    Domestic Bottle Chiller



    Hello everyone

    Can someboby tell me how to test a small single phase compressor to see ifs its electrically faulty, can this be done with a multimeter or do you have to have some other tester ( its probably a simple answer) and if there is any websites on electrics and how to test and use various electrical equipment

    Thanks :



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Domestic Bottle Chiller

    Hi Flump,

    First check that none of the three electrical connections (pins) are down to earth.

    Measure the resistance at each of the pins against the other two. You should end up with three different readings, the sum of two of them adding up to the third measurement.

    That's the start, the compressor may be electrically OK but can still be stuck.

    Good hunting.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Domestic Bottle Chiller

    Hi FLUMP.

    First, check with a Megger for earth loop.

    If you post manufacturer name and model, I can tell you what resistance you should read.

    But the most simple way without any tools is to connect it through a RCB, make sure earth is connected and start it.

    If it runs ok then motor is OK. If it trips. replace, no need for other tests.
    Now check theif it holds discharge and suction pressure.
    Holds, fine. If not, replace.

    chemi

  4. #4
    Join Date
    Dec 2002
    Location
    uk
    Age
    45
    Posts
    10
    Rep Power
    0

    Re: Domestic Bottle Chiller

    Thanks Chemi

    How did you get one with the container. So you really just need a meggar to make sure the compressor is down

    Thanks
    Flump

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  2. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  3. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  4. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  5. Chiller Fault
    By iceman007 in forum Air Conditioning
    Replies: 2
    Last Post: 13-05-2006, 07:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •