    Air Energy Heat Pump for swimming pool



    Hi all i have been asked by a friend to look at his heat pump ( An Air Energy 550Ti1 ) for his pool, it seems that when he sets the temperature to 32 degrees c, the monitor says 32 but the water temperature is actually 25 degrees c.

    The system runs on R407C and the pressures are

    70psi suction i presume and 300 discharge.

    The water sensor seems fine.

    Can anyone shed some light on why the water temperature is not reading what it says on the controlls.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Air Energy Heat Pump for swimming pool

    Can you calibrate the temperature controller -7°C?

    Your head pressure is too high, check it.

  3. #3
    Join Date
    May 2008
    Location
    spain
    Age
    54
    Posts
    63
    Rep Power
    16

    Re: Air Energy Heat Pump for swimming pool

    Quote Originally Posted by chemi-cool View Post
    Can you calibrate the temperature controller -7°C?

    Your head pressure is too high, check it.
    Hi Chemi-cool thanks for the quick reply.

    Can you give me a step by step proceedure on how to calibrate the temperature controller as i have no experience in pool heat pumps.

    Thanks

  4. #4
    Join Date
    Jan 2009
    Location
    Canary Islands
    Age
    74
    Posts
    144
    Rep Power
    16

    Re: Air Energy Heat Pump for swimming pool

    Hi Debonair. I'm reasonably sure that the discharge pressure and apparent error with temperatures are linked. Most of these heat pumps have the sensor within the heat exchanger inlet, but frequently after the first condenser coil. If the water flow is too slow, the water will have started absorbing heat and this will show on the controller. At the same time, and this is relatively important, the slow water flow ahs the same result as partly covering the coil on a condenser set! Result - high discharge pressure and temperature.
    Make sure both valves in the water system are fully open, and that the by-pass is either closed (diverting all flow through the HP), or open no more than a third. Suction pressure is about right for R407, but increasing water flow should reduce discharge to around the expected 250/275 (19/20Bar).
    Have had experience of this kind of problem before - I have found 'tinkeritis' the biggest culprit!! Best of luck.

Similar Threads

  1. Design heat pump for a pool
    By rolandh in forum Heat Pumps
    Replies: 10
    Last Post: 23-09-2010, 10:50 AM
  2. Pool heat pump water side diagram
    By nike123 in forum Heat Pumps
    Replies: 23
    Last Post: 22-03-2009, 07:42 PM
  3. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  4. swimming pool heat pump
    By Andy AC in forum The Trail of Tears
    Replies: 8
    Last Post: 26-08-2007, 04:02 PM
  5. Thermal Efficiency of Refrigeration System
    By hussain316 in forum Refrigeration Books
    Replies: 5
    Last Post: 31-07-2007, 08:59 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •