    Compressor selection issue



    hi,
    We are designing a heat pump to aid a domestic water heater for our senior design project at Arizona State University and I am having trouble finding a compressor that will work for my needs.
    here are the specs. it needs to handle:

    refrigerant: r410a
    Freq: 60hz
    voltage: 120 V
    Capacity: 5585.17 Btu/hr
    pressure: from 159 to 525 psi
    efficiency: around 70%


    Thanks,
    Paul.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Compressor selection issue

    Any rotary compressor for modern split system AC will do that pressures/temperatures. Check Toshiba, Daikin, Matsu_s_hita, Sanyo, Mitsubishi spare compressors for their split system AC-s of that capacity.

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Compressor selection issue

    Your isentropic efficiency at 70% is probably asking for a lot - nice if you can get there. Most would be closer to the 60% mark at high temp.

    Why R-410A for a water-heating heat-pump? Don't you need a fluid with a higher critical temp? What temperature do you want to heat your water to?

    Have you looked into alternative refrigerants?
    Last edited by desA; 07-04-2009 at 06:09 AM.

  4. #4
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: Compressor selection issue

    Dear You can look for samsung rotary comporessor
    G4C065JU, slightly higher in capacity.
    thanks
    amit

  5. #5
    Join Date
    Apr 2009
    Location
    tempe, AZ
    Posts
    5
    Rep Power
    0

    Re: Compressor selection issue

    Amit,
    Thank you for the response, It has been really helpfull. I have a couple of questions for you:
    1) is the fact that the compressor is for 50Hz instead of 60Hz something I should worry about? I don't think that frequency will work here in the US

    2) as far as the capacity being higher, can I adjusted so that it works at the capacity that I want or does it matter at all?

    for DesA,

    R410a is a requirement for the design. This is because we are part of the energy and environment concentration for ME and ASU requires us to use that type of Refrigerant. Trust me, if we could use R-22 instead we would've already be done with the whole thing!!

    For Nike123,

    Thanks for the name brands, I'll check them out right now.


    Thanks for your suggestions.

    Paul.

  6. #6
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Compressor selection issue

    for DesA,

    R410a is a requirement for the design. This is because we are part of the energy and environment concentration for ME and ASU requires us to use that type of Refrigerant. Trust me, if we could use R-22 instead we would've already be done with the whole thing!!
    No need for R-22 - I don't touch it in my heat-pumps. Why not use R-134a? Have a look at its critical temperature compared with a blended refrigerant (R410a).

    For a hot-water heat-pump, you need a refrigerant which operates some 'distance' from its critical temperature.

    Last edited by desA; 08-04-2009 at 12:56 AM. Reason: corrected spelling

  7. #7
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: Compressor selection issue

    DearASU,

    1. What i feel, as the motor is designed for 50Hz but it can also be used in 60Hz it will not make much difference as the comp is slightly overdesigned.
    2.Yes capacity can easily be adjusted with the help of Expansion valve, hence if you select this comp and use the exp valve which is only of capacity required, then comp can not deliver more.
    3. My suggestion is that as your usage is for heat pump so i would recommend R 407C.

    Thanks
    Amit

  8. #8
    Join Date
    Apr 2009
    Location
    tempe, AZ
    Posts
    5
    Rep Power
    0

    Re: Compressor selection issue

    amit,

    I have been trying to get pricing for the samsung compressor model G4C065JU you gave me and I can't find any dealers that would carry that. Do you know of any websites or catalogs I might be able to get that price from?
    thanks,
    Paul

Similar Threads

  1. computer& communication room ac's reliability issue
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 13-04-2009, 10:19 AM
  2. TGV issue
    By pawelkrystek in forum Transport
    Replies: 2
    Last Post: 13-11-2008, 08:23 AM
  3. Flood back issue?
    By Arc in forum Trouble Shooting
    Replies: 15
    Last Post: 28-10-2008, 03:40 PM
  4. CRAC(computer room ac) cost saving issue
    By Lc_shi in forum New Technologies
    Replies: 0
    Last Post: 15-04-2008, 08:22 AM
  5. hydraulic floor heating issue
    By Lc_shi in forum New Technologies
    Replies: 6
    Last Post: 02-01-2007, 09:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •