All , i want to know that what is the procedure to check the thermostatic expansion valve
i have uninstalled the valve from the unit and i want to check that will it work after installation or not.
(danfoss 407c 7.5 ton)
06-05-2009, 07:37 PM #2
Re: thermostatic expansion valve
Measure the superheat at design conditions.
07-05-2009, 10:38 AM #3
Why do you want to check it if you have un-installed it it needs to be installed to check correct operation, you could always take it apart and check the internals for a rough idea
11-05-2009, 11:21 AM #4
Thans for the so suitabe idea
14-05-2009, 07:05 AM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
If you already uninstalled TXV, than it is usually cheaper to install new one than install it back to found out that is faulty and then repeat all again. If you uninstalled it, change it!
14-05-2009, 12:31 PM #6
physical examination of valve might be of help such as damaged bulb, kinked capillary , bellow inside for visual crack if any . Function test only after you start system & observe design parameters.
15-05-2009, 11:12 AM #7
thanks All
for suggestions and the time to send
03-06-2009, 04:43 PM #8
TEV and TXV is one and the same?
03-06-2009, 04:58 PM #9
03-06-2009, 05:02 PM #10
Hello Gary. May one accronym be in American usage, another in British? (only which where?)
03-06-2009, 05:05 PM #11
I have heard it both ways on both sides of the pond, but TEV seems to be far more commonly used outside of the USA.
03-06-2009, 05:05 PM #12
Yes, thank you - TXV is rather the obsolete term.
thermostatic expansion valve sizing
By ank_gl in forum Air ConditioningReplies: 2Last Post: 03-03-2009, 03:22 PM -
Actual Expansion Valve Process
By AastroGuru in forum FundamentalsReplies: 11Last Post: 03-02-2009, 09:53 AM -
Thermostatic Expansion Valve TXV - Block Type
By AastroGuru in forum FundamentalsReplies: 10Last Post: 24-12-2008, 09:53 AM -
the function of the electronic expansion valve
By Crystal-426 in forum FundamentalsReplies: 10Last Post: 22-06-2008, 12:29 PM -
Need Divine Intervention - plugged drier or expansion valve?
By archibaldtuttle in forum Trouble ShootingReplies: 4Last Post: 08-06-2008, 06:52 PM