    This is a pic from a Copeland Semi 8Hp control panel.
    I need to identify certain components........ie: 3 phase protection , etc

    From the pic can any members identify??
    Last edited by Abe; 11-01-2006 at 10:34 AM.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Control Panel

    Hi Abe.

    QSG is main isolator.
    QM1 is compressor overload
    KM1 is compressor contactor
    QM2 is fan overload
    KM2 is fan contactor
    QM7 is "0" protector
    KT1 is a timer most probably short cycle protection
    KA2 is a control relay and so is the other.

    the control box is not connected to the mains, why?

    Thats what I can see from here (4500KM away)

    Does it help?

    Chemi

  3. #3
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Control Panel

    Hi Chem,

    You did a brilliant job analysing the photo, from far away. !!!
    I need to take in what youve put down............
    How did you manage to read the stuff on the devices???
    You must have eyes like an eagle !!

    The system is not connected.......

    I disconnected it, the compressor is not working,

    You would make a very good sleuth.........( detective !!! )
    lol

  4. #4
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Control Panel

    Now on the existing set up, if I lost a phase, would QM1 trip and shut the compressor down??

    I think Im confused between what a phase protection device is and what a overload device is

    Are the both the same? Can they both do the same job?

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Control Panel

    My eyes are not so good but my reading glasses are as thick as a Coca-Cola glass bottle's bottom.

    Its prety clear Abe.
    If you want to add a phase sequence protector, connect it after the main isolator and from the QM7 take the "0" through the NC contacts.

    That should do the job.

    Forgot to mention, I use photoshop to play with the picture

    Chemi

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Control Panel

    Hi Abe.

    I've sent you a pdf showing a phase sequnce data sheet.

    Too big to post her.

    Chemi

Similar Threads

  1. Replies: 21
    Last Post: 05-07-2008, 10:48 AM
  2. Control scenario
    By Mike Hopkins in forum Technical Discussions
    Replies: 5
    Last Post: 14-09-2007, 11:25 AM
  3. Searle cellar cooler control problem
    By iceman007 in forum Electrical
    Replies: 6
    Last Post: 06-07-2004, 08:57 PM
  4. New Capacity Control Solution
    By embrown in forum New Technologies
    Replies: 19
    Last Post: 30-12-2003, 01:33 PM
  5. Pego Control Panel
    By Abe in forum Trouble Shooting
    Replies: 4
    Last Post: 24-10-2001, 07:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •