: 12-02-2008, 08:34 AM -
How to adjust head on a water cooled condenser
By kengineering in forum Technical SpeculationsReplies: 5Last Post: 30-05-2007, 10:37 PM -
water cooled condenser shell type
By abbasi in forum New TechnologiesReplies: 0Last Post: 27-04-2005, 08:32 AM -
air cooled condenser design
By abbasi in forum FundamentalsReplies: 1Last Post: 26-03-2005, 08:33 PM -
water cooled condensers
By aaron crimmins in forum FundamentalsReplies: 2Last Post: 22-07-2002, 04:24 PM