    R502 Replacement.



    Got a Frozen Food Coldroom on R502 which due to leak on remote condensor has lost gas.

    A company has been previous to my visit but no gas ID label is on unit. Exp valve is R502 so I will have to assume that R502 is what is in the system. Customer does not recall what engineer did on previous visit.

    If I use R404A what oil do I need and do I need to do anything with expansion valve i.e orifice size (not sure of size at mo)?

    Or is there another gas I could use that involves no oil change and minimal adjustments R407A for example?

    Thanks



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: R502 Replacement.

    Hi lucas.

    Personally, now adays I don't like the retrofits.

    With 404A you need to use POE oil.

    For flushing Contact your refrigerant supplier.
    Capacity don't change but you have to install new TEV for 404A - the same capacity.
    As oil and dirt stays at the bottom of the receiver. It need to be replaced and of course 404A compressor.

    Pressure controlls will have to be re adjusted.

    Good Luck

    Chemi

  3. #3
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: R502 Replacement.

    Hi lucas

    Just to expand on chemis valid points Retrofitting is the way to go long term.However FX10 (R408A) will drop in the place of R502 with minimal problems,Available from HRP etc.( phase out period applies).

    Best regards

    Mark

  4. #4
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: R502 Replacement.

    Hi Lucas,
    As Mark says, R408A is the short term drop in replacement and i have used in on loads of occasions and works fine.

    At the end of the day to convert to R404 is going to cost and with the age of the equipment is it really worth it. I have so far never conveted a unit to 404 purely because of the cost compared to the short term life of that age of a unit. Either scrap the whole unit & but a new more reliable one or just use 408

    Regards

    Raymond

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: R502 Replacement.

    Why can't you have a look at the last engineers report sheet to see what work he carried out on the system? Surely the customer should have a copy?

  6. #6
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: R502 Replacement.

    Use Drop In Isceon R69 or R403B

  7. #7
    Join Date
    Sep 2003
    Location
    UK
    Posts
    54
    Rep Power
    21

    Re: R502 Replacement.

    No report history available otherwise I would of read it.

    Thing that amazes me is that the unit is not even labeled for R502 nor are there any signs of labels being removed. Just cannot understand why people cannot take time to label things!

    Will suggest customer has to look at new equipment but for now go for the drop in option. Unit at least 12-15 yr old so cost has to be a factor here, so as ever it is up to the customer and as usual they will go for cheapest option of course guaranteed.

  8. #8
    Join Date
    Jan 2002
    Location
    Long Beach Ca
    Age
    48
    Posts
    47
    Rep Power
    0

    Re: R502 Replacement.

    stateside 502 replacement most common now is 507 , poe retro, same valve most applications

  9. #9
    Join Date
    Jun 2001
    Location
    Gloucestershire
    Posts
    13
    Rep Power
    0

    Re: R502 Replacement.

    Hi Lucas,
    Why don't you try ISCEON 79 its not HCFC based like R408A but it can be used with same oil type that is in system.


    Regards

    Peter

  10. #10
    Join Date
    Aug 2004
    Location
    Holland
    Posts
    55
    Rep Power
    20

    Re: R502 Replacement.

    For the rare occasion where we encounter R502 and have to change to the refrigerant, we use HP 80 = R402a just drop in, no oil or tev change, works perfect, in holland is is a gas witch will be phased out in future.

    BTW wats wrong with selling a new and modern installation.

    Regards Victor

  11. #11
    Join Date
    Dec 2001
    Location
    nottingham
    Age
    62
    Posts
    96
    Rep Power
    23

    Re: R502 Replacement.

    FX10 works well as a drop in, just remember to charge system to correct operating pressures, i have found systems in the past charged to a full sight glass have been way over charged

  12. #12
    Join Date
    Jun 2004
    Location
    Wirral UK
    Age
    58
    Posts
    68
    Rep Power
    20

    Re: R502 Replacement.

    R402a R402b R403 R408a Are all pretty much the same in the feild in my experience. Depending on the size of the system if it is quite small I would advise the customer to prepare himself to pay for the cost of a new system in the next couple of years. If however it is larger I would sugest looking at changing it over to a longer term replacement. I recently was involved with a R502 Blast Freezer that had been changed over to R22 by company policy and then changed over to Isceon 59(R417a) It works really really well and out performs it's 25 year old design spec. It is quite a big blast freezer though.
    "It's better to remain silent and be thought a fool than open ones mouth and remove all doubt"

  13. #13
    Join Date
    Apr 2002
    Location
    Hamilton, Canada
    Age
    58
    Posts
    26
    Rep Power
    0

    Re: R502 Replacement.

    why would someone want to use HP80. too high of a discharge pressure, causes allot of gtief in the summer time with high head problems, anything i service that was 502 and now HP80, needs a sprinkel on the condenser in summer

    go to 404 or 507 (less glide) and POE oil, no need to change TEV

  14. #14
    Join Date
    Nov 2007
    Location
    USA
    Posts
    17
    Rep Power
    0

    Re: R502 Replacement.

    Stan
    In the west cost R-507 is popular
    In the east cost R-404A is popular
    most supply hoses dont carry more then 3 to 4 jugs of R-507

  15. #15
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: R502 Replacement.

    Quote Originally Posted by yoelyeve View Post
    Stan
    In the west cost R-507 is popular
    In the east cost R-404A is popular
    most supply hoses dont carry more then 3 to 4 jugs of R-507
    Have you noticed the dates on these posts.
    I doubt you are going to get relevant replies!
    Grizzly

  16. #16
    Join Date
    Nov 2007
    Location
    USA
    Posts
    17
    Rep Power
    0

    Re: R502 Replacement.

    Shaun
    I have 4 Ice cream plant's running on R-408A and I'm getting better performance then R-404A by about 6% even on a 95F day
    Box temp About -22F
    Dont need no sprinkler

  17. #17
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: R502 Replacement.

    Quote Originally Posted by yoelyeve View Post
    Shaun
    I have 4 Ice cream plant's running on R-408A and I'm getting better performance then R-404A by about 6% even on a 95F day
    Box temp About -22F
    Dont need no sprinkler
    This thread iis over 6 years old
    My wife used to say you never listen to a word I say at least I think that what she said

Similar Threads

  1. R 417 A direct replacement of R 22
    By abbasi in forum Refrigerants
    Replies: 28
    Last Post: 08-09-2011, 12:47 AM
  2. Replacement stat
    By Lucas in forum Domestic
    Replies: 13
    Last Post: 02-08-2006, 11:28 PM
  3. R-22 replacement
    By shogun7 in forum Refrigerants
    Replies: 1
    Last Post: 26-07-2004, 07:57 AM
  4. F 11 replacement for flushing
    By andrewuk in forum Refrigerants
    Replies: 1
    Last Post: 17-10-2003, 11:03 PM
  5. Best refrigerator, R22 or r502
    By AndrOvr in forum Refrigerants
    Replies: 2
    Last Post: 08-07-2003, 03:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •