    Problematic unit, please help



    Hi all,

    I am having a bit of a problem with a package unit on r407c. I have recently repaired a leak and recharged the unit but now 2weeks down the line the unit is going out on low pressure AND high pressure.

    I have a good air flow over the evapourater and condenser.

    I am getting a suction pressure of around 3.5 bar but this then drops to about 1 bar slowly as the condenser fan comes in and out until the lp switch triggers. and I have measured the evap outlet pipe surface temp of 13 degrees. this gives me high superheat (correct me if im wrong).

    Does the system seem to have sprung another leak? or could I have a problem with the tev underfeeding?

    Thank you in advance for anyones views



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Problematic unit, please help

    Is it cap tube or TXV?

    What is the subcooling?

    What is the superheat?

  3. #3
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Problematic unit, please help

    It is TEV, I was getting a subcooling measurement of approx 10 degrees

    and a superheat of around 17 degrees

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Problematic unit, please help

    ^ We assume that you are talking Centigrade readings.....
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Problematic unit, please help

    Quote Originally Posted by Brian_UK View Post
    ^ We assume that you are talking Centigrade readings.....
    Sorry, yes that is correct

  6. #6
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Problematic unit, please help

    it does sound like you could have a blocked filter before or after the TEV depending on what mode you have it in or the TEV is getting jammed.
    What model of unit is it as if it is a multi speed condenser fan motor one of the relays could be gone on the pcb so it thinks it is running in medium fan speed but the fan speed turns off.
    what mode are you in and what is the model number?
    You should check the cycling of the condenser fan motor in all speeds and also chck for icing at the TEV.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Problematic unit, please help

    Yes, it sounds like some sort of intermittant blockage. Or possibly moisture freezing in the TXV and then defrosting when the high side pressure/temperature rises (fan off).

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Problematic unit, please help

    I would be de-canting system charge, evacate system. And start again with fresh system charge. From memory R407C is a ****tail blend, so which bit did you lose with the leak.
    Just a thought. I stand to be corrected.
    magoo

  9. #9
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Problematic unit, please help

    Thanks for the input so far guys

    I re-charged with new r407c with it being a zeotrope I didnt want to take any risks,

    There is slight frosting around the t.e.v and the pipes branching off it too which made me think the t.e.v is ok (might be wrong).

    As for the condense fan It is a lennox package unit LHA088 model Ithink the speed is single speed (again I mite be wrong), I have replaced the Full PCB as I had a spare to hand,to eliminate this.

  10. #10
    Join Date
    Jun 2009
    Location
    Scotland
    Age
    60
    Posts
    34
    Rep Power
    0

    Re: Problematic unit, please help

    less8110, in one of the previous posts you noted a supertheat reading of 17C. Given that the system was operating as intended this would be a cause for concern since the almost universal setting for most TX valves is 6C. Remenber below 4C the differential is too slight to allow the valve to operate as intended.
    I suggest that you revist the site and having established good running conditions check the value again- with a view to adjusting towards the 6C value. During this process conformation of improvement should be evident with better heat rejection from the condenser and improved duty over the coil.
    The risk in not checking is that the superheat cooling provided for the compressor is not adequate and therefore you could have a failure in the near future.
    If you can recheck and post it would help any additional thoughts.

    tmm

  11. #11
    Join Date
    Nov 2008
    Location
    australia
    Posts
    136
    Rep Power
    16

    Re: Problematic unit, please help

    hi ,
    sounds like there might still be a little bit of moisture in the system maybe? did you use a vac stat? ester oil is very hygroscopic .
    let us know how you go with it.
    ct

  12. #12
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Problematic unit, please help

    Ok guys, I fitted a new TEV to this last week and it seems to have ran ok since, the pressures settled to a constant and it was cooling away unlike before!

    I also noticed when I had removed the old tev the part number didnt match up to the new one Lennox had sent me, having given them the serial number of the unit, and after a bit of research it turned out the tev fitted should have been on the cond coil (heat pump, dual tev). So makes me wonder if this unit has ever cooled properly until now!

    Thanks for all the input guys
    Last edited by lees8110; 25-06-2009 at 09:02 PM.

  13. #13
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Problematic unit, please help

    Two/three weeks down the line and it has gone out on LP again!!!
    What is wrong with this unit!!?
    According to the client this unit has run fantasticly in the previous hot weather we have just had until now!
    I had a quick play with the unit and I noticed if I run the unit in heat ( bypassing the evap tev) it runs perfect and then when I switch back to cooling after doing this it does run ok until it reaches desired room temp then when it starts back up it goes out on LP again.
    This sounds to me like the one way check valves could be sticking??? or do the symptons give something else off?

    Please help if anybody could offer their advice

    Thanks Lee

  14. #14
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Problematic unit, please help

    Evap air in temp
    Evap air out temp
    Low side pressure
    Suction line temp at TXV bulb

    Cond air in temp
    Cond air out temp
    High side pressure
    Liquid line temp at condenser outlet

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Vrv
    By tgoonter in forum Air Conditioning
    Replies: 4
    Last Post: 11-01-2011, 06:25 AM
  3. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  4. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM
  5. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •