    Copeland Scroll shutting down



    I have a Copeland Scroll #ZB11MA-TWD-551 that keeps shutting down on the motor protection module. it shuts down about 3 sec after it starts. We at one time thought we had it nailed down to a voltage imbalance, however the last time it shut down the voltage was pretty equal across all three legs. At least it was within the 3% that Copeland recommends. Anyone know how common it is for these modules to go bad? The module is a Kriwan 071-0547-00. This system will work sometimes and sometimes it won't. It seems once it runns past a 1/2 hr or so the customer is fine until he shuts it down on the weekend.

    By the way this compressor is being used on a 15 ton water cooled portable chiller, making chilled water at 50 F. System parameters when running 18F sh, 12F sc, 280 hp, 50 lp.

    Any advice on what to do next?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Copeland Scroll shutting down

    hi arkma,

    i would suggest first to disconnect the compressor from the system and let it run for a minute with no resistance.

    if the guts are ok then the problem could be an obstruction in the discharge.

    compare the the head pressure with another compressor.

    scrolls are very sensitive to high pressure=heat.

    please let us know what you have found.

    chemi

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Copeland Scroll shutting down

    I have found for you some more information, have not read it yet, I hope it will shed some more light.

    http://www.copeland-corp.com/americas/ae1302.pdf

    chemi

  4. #4
    Join Date
    Jan 2003
    Location
    Buffalo, NY
    Posts
    21
    Rep Power
    0

    Re: Copeland Scroll shutting down

    Chemi,
    Thanks for all the info...at this point I don't have the luxuary of having the customer disconnect the compressor. I'll keep you posted..anything else you can think of would be helpful.

    Arkma

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Copeland Scroll shutting down

    Telling us the pressures doesn't do much good if we don't know what refrigerant is being used.

  6. #6
    Join Date
    Jan 2003
    Location
    Buffalo, NY
    Posts
    21
    Rep Power
    0

    Re: Copeland Scroll shutting down

    Sorry...R-22

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Copeland Scroll shutting down

    The high side pressure seems excessive. Is the condenser clean? Is the fan running in the right direction? At what points are you measuring subcooling and superheat? Is the compressor above or below the evaporator?

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Copeland Scroll shutting down

    Is this a TXV system? Does it have an EPR or other capacity control device? How is the water temperature being regulated? How exactly is the subcooling and superheat being calculated?

  9. #9
    Join Date
    Jan 2003
    Location
    Buffalo, NY
    Posts
    21
    Rep Power
    0

    Re: Copeland Scroll shutting down

    Unit is water cooled. Compressor is below the evap by about 1 foot. Subcooling at the outlet of the reciever, superheat at the TX bulb.

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Copeland Scroll shutting down

    Quote Originally Posted by Arkma
    Unit is water cooled. Compressor is below the evap by about 1 foot. Subcooling at the outlet of the reciever, superheat at the TX bulb.
    Is the condenser using tower water or domestic water? What are the condenser entering and leaving water temps?

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Copeland Scroll shutting down

    Whenever the compressor is below the evaporator there is a potential problem on startup.

    During the off cycle, liquid refrigerant will accumulate in the coldest part of the system, which is usually the evaporator. If the suction line loops above the evaporator before going down to the compressor, then that liquid is contained in the evaporator. However, if the suction line goes straight down to the compressor, then gravity will deliver that liquid to the compressor, and the compressor can be full of liquid on startup.

    Options are to loop the suction line above the evap and/or to close a liquid line solenoid on shutdown with or without pumpdown, so that refrigerant cannot travel to the evap. Another option would be to install an accumulator to catch the liquid.

    Compounding this, if the system has been overcharged, there is more refrigerant to gather in the evap.

    I am looking for clues here, and that high side pressure jumps right off the page at me.
    Last edited by Gary; 09-06-2004 at 02:02 PM.

  12. #12
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Copeland Scroll shutting down

    Arkma,
    It should be polite if you told us what was wrong with the unit.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  13. #13
    Join Date
    Jan 2003
    Location
    Buffalo, NY
    Posts
    21
    Rep Power
    0

    Re: Copeland Scroll shutting down

    Quote Originally Posted by Peter_1
    Arkma,
    It should be polite if you told us what was wrong with the unit.
    We rplaced the module and the unit has been running fine ever since. Sorry I didn't get back to you guys, your always so helpful. Not very thoughtful on my behalf.
    Mark

Similar Threads

  1. Compressor shutting down on overtemp?
    By Larry2 in forum Air Conditioning
    Replies: 50
    Last Post: 01-08-2006, 11:36 PM
  2. Portable chiller shutting down on High Head
    By Arkma in forum Trouble Shooting
    Replies: 10
    Last Post: 17-06-2005, 01:24 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •