    Panasonic Cassette



    Hi guiys i have a problem with a panasonic cassette Indoor - CS-F50DB4E5
    Outdoor - CU-B50DBE8

    Now what happens is after 10 mins of running the unit shuts down the compressor and outdoor fans as if it was cycling off. Problem was return air was at 19 degrees and i had it set at 16. So i held the air on sensor to heat it up and nothing unit would not cut back in. So i turned the unit off and back on at the remote and unit kicked in.

    I spoke to service center and they said may be a thermistor problem. I have previously installed new PC Boards to indoor and outdoor unit have i done something wrong? There is no wall controller only remote so i can only go by fault code LED on the outdoor unit.

    Here are my temp readings.
    Indoor on High Fan speed - Air ON - 19 degrees
    Air Off - 5-7 degrees
    Suction pressure was about 750kpa on R410a

    Condensor Outdoor fans appeared to be on high fan.
    Air On - 30.5 degrees
    Air off - 23.5 degrees

    Compressor Amp draw was 8.2 amps on all 3 phases.

    Thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Panasonic Cassette


  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Panasonic Cassette

    Quote Originally Posted by rude View Post
    I have previously installed new PC Boards to indoor and outdoor unit have i done something wrong?
    If error is occurred after that, than you probably done something wrong.

  4. #4
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Panasonic Cassette

    Well what oringinally happened was i was getting a coms error. Turned out to be the interconnection cable. So i changed the boards and then changed the cable. It did say to run a test mode on cooling for more than 5 mins then switch off to allow heating to run.

    Its a strange fault. Maby i should run the cooling test for longer than 10mins and see what happens.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Panasonic Cassette

    Quote Originally Posted by rude View Post
    Well what oringinally happened was i was getting a coms error. Turned out to be the interconnection cable. So i changed the boards and then changed the cable.
    I taught that we should first check cables and then change boards.

  6. #6
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Panasonic Cassette

    haha i was 1 step ahead of you

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

  8. #8
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Panasonic Cassette

    I have to pay to access that. Ill get a service manual tommorow at work. I usually fix these things with some success but this ones a strange one.

  9. #9
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Panasonic Cassette

    Panasonic will not cool below 19, run it in test mode to check pressures etc., temps look fine to me.

    al

  10. #10
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Panasonic Cassette

    Quote Originally Posted by al View Post
    Panasonic will not cool below 19, run it in test mode to check pressures etc., temps look fine to me.

    al
    i have ran it in test mode and all pressure were fine from what i could see. But i only ran it for 10mins. Im sure the ac is capable to run below 19? It says no where in the manual that it cant. It specifys a temperture setting of 16-31.

    I think what im going to do is change the sensors. But before i do that run the test mode for say 15-20 mins, because as i see in test mode it would by pass any set points? So if it does run id say it would be a sensor issue. I hope im right.

  11. #11
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Panasonic Cassette

    I would have run it in test mode if possible to see whether it's cutting out on percieved temp or due to another reason.
    I was going to suggest that yesterday, but because I don't remember much about pana cassettes, I thought I'd leave it for someone like stefscruiser to comment on, or the official tech suport guys that you could use. The last pana cassettes I saw were around the corner from you, next to the TAB office on hassler rd, and that was over two years ago.

    As far as pana not cooling below 19C, it may be the case with casettes, I don't know. But I know most of their remotes go down to 16C, it would seem strange if they would only cool to 19C, when the other brands that can only go down to 18C, can manage 18C.
    But anyway, I wouldn't be changing any more parts until you can talk to stef or whoever is their tech support on the phone.

    edit: I forgot, I have an old ducted pana doing the same thing. Some old lady says the house gets warm, she turns it off and then on again at the controller and it fires up again. I've checked everything and it seems oK, and of course it all works perfect when I'm there, no fault codes, no dodgey readings. Of course I don't want to spend too much time there and charge this old lady heaps of money sitting around waiting for it to fault, and they aren't too good at keep records or remembering exactly was was happening at the time or noticing when it stops until an hour later. But it sounds like a similar fault, although this unit will run for days without stopping, not minutes like yours. But both need to be turned off then on again to fire it back up.
    Last edited by paul_h; 03-04-2009 at 03:01 PM.

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Panasonic Cassette


  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Panasonic Cassette

    .............................
    Last edited by nike123; 03-04-2009 at 09:52 PM.

  14. #14
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Panasonic Cassette

    Quote Originally Posted by paul_h View Post
    I would have run it in test mode if possible to see whether it's cutting out on percieved temp or due to another reason.
    I was going to suggest that yesterday, but because I don't remember much about pana cassettes, I thought I'd leave it for someone like stefscruiser to comment on, or the official tech suport guys that you could use. The last pana cassettes I saw were around the corner from you, next to the TAB office on hassler rd, and that was over two years ago.

    As far as pana not cooling below 19C, it may be the case with casettes, I don't know. But I know most of their remotes go down to 16C, it would seem strange if they would only cool to 19C, when the other brands that can only go down to 18C, can manage 18C.
    But anyway, I wouldn't be changing any more parts until you can talk to stef or whoever is their tech support on the phone.

    edit: I forgot, I have an old ducted pana doing the same thing. Some old lady says the house gets warm, she turns it off and then on again at the controller and it fires up again. I've checked everything and it seems oK, and of course it all works perfect when I'm there, no fault codes, no dodgey readings. Of course I don't want to spend too much time there and charge this old lady heaps of money sitting around waiting for it to fault, and they aren't too good at keep records or remembering exactly was was happening at the time or noticing when it stops until an hour later. But it sounds like a similar fault, although this unit will run for days without stopping, not minutes like yours. But both need to be turned off then on again to fire it back up.
    I did speak to tech support as was told it may be cutting out on a low coil temp. But i know the gas charge is correct because i weighed it in. The only other thing they said maby a sensor was dodgy. Problem is the unit doesnt have a wired remote control so it doesnt display any codes. All i have is a remote with no check function. Ill see if these new sensors do anything, if they dont work ill have to sort it out with tech support. Just thought someone on here might have come accross it.

  15. #15
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Panasonic Cassette

    all brands i've seen have set point of 16, none cool below 18/19, rather than changing sensors why not order a controller? shouldn't be too expensive and can be used on all such systems? if no leds are flashing then the unit doesn't appear to be seeing a fault?

    al

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Panasonic Cassette

    After studying service manual for a while, I would also say that frost prevention control is acting and that you should check indoor heat exchanger thermistor for proper value against actual coil temperature before doing anything else.
    Test function will probably not override that function.

    Remove thermistor from PCB and put it in water-ice mixture. It should have 67,3KOhm +-5% resistance.
    If that is OK than PCB is faulty or connection to PCB has cold solder/bad contact.
    Are you sure that thermistors are not interchanged when you changed PCB's?
    They have similar values and unit may not see that as abnormal thermistor value.
    Last edited by nike123; 03-04-2009 at 10:07 PM.

  17. #17
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Panasonic Cassette

    Quote Originally Posted by nike123 View Post
    After studying service manual for a while, I would also say that frost prevention control is acting and that you should check indoor heat exchanger thermistor for proper value against actual coil temperature before doing anything else.
    Test function will probably not override that function.

    Remove thermistor from PCB and put it in water-ice mixture. It should have 67,3KOhm +-5% resistance.
    If that is OK than PCB is faulty or connection to PCB has cold solder/bad contact.
    Are you sure that thermistors are not interchanged when you changed PCB's?
    They have similar values and unit may not see that as abnormal thermistor value.
    I did check that they were plugged into the correct sockets on the board. I will check the resistance of sensors and go from there. i have ordered the new ones so i can check between the new and the old ones for any differance.

  18. #18
    Join Date
    Sep 2007
    Location
    Dorset
    Age
    55
    Posts
    8
    Rep Power
    0

    Re: Panasonic Cassette

    when changing the boards its always a good idea to change the probes aswell. most faults lie with the probes and not the boards anyway

  19. #19
    Join Date
    Feb 2008
    Location
    QLD
    Age
    54
    Posts
    74
    Rep Power
    17

    Re: Panasonic Cassette


    only remote so i can only go by fault code LED on the outdoor unit.
    Is the unit displaying any faults? the outdoor PCB will indicate this with LED's

    If not, than the micro must think that everything is perfectly normal.
    Not quite sure why anybody would want a temp lower than 19 degrees C, but I would be checking the RA sensor.

    Where are you measuring the room temp, is it possible that some air is being deflected back into the unit? Sometimes it is good to cable tie your digitemp sensor with the RA sensor, to get a clearer idea.

  20. #20
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: Panasonic Cassette

    Dear Check for the sensor which is controlling the Compressor cycling as i feel it is misplaced as there is no problem with your unit.
    thanks
    amit

  21. #21
    Join Date
    Sep 2006
    Location
    New Zealand
    Age
    54
    Posts
    17
    Rep Power
    0

    Re: Panasonic Cassette

    Check indoor coil for blockage, had something similar to this awhile back and coil was choked up. Anti freeze protection stopped unit for 45 mins at a time.Cleaned coil and now all good.

  22. #22
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Panasonic Cassette

    Quote Originally Posted by Below 0 View Post
    Check indoor coil for blockage, had something similar to this awhile back and coil was choked up. Anti freeze protection stopped unit for 45 mins at a time.Cleaned coil and now all good.
    Isn't then dT at indoor coil would be higher than 12-14K?

  23. #23
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Panasonic Cassette

    Quote Originally Posted by stefs_cruiser View Post
    Is the unit displaying any faults? the outdoor PCB will indicate this with LED's

    If not, than the micro must think that everything is perfectly normal.
    Not quite sure why anybody would want a temp lower than 19 degrees C, but I would be checking the RA sensor.

    Where are you measuring the room temp, is it possible that some air is being deflected back into the unit? Sometimes it is good to cable tie your digitemp sensor with the RA sensor, to get a clearer idea.
    I did tie the digitemp to the plastic to get the RA. I only had it running on 16 to test. They had it set on 22 but felt no cooling on a hot day.

    ive been on holidays for a week so hopefully ill get back out there some time this week.

  24. #24
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Panasonic Cassette

    OK bit of an update. Changed all sensors indoor and outdoor. Problem still occured. So i tested on heating and the unit ran for 20mins with no faults.

    But on cooling wouldnt run for any more than 10mins. So i decided to put in the old indoor pc board that i had previously replaced and ran the unit and it started working!!!

    So i really have no idea why or how it fixed itself but it did.

    thanx for all your suggestions.

  25. #25
    Join Date
    Feb 2008
    Location
    QLD
    Age
    54
    Posts
    74
    Rep Power
    17

    Re: Panasonic Cassette

    I am still intrigued as to what temperature the end user wants to run it on?
    and did it fault at those settings?

    Would you mind telling me the customers normall settings please?
    Last edited by stefs_cruiser; 16-04-2009 at 05:37 AM.

  26. #26
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Panasonic Cassette

    Customers normal settings was 22 degrees

    and yes they first noticed it wasnt cooling set at that temp, so naturally tried to lower the set point and unit would still not cut in.

Similar Threads

  1. Daikin 7kW Cassette +supply duct to small office
    By Makeit go Right in forum Air Conditioning
    Replies: 6
    Last Post: 12-12-2007, 03:41 AM
  2. Panasonic CS-80U32JP cassette.
    By Temprite in forum Air Conditioning
    Replies: 0
    Last Post: 01-03-2007, 11:25 AM
  3. LG Cassette
    By Abe in forum Air Conditioning
    Replies: 16
    Last Post: 01-07-2005, 07:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •