Results 1 to 14 of 14
Thread: They ran it backwards
14-06-2004, 05:47 PM #1
I have a customer that ran their 3 ton Copeland scroll compressor backwards for the weekend. How can we verify the compressor is shot. R-22 system high side 140, low side 135. that about sums it up dosen't it?
14-06-2004, 06:29 PM #2
Re: They ran it back wards
They can't run back wards!!
There is a kind of clutch to prevent it.
But they sure can burn back wards.
Verify that compressor is shot?
Install a green led marked RUN parallel to the contactor coil. When its off, compressor is shot.
Chemi
14-06-2004, 06:34 PM #3
Re: They ran it backwards
Thanks Chemi, We have a run light installed on the system, which is "on" by the way. The compressor is running, but it is not generating any pressure. I'm fairly confident that this compressor is shot...
14-06-2004, 06:44 PM #4
Stop it before it burns and change direction of rotation.
I belive its a three phase compressor cause if its not then the shaft inside might be broken.
Chemi
14-06-2004, 06:52 PM #5
They can run backwards.
First thing you need to do when starting up a scroll is measuring pressures HP and LP. When they 're not in the expected range, reverse phases and check again.
After some time, you will hear if he's pumping correct (and feel it on the discharge and suction lines on the compressor)
You also can install a reverse phase protector (like Daikin do in his AC's)
I suppose you changed phases and problem remained the same?
If so, my advise: replace compressor, suction filter.
Normally they can run a long time backwards but the main thing which is happening in the first running hours is a very fine grinding, iron of upper scroll againts iron of lower scroll with some oil between i tso that they fit exactly together.
A scrolls pumping capacity increases after some running hours due to this grinding.
Good lesson afterwards, open up the compressor and look what happened.
Share it with us.
My gues: scrolls completely worn/grinded out the wrong way.
Or the internal safety check valve has opened and stays open.Last edited by Peter_1; 14-06-2004 at 06:55 PM.
14-06-2004, 07:05 PM #6
I had this a while ago and it was covered in an old thread http://www.refrigeration-engineer.co...96&postcount=1. Hope the link works as it's the first time I've tried to paste a link!
Ooops - try this one http://www.refrigeration-engineer.co...02&postcount=4
How do we do it properly Dez?
14-06-2004, 07:05 PM #7
Yes, phase is three phase. customer reversed phase and problem still exists. No cooling and the pressures are equal.
14-06-2004, 07:09 PM #8
Hi Peter,
The last scroll I've replaced was turning backwards and made a bad noise, changed direction and it was fine.
The Copeland people here told me to check direction but if you say it can run backwards I'll have to open one and see how it works on the inside.
chem
14-10-2004, 04:59 PM #9
Originally Posted by chemi-cool
It explains and shows how a scroll worksLast edited by Coolie; 14-10-2004 at 05:00 PM. Reason: missed out some info
03-12-2004, 01:13 PM #10
Originally Posted by nighter1
Explain us why you see it otherwise but you're completely wrong.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
04-12-2004, 05:35 AM #11
Originally Posted by Arkma
Most scroll designs have a groove machined into the scroll "tips" where a "tip seal" is inserted. The tip seal's sole purpose is to prevent leaks when the fixed and orbiting scrolls are mated together and running.
Copeland's scroll elements are precision machined to microns of an inch in length, providing a metal-to-metal sealing surface that polishes itself in over time. It actually improves the surface microfinish as it runs but if it runs backwards any length of time the sealing surface is destroyed and the compressor is for all practical purposes useless
04-12-2004, 02:24 PM #12
Likewise the saturated suction temp (SST) will be near ambient temp, and the suction line cannot be above ambient, so the superheat will be low, not high.
Low SCT and high SST is common to both inefficient compressors (abnormal) and high efficiency systems (normal). It is not quite as simple as you think. In this particular case, it is extreme enough to be obvious, but in a borderline case, the symptoms you describe are not going to tell you what you need to know.
04-12-2004, 06:23 PM #13
Sorry, but English is not my mother language so your explanation was almost not understandable for me.
It's no critic on you personally but you must use shorter sentences, comma's, more points and start new sentences with a capital.
Your statement were 2 sentences.
Although, I tried to read what you said and tried to understand what you said but you re-invented the hot water and turned centuries old thermodynamics laws upside down.
I see now when reading next posts to yours that also Gary disagrees with you.
Something else... when I was at Copeland Welkenraedt (here in Belgium) where they make the scroll compressors, I asked there if a compressor can break mechanically if it runs a longer time backward.
They said it will not break but the motor will be cooled not enough and it will trip on thermal safety. But it will not break the scroll itself.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
23-12-2004, 04:36 AM #14
wesmaxWes Maxfield
Fan running backwards
By dnuse in forum ElectricalReplies: 23Last Post: 27-11-2006, 04:20 AM -
Danfoss compressor running backwards
By kengineering in forum Technical DiscussionsReplies: 19Last Post: 04-05-2006, 09:42 PM -
Capacitor query
By Coolie in forum Trouble ShootingReplies: 14Last Post: 05-11-2004, 06:35 AM -
HP w/Scroll
By subzero*psia in forum Air ConditioningReplies: 3Last Post: 08-01-2003, 07:20 PM