    Robertshaw Controls



    Hi All

    wondering if any can help.

    I need the cut out and cut in resistances for a Robert Shaw MP50-9203 Gaurd-Pak V motor protection system.

    Its fitted on a compressor for York LCHM60, at the minute its locked out and I am averaging 1.4 ohms across all three sensors.
    If this is within its running parameters then i know its knacked, if it isnt isnt then i will need to look into this further.
    Attached Images Attached Images



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Robertshaw Controls

    Has the Red L.E.D. on the opto isolation board gone out?

    This lights to say motor protection is good.
    No light means an issue.
    Although I suspect you already know this from what you have said?
    Grizzly

  3. #3
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Robertshaw Controls

    hi coolments york motor protection on these compressors ntc as the motor gets hot then the ohms readings come down,the readings start at around 1.7k and come down to about 300 ohms and then the module cuts out so your readings are fine and your module is knackered,any other compressor problems let me know and i might be able to help
    Last edited by GHAZ; 24-04-2009 at 08:26 PM.

  4. #4
    Join Date
    Mar 2007
    Location
    uk
    Age
    51
    Posts
    120
    Rep Power
    18

    Re: Robertshaw Controls

    Quote Originally Posted by Grizzly View Post
    Has the Red L.E.D. on the opto isolation board gone out?

    This lights to say motor protection is good.
    No light means an issue.
    Although I suspect you already know this from what you have said?
    Grizzly
    thanks grizzly, didnt know that about the light, i just know i had an open circuit across T1 & T2. that tips logged in the memory now.

  5. #5
    Join Date
    Mar 2007
    Location
    uk
    Age
    51
    Posts
    120
    Rep Power
    18

    Re: Robertshaw Controls

    Quote Originally Posted by GHAZ View Post
    hi coolments york motor protection on these compressors ntc as the motor gets hot then the ohms readings come down,the readings start at around 1.7k and come down to about 300 ohms and then the module cuts out so your readings are fine and your module is knackered,any other compressor problems let me know and i might be able to help
    Thanks for that info, i will get one on order and get back there to fit it.

Similar Threads

  1. Johnson Controls.
    By Jacek in forum Chit Chat & Service Stories
    Replies: 15
    Last Post: 03-03-2010, 10:02 AM
  2. Controls
    By shogun7 in forum Technical Discussions
    Replies: 2
    Last Post: 28-01-2010, 01:26 AM
  3. defrost controls
    By chilldis in forum Electrical
    Replies: 3
    Last Post: 20-04-2009, 12:48 AM
  4. Honeywell Residential Controls
    By bethlehemtech in forum Tools and Calculators
    Replies: 2
    Last Post: 12-07-2008, 12:24 AM
  5. Electronic Controls
    By Bones in forum Supermarket Refrigeration
    Replies: 16
    Last Post: 04-04-2004, 06:52 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •